Motor Normally Operated of Rated Current

05/19/2013 9:57 PM

Hi guys, I just need your technical advise and help I on this.

There is a motor rated at 400VAC +10%/- 5%, 3 Ph, 50 Hz,0.37 W, FLC=1.5A.

Efficiency:0.62

Now I have to run it on the motor voltage at 410VAC ,3 Ph, 50 Hz. star connection ,DOL control with out any load ,but the amp is already at FLC:1.58 ,motor temp is 69°C w/o trip...

the question is :why the amp with out load is already at FLC?

Motor normally operated of w/o load is how many rated current ?

is any formula for calculate?

when i connect the pump ,and run again complete with pump, measure the amp is same at 1.5 amp…why ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: Motor normally operated of rated current

05/19/2013 10:41 PM

Check your meter(calibration) and connection(star or delta) in nameplate.

__________________
pnaban
Register to Reply
Participant

Join Date: May 2013
Posts: 4
#2
In reply to #1

Re: Motor normally operated of rated current

05/19/2013 10:47 PM

Dear pnaban,

meter is calibrate by last month, and the motor 400vac is for star connection .

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Motor Normally Operated of Rated Current

05/19/2013 10:54 PM

What's the service factor?

Register to Reply
Participant

Join Date: May 2013
Posts: 4
#5
In reply to #3

Re: Motor Normally Operated of Rated Current

05/19/2013 11:16 PM

power factor :0.66

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Motor Normally Operated of Rated Current

05/19/2013 11:11 PM

The power factor is no doubt quite low (and hence reactive current would be high) at no load; but even so, 1.58A does seem unusually high.

What is the ambient temperature? Motors are commonly rated for 40°C rise, so 69°C might or might not be excessive.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: May 2013
Posts: 4
#6
In reply to #4

Re: Motor Normally Operated of Rated Current

05/19/2013 11:24 PM

Dear Tornado,

Ambient temperature:-15°C - + 40 °C

Insulation class:F

, i test at Environment conditions:~30 °C

Motor normally operated at 80-85% of rated current w/o load... For is information is right?? i can't found this information

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Motor Normally Operated of Rated Current

05/19/2013 11:35 PM

There isn't really a standard for no load current of motors. Some mfrs do (and others don't) provide this information.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #7

Re: Motor Normally Operated of Rated Current

05/20/2013 12:01 AM

if all motor manufacturers print no-load current in the name plate,it would be very useful to check a motor's no load current after rewinding/replacing bearings etc

__________________
pnaban
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #8

Re: Motor Normally Operated of Rated Current

05/20/2013 12:15 AM

Maybe....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Motor Normally Operated of Rated Current

05/20/2013 3:38 AM

Because at no load, the angle between the voltage waveform and the current waveform is quite high, and at full load, it is quite low. Welcome to Power Factor.

None of the figures here give any immediate cause for concern.

Make sure that a motor overload device is wired into the starter circuit and that the unit is set correctly for the full load current of the motor. After that, don't worry, chicken curry.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Motor Normally Operated of Rated Current

05/20/2013 11:50 AM

When the voltage is higher than nameplate, even if within tolerance, the motor windings saturate a little and use more current as heat, that's why you are seeing the high temperature. At 1.58A on a motor rated 1.5A, your current is only 5% high, your overload relay pickup point is likely no lower than 115%, so i would not expect it to trip. Combined with the low power factor when unloaded, you are not seeing anything that unusual, especially with a motor that is only 62% efficient! By the way, that SUCKS, i would look for a better motor if I were you.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#12

Re: Motor Normally Operated of Rated Current

05/20/2013 4:37 PM

You have not told us the motor rated speed. As the number of poles increases and speed falls, the power factor gets worse and difference between full load and no-load currents becomes small.

For example, a modern high efficiency, Brook Crompton Motors type "W", 700 rev/min, 0.37 kW motor has FLC 1.63 amp @400V 3 phase, efficiency 62%, power factor 0.53 at full load, falling to 51%, 0.34 p.f. at half load. Refer http://www.brookcrompton.com/pdf-files/20113E_W_CI_IE2.pdf.

For example, with 0.6 power factor, the inductive current is 0.8 x FLC.

N.B. Right angle triangle with sides of length 1, 0.8, 0.6 represents 0.6 power factor.

Since the losses are high with 0.62 efficiency and magnetising losses are little reduced at no-load, while resistive loss will fall little if current is near FLC; little change no-load to full load is expected.

Note that if the losses are still near FLC value ~ 40%, the resistive side of the current triangle would be 0.4 X 0.6 = 0.24. With inductive side at 0.8, the resultant line current would be Square root (0.8 x 0.8 + 0.24 x 0.24) or about 0.84 rated.

You have raised the the line voltage, increasing no-load current - in any case, the tolerances on no-load magnetising current are high, like 10%.

Also, if you are using an ammeter on 10 amp range, a 2% full scale error is 0.2 amps.

So, in summary, if you have an 0.37 kW low speed motor, your numbers are not alarming. Worry if temperature rise is high at rated load.

67model

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#13
In reply to #12

Re: Motor Normally Operated of Rated Current

05/20/2013 5:12 PM

Add to post #12,

If you have winding 69 Celsius at 20 ambient, that is 50 degrees rise compared to probably 80 max for class B insulation.

No load at 85% rated current would be 0.72 x rated copper loss. For a small motor with 60% efficiency, expect 10% mechanical, 15% copper and 15% iron losses. Dropping copper loss to 72% rated only reduces loss 5% (in 40%) compared to full load. Temperature rise of about 50/0.72 = 69 degrees would be expected at worst, forgetting that rotor current would fall a lot.

67model

Register to Reply
Active Contributor
India - Member - New Member

Join Date: Oct 2010
Location: India
Posts: 20
#14

Re: Motor Normally Operated of Rated Current

05/21/2013 1:49 AM

There is no hard & fast rule for the calculation of motor starting current. It depends on construction and manufacture.. we do have some old motor(Made in Romania ) which are 0.65KW rating and taking 4 Amp. of current. It's temperature after running few hours is 80 degree C.

__________________
pstanwar9229
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #14

Re: Motor Normally Operated of Rated Current

05/21/2013 4:43 AM

Those are good candidates for early replacement on efficiency and on personal safety grounds.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#16

Re: Motor Normally Operated of Rated Current

05/25/2013 11:43 AM

my only question is.....other than a simple spin test under power to check rotation quickly and to verify that the motor works, why are you running it without a load?? the ratings are really only useful if the motor is performing work your voltage is within range. fire it up!

Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); chteng (3); Fredski (1); JRaef (1); lyn (1); pnaban (2); pstanwar9229 (1); PWSlack (2); Tornado (3)