Testing Isulation Resistance

05/07/2013 10:12 AM

Hi,

What is the difference between using DC and AC tester for testing insulation resitance?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: testing isulation resistance

05/07/2013 10:37 AM

A DC tester uses direct current to test IR and an AC tester uses alternating current to test IR.

Do you see any difference in the two types of current? Look at them on a scope.That may be a clue.

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#2

Re: Testing Isulation Resistance

05/07/2013 12:20 PM

if AC is used then the capacitance introduced by the insulation will be part of the impedance measured and then the resistance is required to be calculated . . . DC is used if resistance alone is required to be measured

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Testing Isulation Resistance

05/07/2013 12:28 PM

You have not told us the type of equipment nor the operating voltage. If it is ordinary "stuff" like house wiring it won't make a difference. If it is medium or high voltage power equipment then the tests provide different clues as to their health. Also some tests are inappropriate/less sensitive/more destructive if used indiscriminately or on the wrong type of equipment. Google on the title of your question for more info.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Testing Isulation Resistance

05/08/2013 12:23 AM

Not only for IR for HV test(Hipot) too AC & DC are used,google and see.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Testing Isulation Resistance

05/08/2013 3:33 AM

The square root of 2 is one difference.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#6

Re: Testing Isulation Resistance

05/08/2013 1:07 PM

On a high speed production line, where products come into contact with a high voltage DC hipot.......there is no difference because making contact with the probes sets up an impulse which by definition in terms of LaPlace Transforms contains lots of high frequency components. A continuous AC tester will most likely do the same. Sometimes, it is not the device but the method that makes a difference.

An AC tester that uses a zero crossover start and stop circuit however will generally just supply the fundamental frequency thereby setting up a condition by which the impedance (including capacitance and resistance) can be carefully measured.

A DC tester that ramps up at some rate will still have some AC component. You have to decide what you really are trying to test and then check your method.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#7

Re: Testing Isulation Resistance

05/08/2013 11:04 PM

i guess the question, by Selimo, is very simply relating to insulation resistance measurement using a simple instrument commonly known as a Megger . . . Selimo, please clarify so that all of us chase the same goose . . . if i have guessed wrong, i will be happy to be corrected . . .

Register to Reply
Participant

Join Date: Jan 2013
Posts: 4
#9
In reply to #7

Re: Testing Isulation Resistance

05/13/2013 4:29 AM

What was actually happening Soebfatehi is that, we had a 11kv bus bar fault where we took off all the bars pieces and spouds to be cleaned and bars to be re insulated with reychem insulation, after that we wanted to test(inject about 11 to 22kv in to the bars) to make sure all is right, yes i understand i have to know my country standards, which is Lesotho standards.

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#10
In reply to #9

Re: Testing Isulation Resistance

05/13/2013 6:33 AM

i stand corrected

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2013
Posts: 18
Good Answers: 2
#8

Re: Testing Isulation Resistance

05/09/2013 1:05 AM

Get one of these.

http://www.fluke.com/Fluke/usen/Insulation-Testers/Fluke-1555-1550C.htm?PID=69212

Generally DC testers are used in a DC environment, AC in an AC environment.
Unless you're testing high voltage traction motors, etc. A DC meter is probably not needed.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11

Re: Testing Isulation Resistance

05/13/2013 8:27 AM

Use DC for IR Test

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); Horizon3 (1); lyn (1); NotUrOrdinaryJoe (1); pnaban (1); PWSlack (1); RAMConsult (1); selimo (1); soebfatehi (3)