Voltage Drop Calculation

05/19/2013 9:11 PM

In voltage drop calculation, when the phase conductor is 2 sets and earth conductor is 1 set utilized, should i consider the resistance and inductance are half of the value that the conductor have? how do i calculate?

Register to Reply
Pathfinder Tags: Voltage Drop Calculation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Voltage Drop Calculation

05/19/2013 9:21 PM

What constitutes a "set"?

Resistance has something to do with cross-section of conductors. All of them, providing the connections are able to carry the current.

Register to Reply
Member

Join Date: May 2013
Posts: 6
#2
In reply to #1

Re: Voltage Drop Calculation

05/19/2013 9:52 PM

2 sets [4x300sqmm XLPE/LSHF] + 1 x 150sqmm LSHF (E) total distance run of 250m.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Voltage Drop Calculation

05/19/2013 10:15 PM
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #2

Re: Voltage Drop Calculation

05/19/2013 10:38 PM

Measure the current in one cable and calculate or measure with a meter. If current distribution is unequal,check why.

__________________
pnaban
Register to Reply Score 2 for Off Topic
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#5

Re: Voltage Drop Calculation

05/20/2013 1:33 AM

The earth conductor is not part of voltage drop calculation. Using 4c cable means neutral cross section is same as that of phase. Ohms law applies with due consideration of 2 runs of phase and neutral conductor of equal cross section.

Register to Reply
Member

Join Date: May 2013
Posts: 6
#6
In reply to #5

Re: Voltage Drop Calculation

05/20/2013 2:14 AM

Using 2 sets of cables will help reduce the volt drop % instead of upsizing the cable?

In my point of view, it is not.

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#7

Re: Voltage Drop Calculation

05/20/2013 2:41 AM
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Voltage Drop Calculation

05/20/2013 3:40 AM

There shouldn't normally be any current in the earth conductor, as it is there only to carry the fault current until the moment the circuit protective device(s) disconnect the supply from the fault.

British Standard 7671 gives full cable sizing protocols.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9

Re: Voltage Drop Calculation

05/20/2013 5:26 PM

Some puzzlement here! If you have 2 sets 4 core, is that 3 phase and earth in each set - 2 cores for each phase, same colour/number core (whatever 3 phase colours/numbers you have)??

If that is so, you can happily halve the resistance and inductance compared to one cable.

However, if you mean single phase....

67model

Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#10

Re: Voltage Drop Calculation

05/20/2013 11:48 PM

I think the OP is talking about a standard single phase (Line) (Neutral) (earth) or (Line 1) (Line 2) and (Earth).

Earth only carries the fault current, so it's not included.

You have to consider the length of the conductor to be twice the one way distance to the load.

The basic equation is R=pL/A, but for Electricians the equation has been simplified to use the info from the wire gage table and constants for Aluminum or Copper.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11

Re: Voltage Drop Calculation

05/21/2013 7:01 AM

Calculation is not easy. Measurement is better. Cable makers publish data - example below....

http://www.eland.co.uk/bs-standards/bs5467/cable61/swa-cable--bs5467-steel-wire-armoured-pvc.html

click on the tab marked "Download product spec" on the above web page.

Recent cables have the standard embossed on the sheath.

National standards usually include safe impedance values, but do not separate inductance, which does matter at 300 sq.mm.

Remember that if you run "go" and "return" in different cables you will increase losses (volt drop) seriously [causing cable failure] and values tabled for inductance will be wrong.

67model

Register to Reply
Member

Join Date: Jun 2013
Posts: 5
#12

Re: Voltage Drop Calculation

06/12/2013 9:46 PM

Please refer to the below Calculation format.

Register to Reply
Register to Reply 12 comments