Starting of Induction Motor

04/15/2013 7:43 AM

How much time Induction motor will take to reach the rated speed?

And how much current will it consume in that time?

Register to Reply
Pathfinder Tags: Starting of Induction motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Starting of Induction motor

04/15/2013 7:55 AM

A1) It depends upon the inertia of whatever it is driving.

A2) Starting at about 5 times full load current dropping back to full load current or below in the time A1↑.

Current isn't consumed. It is drawn, taken or supplied, among other things.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2012
Posts: 115
#2

Re: Starting of Induction motor

04/15/2013 7:58 AM

Thank you can you give me the time current Characteristics for star delta starter for an example?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Starting of Induction motor

04/15/2013 7:59 AM

Not possible, as there is no information on what the motor is turning, which affects the gradient of the slope at any point on it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Starting of Induction motor

04/15/2013 9:17 AM

The other factors that affect the slope are:

  • The rating of the motor
  • The voltage of the supply
  • The torque/speed characteristic curve of the load
  • The timer settings in the starter
  • The rating of the supply
  • The loads applied elsewhere on the supply
  • Etc.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5
In reply to #2

Re: Starting of Induction motor

04/15/2013 9:22 AM

Please note that the magnitude of the starting current of an induction motors is decided by the motor parameters and is normally given by the motor manufacturer. The duration of the starting current is decided by the inertia (GD2) of the motor's rotor AND of the connected load. Obviously, the higher the total GD2, the more would be the starting time.

For example, if a motor with a rated full load current of 100A, draws, let us say, 6 times its rated current during starting (with a DOL starter), then even if the motor is not coupled to any load, it would still draw 600A; but, in such a case, this 600A starting current would last for a very small duration of, say, about 4 seconds. Now, if this motor is coupled to a centrifugal pump, then again this motor would draw the same 600A during starting, but now the starting current would last for about 10 seconds. If the same motor is coupled to a centrifugal blower, again there would be a starting current of 600A, but now, this might last for about 20 seconds.

With star delta starting, the acceleration time would increase for the same load, as the starting torque of an induction motor is proportional to the square of the applied voltage. And, with star delta starting, the voltage at the time of starting is reduced by root 3 times and thus the starting torque would reduce by 3 times and hence the longer acceleration time.

Hope it is clear.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Starting of Induction Motor

04/16/2013 11:48 PM

As it was already said in the above posts, the starting time depends on the acceleration torque, motor rpm and inertia moment of the motor and the load. See-for instance:

http://www05.abb.com/global/scot/scot259.nsf/veritydisplay/bf88560fb1b0335cc2256fc6003e4e05/$File/Motor%20guide%20GB%2002_2005.pdf

section 4.3.3 Starting characteristics

ts=2*pi()*rpm/60*(JM+J'L)/Tacc ts =starting time [sec]

JM=motor inertia moment [kg*m^2 ] JL=load inertia moment [kg*m^2]

J'L=JL*(rpmLoad/rpmMotor)^2 if there is here a gearbox.

Tacc=Tmotor-Tload acceleration torque[Nm]

Tmotor=0.45*(Ts+Tmax) approx. Ts=start torque Tmax =maximum torque

Tload=kl*Tratedload Tratedload=Tnmot=rated motor torque [usually].

Kl=1/3 for centrifugal compressor or pump.

__________________
Julius
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); electricalexpert65 (1); Muthuvel (1); PWSlack (3)

Previous in Forum: Modular Blocks for PLC Applications   Next in Forum: CT Magnetisation Current Ie

Advertisement