Drawout Type MCCB

04/18/2013 2:32 PM

Greetings

Can any body tell the advantages of fixed type MCCB over drawout type MCCCB in a low voltage panel.

Actually our client had ordered us to make panel with drawout type MCCBs & we made it with fixed type MCCBs. How can i justify it to my client?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Drawout Type MCCB

04/18/2013 2:51 PM

"How can i justify it to my client?"

By having proper documentation and back-up information given to you by a qualified engineer who is familiar with the project requirements.

I'd also ask them to represent you with the customer, who will see immediately that you don't have a clue, if you try to bluff your way through this using total strangers as your only reference.

Hire an engineer.

By the way. Why didn't you give the customer what they wanted in the first place?????

Now you're trying to justify your companies incompetence with smoke and mirrors.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Drawout Type MCCB

04/18/2013 3:11 PM

Actually our client had ordered us to make panel with drawout type MCCBs & we made it with fixed type MCCBs. How can i justify it to my client?

You mean how can you get out of your mistake.

Supply the customer with what they specified, ordered AND paid for free of charge (at your expense). The customer is right in this case and likely had very good reasons for ordering the panel with drawout type MCCCB(s).

Additionally talk it over with your customer - if you have made a mistake TELL them that and see what the two of you can work out, perhaps the two of you can compromise on a solution.

Don't try and bull$hit them because if you have to ask this question on a forum then the customer probably knows more than you do and it will only make things worse.

Jack - The customer is always right.

__________________
jack of all trades
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Drawout Type MCCB

04/18/2013 4:38 PM

Cheaper price is the principal justification. But if it was cheaper only to you, and not to the client, that would be very poor justification.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Drawout Type MCCB

04/18/2013 9:04 PM

Wow, gotta love the size of his big brass cojones...

Can you imagine?

"I was low bidder on this drawbridge, but decided to build it as a fixed bridge. Please can someone tell me the advantages of a fixed bridge over a drawbridge so that I may explain to my customer why he does not need a drawbridge."

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #4

Re: Drawout Type MCCB

04/18/2013 10:28 PM

What are you complaining about, boats can go through both and both can move, what's the problem?

__________________
jack of all trades
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #4

Re: Drawout Type MCCB

04/19/2013 3:37 AM

That's an interesting parallel.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5

Re: Drawout Type MCCB

04/18/2013 9:45 PM

So you want to CYA? Why the h*** did you not use drawout MCCBs in the first place? OK, others have covered all this rather well (especially the bridge analogy)

You should really have convinced the customer to save himself some money at the time of ordering... "MCCBs are not maintainable, so why drawout? You can only replace an old, (perhaps damaged) MCCB with a new one. You can as well take a little time about it and save yourself the extra cost. Not to mention the extra plug contacts which will add to the heat in a drawout MCCB...." Any number of good reasons are available for both, provided you know the business, which you don't seem to know. Want me to convince you why drawout MCCBs are better?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #5

Re: Drawout Type MCCB

04/19/2013 12:11 AM
  • "MCCBs are not maintainable, so why drawout?"

So that you can remove and replace a single MCCB in a panel without killing power to the entire panel. That's the ONLY reason I have ever had to use one.

Exactly one in a 30+ year career...

But when I worked for Siemens, we offerred that accessory and I recall seeing a presentation from the product group that indicated some specific industries that required them in certain applications. Can't remember the industries or the applications now though, I just remember thinking "Oh well, I don't have any of that around here, make room for some other piece of trivia..."

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster #2
#8

Re: Drawout Type MCCB

04/19/2013 12:25 AM

Hi,

Advantages of fixed type MCCB over drawout type MCCB.

1) Fixed type MCCB's can be mounted in any orientation (vertically and horizontally).

2) Foot print of the MCCB is very less when compare to the draw out type MCCB.

3) Contact losses are more in draw out type (connection is made with spring reinforced jaw clamps designed to hug the bus in draw out type MCCB, so if spring fails then the temperature rise in the contacts points will lead fire hazardous)

4) and of course the price is cheaper.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #8

Re: Drawout Type MCCB

04/19/2013 10:51 AM

Re: 1) and 2), The draw-out accessory for the Siemens VL series breakers I saw were not subject to any orientation constraints and were barely a fraction of an inch larger footprint than the breaker itself. The depth was significantly more, but you said footprint.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#11

Re: Drawout Type MCCB

04/19/2013 11:27 AM

The two biggest advantages are safety and up-time.

Safety because a drawn out breaker can't be "accidentally" closed and energize a locked-out circuit, also the type of construction reduces the level of potential arc-flash exposure and the required type of PPE.

Up-time because a draw-out breaker can be replaced in under a minute and without requiring the shutdown of adjacent circuits.

More than likely your client has a critical need to maximize the availability of power to his installation, something that you had no right to second-guess. Replace the equipment and eat the cost, you cannot justify your actions (...and maybe your client has learned to question why one bid was significantly lower than the others.)

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12

Re: Drawout Type MCCB

04/20/2013 5:51 AM

I would love to be a fly on the wall the when you try to explain to the customer he ordered the wrong thing.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster #3
#13

Re: Drawout Type MCCB

04/20/2013 1:42 PM

Deliver what is ordered. (don't try to justify).

And

learn from mistake....

Reply Score 1 for Good Answer
Active Contributor
Engineering Fields - Electrical Engineering - New Member

Join Date: Mar 2013
Location: Papua New Guinea
Posts: 10
#14
In reply to #13

Re: Drawout Type MCCB

04/30/2013 12:00 AM

I understand your situation. It is better to own up. Tell him you have made the wrong one and are in the process of making the right ones. Apologise to him for the error. Do not decide for the client the next time unless he allows you to do so.

__________________
"Whatever your mind can concieve, and believe, it can achieve"...Napolean Hill
Reply
Reply to Forum Thread 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); jack of all trades (2); JRaef (3); kvsridhar (1); lyn (1); nick.mapun (1); PWSlack (1); RAMConsult (1); TonyS (1); Tornado (1)

Previous in Forum: Any Ideas For A 35V DC Voltage Regulator?   Next in Forum: Unbalanced Standard - ETAP

Advertisement