Ungrounded 12,470V System - Requirements

05/02/2013 1:25 PM

I am working on a project that has a GSU transformer that is 480V delta to 12,470V ungrounded wye. This project is in the United States. NEC 250.20(c) states that systems over 1 kV shall be permitted to be grounded.

Is there a requirement to ground my medium votlage system?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Ungrounded 12,470V system - Requirements

05/02/2013 1:27 PM

What does the code say? Local code, too.

What is the location?

Are you a licensed electrical contractor, licensed in the local in which you are now working????

Register to Reply
Active Contributor

Join Date: Apr 2011
Posts: 15
#2
In reply to #1

Re: Ungrounded 12,470V system - Requirements

05/02/2013 1:31 PM

Both of my codes says it is permitted to be grounded, but I could not locate anything that said it "HAD" to be grounded. I don't like that it is not grounded because of the transient overvoltages associated with it. I really want to ground it but with no code the client won't do it.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Ungrounded 12,470V system - Requirements

05/02/2013 1:33 PM

Then your next call should be to the local permitting/inspection agency to ask them.

Requirements vary from town to town, county to county and state to state.

Register to Reply
Active Contributor

Join Date: Apr 2011
Posts: 15
#4
In reply to #3

Re: Ungrounded 12,470V system - Requirements

05/02/2013 1:34 PM

Thanks - will do.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#6
In reply to #3

Re: Ungrounded 12,470V system - Requirements

05/02/2013 3:26 PM

Authority Having Jurisdiction (AHJ).

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Ungrounded 12,470V system - Requirements

05/02/2013 5:42 PM

Thanks.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5

Re: Ungrounded 12,470V System - Requirements

05/02/2013 2:04 PM

If the 12,470V will be connected to the local utility's system, they may have something to say also. Check with their protection engineer.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Ungrounded 12,470V System - Requirements

05/02/2013 7:23 PM

I can't see why you have a problem with earthing the neutral point.

You don't say the size of this transformer or its intended use. A NER would be the usual option for MV but with no information it's just guess work.

This smacks of homework.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Apr 2011
Posts: 15
#9
In reply to #8

Re: Ungrounded 12,470V System - Requirements

05/03/2013 10:45 AM

I can't earth the neutral point because the service is solidly grounded with induction disk relays (no directional ground fault detection) and the standby generators are grounded through a 200A impedance. The original design was to never island now they want to island.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10
In reply to #9

Re: Ungrounded 12,470V System - Requirements

05/03/2013 11:43 AM

"...The original design was to never island now they want to island...", all bets are now off. This is a radical departure from the original design and requires a new complete system study, including a review of the existing system and coordination with the local utility.

This is not a simple "handbook engineering" exercise; personnel and equipment safety are at issue, as well as code compliance and insurability. Hire a competent electrical power engineer who has done this type of thing before.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #9

Re: Ungrounded 12,470V System - Requirements

05/03/2013 1:17 PM

Tell them they can't do it! Then quit.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#12

Re: Ungrounded 12,470V System - Requirements

05/14/2013 11:40 PM

Try "ASK THE EXPERT" feature in www.igard.com"

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers: