Anonymous Poster #1

Braking Resistors

05/02/2013 7:17 AM

In EOT cranes the induction motors are controlled by VFD s also braking resistors are also provided.It is said that the braking resistors are provided to reduce the DC bus voltage building up to a high level when the motor is stopped quickly.

My doubt is that if we are using a contactor in between the vfd terminals and cable connecting the induction motor terminals and if we do the control wiring in such a way to isolate the vfd from the motor at the time of stopping so that the voltage building up in dc bus can be avoided..?

And one more doubt is that what will happen if the ac induction motor is stopped suddenly..? (considering that it is directly fed from the supply with out the vfd and no braking resistor is used at the time of stopping.)

Will the motor burn out...? sorry to ask it may be a silly or a stupid question but i would like to know about this..

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Braking resistors

05/02/2013 7:37 AM

Why can't the crane manufacturer answer all these questions over the telephone, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Braking Resistors

05/02/2013 9:13 AM

You should not make any alteration to a cranes control system without consulting the manufacturer.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Braking Resistors

05/02/2013 10:13 AM

...as to do so may invalidate any indemnity insurance cover on the equipment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
7
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Braking Resistors

05/02/2013 10:25 AM

1. Opening and closing a contactor on the output of a VFD under load will cause damage to the transistors and premature failure of the VFD.

2. Killing power to the motor may result in uncontrolled movement /swinging on the crane (assuming travel here) because if the VFD was intended to be the primary control element, the brakes may have been modified to only be holding brakes, vs an "S-curve" deceleration profile in the VFD.

3. The dynamic braking via the resistors is a very good way to control a bridge crane travel. Why mess with it by removing half of the benefits?

4. As the others have said, discuss this with whomever made the decision to put in the VFD in the first place before doing anything.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 7)
Anonymous Poster #1
#5
In reply to #4

Re: Braking Resistors

05/02/2013 1:29 PM

Thanks JRaef that was really helpful.

One more thing i need to ask which keeps me confused

if a freely rotating induction motor is stopped suddenly after the power being cut off what will happen to the energy stored or voltage generated.? where will it gets dissipated , across the windings or across the windings and the cable connected and if so will the motor winding gets damaged..??

Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #5

Re: Braking Resistors

05/02/2013 5:19 PM
  • "... if a freely rotating induction motor is stopped suddenly after the power being cut off what will happen to the energy stored or voltage generated.? where will it gets dissipated , across the windings or across the windings and the cable connected and if so will the motor winding gets damaged..??"

In order for an induction motor to regenerate, you must have the windings excited (so that the electromagnets are created) and the mechanical speed of the motor must be higher than the synchronous speed of the motor. When you kill power to an induction motor, the magnetic fields collapse in about 1/2 second, so it is no longer regenerating anything.

The reason why you can have regen in a motor controlled by a VFD is that the when decelerating, the VFD is still energizing the windings, AND is giving the motor a LOWER synchronous speed than the mechanical speed, thus satisfying the necessary conditions. Just turning off the motor by killing power does NOT create a generator. The kinetic energy left over in the spinning mass is dissipated as wind, heat in the bearings and other drive train components over the coast-to-stop time. No winding damage at all.

Side note though; power factor correction capacitors connected "at-load", can keep the motor windings excited a little longer, but there is no relative synchronous speed, so the regen is still not continuous.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#11
In reply to #4

Re: Braking Resistors

05/03/2013 1:27 AM

You always have the best answers on motors and their control.

I will add the reason for the contactor. Its purpose is for safety.

The contactor is energized before the vfd is commanded to run the motor and it is deenergized after the motor is stopped. It is a secondary means to control the motor. It will keep the motor from turning if there is a fault in the control system or vfd which could cause an unintentional start. It could also be used as a secondary means to stop the motor again in the event of a fault.

Reply
Associate

Join Date: Jan 2012
Location: Halmahera Island Indonesia
Posts: 49
#12
In reply to #11

Re: Braking Resistors

05/03/2013 1:49 AM

Yep and always on the incoming side of the VRD. This also serves as a safety device if there is a fault in the VRD then power is removed from it.

I don't know how it is possible to run a VRD in this application without an incoming contactor. This contactor would normally be operted by the HMI which in turn enables the VRD and supplies power.

Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#6

Re: Braking Resistors

05/02/2013 1:42 PM

It's a braking resistor not intended as a circuit control device. It's there to control deceleration of the motor it's applied to. That's why it's called a braking resistor. In a bridge crane in the drive for the bridge the purpose is to slow the motion of the load to a stop to keep the load from swinging to much.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Associate

Join Date: Jan 2012
Location: Halmahera Island Indonesia
Posts: 49
#8
In reply to #6

Re: Braking Resistors

05/02/2013 10:51 PM

Correct me if I am wrong but i have had many years of experience in the EOT industry.

1. The contactor should always be on the input of the VFD. If it is on the output then it is nothing more than a soft starter.

