Current Drawn By A Motor When Starting Via A Variable Frequency Drive

04/17/2013 8:04 AM

Hi everyone...

In most of the cases, for a motor starting via a VFD/VSD, it is mentioned that the starting current is 'lower' than the Direct-On-Line starting of the motor. Is there a value to this 'lower'? I mean, is the VFD starting current same as the full load current or 2-3 times of it as against 5-8 times in DOL starting?

Thanks!!

Register to Reply
Pathfinder Tags: motor starting VFD
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Current Drawn By A Motor When Starting Via A Variable Frequency Drive

04/17/2013 8:22 AM

It depends upon how the drive is programmed, which cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Current Drawn By A Motor When Starting Via A Variable Frequency Drive

04/17/2013 10:34 AM

A VFD definitely has soft starting inherently built-in. But, the starting current even with a soft starter or VFD could not be reduced to the bare minimum. The best one could achieve would be 2 to 3 times the full load current. One cannot go lesser than this.

Register to Reply Score 1 for Good Answer
8
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #2

Re: Current Drawn By A Motor When Starting Via A Variable Frequency Drive

04/17/2013 5:55 PM
  • "The best one could achieve would be 2 to 3 times the full load current. One cannot go lesser than this."

This statement is true for Reduced Voltage Solid State Soft Starters, but not for VFDs.

Because a VFD is controlling both the voltage AND the frequency (unlike a RVSS that controls the voltage only), you can in theory get a motor to produce full torque at any speed, and if you use a Vector Control VFD, that is absolutely true. Given that then, you can accelerate a motor with no more than 100% of motor rated current.

HOWEVER, what will change is the amount of time. If there is a lot of inertia, 100% of motor rated current may take you 1, 5, 10 or 15 minutes to fully accelerate it, or if you want to accelerate it in 10 seconds, you might have to allow the VFD to go to Breakdown Torque output, which means upward of 250% current. So without knowing the required acceleration parameters you are looking for, you cannot make any accurate prediction of motor starting current when using a VFD.

But to answer your SPECIFIC question, theoretically you can accelerate a motor with 100% of motor nameplate FLC if you use a VFD, as long as you do not care how long it takes to get there. And because you are not exceeding the FLC of the motor, you can take 3 weeks if you want to...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 8)
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Current Drawn By A Motor When Starting Via A Variable Frequency Drive

04/17/2013 3:39 PM

Additional information can be found in the manual for the VFD/VSD depending on how it is set and what motor load you are trying to drive.

__________________
jack of all trades
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2007
Posts: 102
Good Answers: 8
#5

Re: Current Drawn By A Motor When Starting Via A Variable Frequency Drive

05/02/2013 3:57 AM

In VFD's the motor drive is chopped DC. The rectifier output is fed to chopping devices via a low-pass filter consisting of a large capacitor. During motor start the majority of the motor's current is reactive. During the time power is being fed back from the motor (twice each cycle each phase) the energy charges the filter capacitor.

No energy goes back through the rectifier. The rectifier input corresponds to motor power, effectively filtering watts from VA. The VAR merely shuffles in and out of the filter capacitor. Depending on design the rectifier input power factor can be almost unity but cheaper designs have substantial mains harmonic currents.

Summing up, the motor's reactive needs are supplied by the capacitor so the supply line current at starting speeds is greatly reduced. With most drives it will be much less than full load current, building up as the motor speed is increased.

The reactive

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); jack of all trades (1); JRaef (1); PWSlack (1); Zaf (1)

Previous in Forum: Cable Sizing   Next in Forum: Transformer Differential and REF Protection

Advertisement