Cable Sizing

04/17/2013 6:28 AM

Regarding cable sizing, let say given all the parameters needed I can compute the minimum required cable size but I opted to chose the next higher size, to have allowance,is that ok? which is the common practise followed by Engineers?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable Sizing

04/17/2013 6:30 AM

The common practice here is British Standard 7671. Oversizing is wasteful.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Cable Sizing

04/17/2013 10:35 AM

If you have taken ALL the parameters needed into consideration, then you NEED NOT oversize.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Cable Sizing

04/17/2013 10:36 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Cable Sizing

04/17/2013 12:41 PM

It takes more electricity to fill those larger cables, so you'll always have a little reserve juice left over.

But, if it stays in the conductor too long it will get stale.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Cable Sizing

04/17/2013 3:44 PM

Does one of these parameters also include expected future increases in load current due to expected plant expansion, future equipment upgrade, etc?

If so then using a larger cable size is much better than having to re-run a larger cable later on, if not then there is no reason to use a larger cable. Copper ain't cheap.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Cable Sizing

04/17/2013 4:57 PM

...in which case the cable would be correctly sized and protected for the larger duty, ready for when the duty comes on. To describe it as oversized would be inappropriate.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7

Re: Cable Sizing

04/17/2013 11:01 PM

It is not a common and general practice to select the next higher size cable if all considerations of cable sizing are appropriately considered. However, many engineers do it to be more safe. In addition to the excess cost of the cable, selecting higher size cable may cause some other issues, such as cable termination, cable bending, space in raceway, excess weight etc. When you select higher size cable, make sure not to arise these issues.

Believe me or not, sometimes cost saving happens with selecting higher size cable. For example, there are five motors to be installed, three of them require 4 AWG, each 400 feet (total 1200 feet) and other two require 2 AWG, each 400 feet (total 800 feet). The cable vendor has minimum order quantity 2000 feet for each size of cables. If we use both size cables, we need to buy 2000 feet 4 AWG cable and 2000 feet 2 AWG cable. But, if we use all 2 AWG cable (it is higher size cable for three motors, 2 AWG instead of 4 AWG), we can completely avoid buying 4 AWG cable and it saves almost 50% of the cable cost.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#8

Re: Cable Sizing

04/18/2013 2:08 AM

Check this for complete Detail
Conductor and Cable Sizing

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); jack of all trades (1); lyn (1); msamad (1); nobodysomebody47 (1); PWSlack (3)