(AC & DC )High voltage

05/23/2013 5:25 PM

Dear all

whats the type of voltage can we use (AC or DC )High voltage to check

generator,transformer,motor ,etc

thanks for all

Register to Reply
Pathfinder Tags: (AC & DC )High voltage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: (AC & DC )High voltage

05/23/2013 6:04 PM

Use the voltage required by the individual generator,transformer,motor ,etc.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: (AC & DC )High voltage

05/23/2013 6:13 PM

Check it for what? ....If you want to test the winding, I suggest a megohmmeter...

http://www.monition.com/electric-motor-winding-testing.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: (AC & DC )High voltage

05/23/2013 6:25 PM

You should use a calibrated voltage to test anything.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: (AC & DC )High voltage

05/23/2013 8:19 PM

I really hope we have a language issue at play here. If we do not...

You should test nothing with any kind of high voltage. The nature of your question tells me you are no where near qualified enough to use any type of high voltage, no matter if it is AC or DC.

High voltage kills! In fact any voltage can kill. Get a pro please.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: (AC & DC )High voltage

05/24/2013 3:15 AM

Follow the equipment manufacturer's instructions, which will be in the User Manual supplied with each piece of equipment.

If the user manual for any piece of equipment is unavailable, then use this

and get a copy of it sent over from the manufacturer straight away.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6

Re: (AC & DC )High voltage

05/24/2013 9:23 AM

It all depends on what test you want to perform. For example, insulation resistance ("megger") test is done with DC. Hipot testing can be DC or AC, depending on what type of equipment you are testing, what conditions you are testing for, and what the manufacturer recommends. Hipot can even be very low frequency (VLF) AC. Contact / connection resistance tests are usually done with DC. Tan-delta, dissipation factor, or Doble power factor tests are always AC. So you can see, there is no single answer to your question.

If you want to know, first find out what tests should be performed on a specific piece of equipment, and then the voltages and test procedures will be defined by the test itself.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #6

Re: (AC & DC )High voltage

05/25/2013 12:34 AM

What are the tests for which HV a)AC used and b)DC used?.

__________________
pnaban
Register to Reply
Commentator

Join Date: Sep 2012
Posts: 58
#9
In reply to #6

Re: (AC & DC )High voltage

05/25/2013 11:14 AM

Dear sir

thank you very much

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#7

Re: (AC & DC )High voltage

05/24/2013 10:16 AM

Check This please

AC & DC High Voltage

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: May 2016
Location: Ahmedabad
Posts: 21
#10

Re: (AC & DC )High voltage

05/10/2016 9:17 AM

It is totally depends on what test you want to perform.

__________________
Control Panels India
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

FADHEL (1); highvoltpower (1); lyn (1); nobodysomebody47 (1); North of 60 (1); PeterT (1); pnaban (1); PWSlack (1); redfred (1); SolarEagle (1)

Previous in Forum: Diode Failure   Next in Forum: Sealing Fitting

Advertisement