Fault Level in Transformer with OLTC

05/02/2013 8:51 PM

In the case of transformer with OLTC,percentage impedence changes with the tap changing and fault level reduced when impedence changes.Then how is the fault level calculation becomes satsified.We design the transformer with the normal percentage impedence.Clarify.Quote IEC 609090-0

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Fault level in transformer with OLTC

05/02/2013 10:00 PM

Choose whichever is the least impedance; i.e., worst case scenario.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Fault level in transformer with OLTC

05/02/2013 10:31 PM

Perhaps I am reading this question wrong or misinterpreting your rather rude tone (it has been a really LONG day).

Do you mean IEC 60909-0 ? I am assuming from the information supplied you are a paid project consultant or transformer company designer? What do YOU think the answer is (the answer is obvious to me by the way).

Why don't you refer to IEC 60909-0 and have a think about it yourself or contract me or some other suitably qualified Engineer to offer you services as a paid consultant.

__________________
jack of all trades
Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Fault level in transformer with OLTC

05/02/2013 10:35 PM

Just out of curiosity, if OLTC is the abbreviation for On-Load Tap Changer, what is the abbreviation for Off-Load Tap Changer? Inquiring minds want to know....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Sep 2008
Posts: 39
Good Answers: 1
#4
In reply to #3

Re: Fault level in transformer with OLTC

05/03/2013 8:54 AM

OCTC -- off circuit tap changer. Atleast this is the way it is called in bangalore (india)

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #3

Re: Fault level in transformer with OLTC

05/03/2013 10:52 AM

In the US it's NLTC (No Load Tap Changer).

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Fault Level in Transformer with OLTC

05/03/2013 11:30 AM

"...percentage impedance changes with the tap changing and fault level reduced when impedance changes...", this is only true if the tap changer is always started at one end of its range.

Short circuit studies are extra conservative; i.e., you want the conditions that provide the worst case scenario, therefore you assume that the tap is set to the end of its range that provides the highest short circuit current (you do know which end that is, don't you?)

On the other hand for load-flow, relaying/breaker coordination, and voltage studies the actual tap setting is very important and will have a major effect on the accuracy of the results.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Fault Level in Transformer with OLTC

05/14/2013 11:39 PM

Obviously do it for the worst case scenario. That is, for the tap with least impedance.

Register to Reply