Can an external pull up resistor be used to convert an NPN output from a sensor to a PNP input to the PLC?
Re: NPN to PNP
05/01/2013 2:33 PM
I believe there is more to it to change from sourcing to sinking, quick here search showed this,
http://cr4.globalspec.com/thread/18551/Replacing-an-NPN-Sensor-with-a-PNP-Sensor#comment192715
I'm sure there is more out there.
Re: NPN to PNP
05/01/2013 3:04 PM
The I/O module on the CoDeSys controller I have has PNP inputs. Here is the single channel rotary pulse generator/linear sensor combination (with NPN output) that I want to use.
It is being used to measure length of a masking paper for indexing after each cycle of a machine.
Good Answers: 32
Re: NPN to PNP
05/02/2013 12:32 AM
Yes you can but you will have to make sure that the pull-up is sufficient to get the input to a high enough voltage to work correctly. The max. output current of your device is 40mA so if you arrange for about a 10mA pull up that should suffice. If it doesn't work as expected check the output on a CRO once connected (you probably know that...).
johny451
Re: NPN to PNP
05/02/2013 7:54 AM
I've used this cable sometimes to convert the input to a PNP input: http://www.ifm.com/products/us/ds/EVC01E.htm
Re: NPN to PNP
05/03/2013 4:37 PM
I would say that you would be better off driving a PNP transistor with your NPN output through a resistor to the base. Connect the PNP emitter to +V and its collector to your PNP input of the PLC.
Re: NPN to PNP
05/06/2013 8:26 AM
I am pretty sure Keyence, and maybe some other sensor manufacturers or terminal block manufacturers make a NPN-PNP converting terminal block. If I am remembering correctly the Keyence part was in the $10-20$ range and was in a convenient 6mm terminal block form.