2. Depending on the size of the motor a braking resistor may not be required. All VFD for this type of application will have a brake relay which will de-energise the motor brake once it has reached a pre-determined ramp down speed, normally 0.

3. Braking resistors are required where there are high torque/ load applications. If not used in this application it will destroy the VSD due to the regenerative energy produced by hte motor during ramp down. And will also be fitted with brake relay for final stop. In this instance the motor brake is a park or holding brake and plays no part in the braking of the crane.

3. Braking resistors do indeed dissipate the regenerative energy produced by the motor during ramp down. This energy is dissipate in the form of heat generated in the resistor.

Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#13
In reply to #8

Re: Braking Resistors

05/03/2013 7:53 AM

Motor size has nothing to do with the use of a braking resistor. It's the application. Example is The new miter saws use of one to increase safety. It reduces the amount of time it takes for the blade to spin down to a stop. Most application that I have seen the resistor is switched in and out of the circuit. If not switched it would leave a high potential on the output of the VSD.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#9

Re: Braking Resistors

05/03/2013 12:34 AM

If you use a four quadrant active front end VFD, the regenerative energy available during deceleration can be fed back to the system provided there are other consumers in the network to absorb that energy. However, in absence of other loads at that moment, the bus voltage will rise and the energy can be dissipated through the braking resistor.

In case of power failure, however, the above methods of braking will no longer be available and the hydraulic operated mechanical brakes will stop the mechanism immediately.

Reply
Associate

Join Date: Jan 2012
Location: Halmahera Island Indonesia
Posts: 49
#10
In reply to #9

Re: Braking Resistors

05/03/2013 12:41 AM

Wow. Hydraulic brakes!! Just how old are your EOT's? EOT brakes are always fail to safe, electrical or mechanical.

Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#16
In reply to #10

Re: Braking Resistors

05/06/2013 12:40 AM

These are not hydraulic thrustor type drum brakes, but hydraulic disc brakes allowing greater braking torques while equipment remains relatively compact. Disc brake inertia is much less than drum brake.

Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#14

Re: Braking Resistors

05/03/2013 9:26 AM

The braking resistors are there to absorb the energy created by regeneration when the load on the motor continues to cause rotatation after the voltage is removed.

Also;

When the applied voltage is removed, the magnetic field surrounding the motor lead conductors, motor winding conductors, and the motor laminations will collapse back into the conductors inducing very high voltage levels that will exceed the insulation breakdown voltage rating of the conductors. (The steeper the angle of collapse up to a limit of 90 degrees, the higher the induced voltage.)

The resistors provide a path to shunt or short this induced current through motor winding and associated conductors to keep the voltage level from exceeding the voltage rating of the system electrical insulation.

This also prevents the dangerously high voltage from getting back into the output circuitry of the VFD and causing damage there.

The operation of the braking resistor contactor is very fast and is more than capable of providing the needed motor protection if working properly.

In some cases the VFD has a separate filter network on the DC buss circuitry that includes resistors which perform the same way as the braking resistors to prevent excessively high voltage from being induced in the buss and conductors from the collapsing magnetic field(s).

This is the same principal taken advantage of by automotive ignition coils to provide high voltage to the spark plugs.

Keep in mind that in many cases such as with a crane, the engineering design incorporates the braking and VFD resistors into one package to save money.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#15

Re: Braking Resistors

05/03/2013 11:21 AM

Lots of good answers here already, but nobody appears to have said that you appear to be misunderstanding the job of the brake resistors completely.

The motor would be "braked/stopped" fastest with a short across the windings after power is removed, but a considerable current would be drawn from the back emf in the motor. This could possibly/theoretically even damage a motor not designed for dynamic braking.....

To drop this current to a reasonable level AND to slow the motor down more slowly/gently, braking resistors are used......

They are an integral part of the way the braking works AND inbuilt safety arrangements, you should leave well alone. No mods.

Stopping once or twice will warm up the motor only slightly. Stopping very often using dynamic braking may eventually over heat a motor not designed for such braking as quite large currents flow, albeit only for very short times....

NOTE.

Any electric motor (that I have heard of!), when spinning, generates a voltage when power is removed. (it is actually there all the time and it "opposes" the flow of current from the supply, which is why it is called "Back" EMF!! but you can ignore that in this situation if you wish).

Shorting this back EMF in some way stops the motor very quickly, like overloading a generator for example. You see this even in good quality hand tools, whether battery or mains driven, in the way the motor stops almost instantly. Cheap tools run on and can be a danger to the user.

If the short remains on the hand tool motor, you will find it difficult to turn at any sort of speed by hand. Remove the short and the motor is then far easier to turn by hand.

Here is a short video using dynamic braking and then only power removal braking on a motor driving a plastic disk via a gearbox, but you can distinctly hear and see the difference.

http://www.youtube.com/watch?v=n9PWwmQJfIs

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Reply to Forum Thread 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: