Dear all
we have an instrument pressure transmiiter and the service is vapours is it possible to install below the tapping point since it is pressure transmitter.
Regards
Re: presure trasnmitter
05/03/2013 11:19 AM
If vapours means a gas, then yes.
Reply Score 1 for Off Topic
Re: Pressure Transmitter
05/03/2013 2:19 PM
Condensate or liquid, or liquid droplets in the line will tend to drop to the bottom of an impulse line below the tapping point and collect there.
Gas pressure measurements are done at an elevation above the tapping point/line in order to keep the impulse line free of liquid.
05/05/2013 6:10 PM
..so the only individual that can answer the question is the one looking at either the location of the proposed installation, looking at the P&IDs and general arrangent drawings, or looking at the instrument hook-up drawing for the instrument in question. It's a bit difficult to see any of those things from here.