UPS Problem

04/14/2013 12:17 PM

Dear all.

Recently we installed a 40 kva UPS having 3 phase 415v input supply & 230v out put.

when we measure the each phase to earth voltage in input side it is 234 v(R-Y-B-E).& in at out put end Phase to Earth voltage is 172 v & Neutral to Earth voltage is around 62V.is it Ok?? we always hear that Neutral to Earth Voltage should be less than 2 V.we also checked our Earth pit Resistance that is 3.22 Ohms.Is any way to reduce it???

here is the drawing of ups.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: UPS Problem

04/14/2013 12:46 PM

Yes.

Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#2
In reply to #1

Re: UPS Problem

04/14/2013 1:04 PM

is 62V ok?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: UPS Problem

04/14/2013 1:17 PM
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #2

Re: UPS Problem

04/15/2013 9:28 AM

In stand alone systems, it does not matter at all. Only when two systems have a data communication between them, and, if the data zero reference is taken from the ground, the neutral-to-ground voltage does matter, as in such a case data corruption might occur, if there is an appreciable neutral-to-earth voltage. In such a system, the ideal neutral-to-earth voltage should be ZERO volts. But, practically up to about 2 volts is permissible.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: UPS Problem

04/14/2013 4:22 PM

Given that circuit, the output is floating. So the voltage to earth could be anything and it is therefore OK. However, the jury is out as to whether a downstream phase-to-earth fault would take out the circuit protection device in the event of a fault before someone gets hurt/killed.

Did this thing get tested and certified by a qualified Electrician before being energised?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#5

Re: UPS Problem

04/14/2013 6:43 PM

It sounds like you are just missing the physical connection between the output common line and the earth ground.

As far as I know its standard procedure to have those both connected together so that earth ground fault sensing devices will work properly.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: UPS Problem

04/15/2013 3:17 AM

...but do check the manufacturer's installation and use instruction leaflet just to make sure.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: UPS Problem

04/15/2013 5:37 AM

Just a WAG - it was a 2013 digital voltmeter and not a 1960s moving-coil multimeter, correct?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#9
In reply to #7

Re: UPS Problem

04/15/2013 1:10 PM

Yes dear this is a 2013 digital multimeter.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #9

Re: UPS Problem

04/16/2013 3:26 AM

Well, then, it's probably of super-high input impedance, and because of that it's picking up a load of capacitance coupling between the supply rails and earth/ground.

  • If one uses a 1960s-style AVO (usual disclaimer) to measure the voltage instead, what happens?
  • If one de-energises and measures ohms from neutral to earth/ground, what happens?
  • If one wires a 15W light bulb between neutral and earth/ground before re-energising, what happens to the voltage?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#12
In reply to #11

Re: UPS Problem

04/21/2013 12:45 AM

1.Yes voltage is the same with analog voltmeter.

2.after disconnecting the incoming supply resistance is varies from 25 to 42 Ohms.

3.When we connect a 11W bulb with Neutral & Ground the voltage remain same.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10

Re: UPS Problem

04/15/2013 2:19 PM

Make sure all of your earth ground connections are connected together with no or minimum resistive connections.

You may have to install a low impedance equipment system ground grid with bare copper interconnecting conductors if the soil is dry and poorly conductive.

The "earth pit" resistance can be decreased by applying a "wetting" agent such as water and/or one of the many chemicals available such as GEM directly around the ground well as per the manufacturer's directions. This works best if the entire length of the ground rod/buss down into the earth ground well is accessible.

Also:

Unless I am mistaken your drawing indicates an ungrounded/unearthed "Delta" primary (input side) with a surge arrestor network and drain to earth ground.

The point at which you attach the meter to take the readings can affect the result as you may be reading voltage drop across an arrestor and/or you may be capacitively coupled through the transformer windings.

FLUKE makes a very good ground grid testing meter that will reveal not only the impedance but the distance from the reading point to the fault (high impedance) location.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); lalit_nawada (3); lyn (2); PWSlack (4); SHOCKHISCAN (1); tcmtech (1)