Anonymous Poster #1

Sealing Fitting

05/23/2013 7:27 PM

Dear All

I've installed control vlv and the armored cable was gland to the positioner however the client request to provide sealing fitting in between the gland and the IP positioner.

my question is it in the standard to provide sealing fitting? because in our approved design doesn't required future more this is not close conduit installation.

Regards

Moh'd

Qatar.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#1

Re: sealing fitting

05/23/2013 7:45 PM

I am aware of 2 reasons for using seal fittings

1) prevent the migration of hazardous gases through the conduit

2) prevent water (condensation or leakage) from migrating through the conduit.

If the client wants to pay, why not do what he wants?

If he's challenging your design without seal fittings, what's his reason for using seal fittings?

Reply Good Answer (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #1

Re: sealing fitting

05/24/2013 4:14 AM

1) is admirable, though not applicable to hazardous area electrical installations in Europe; EEx d equipment there has a tapered gland hole and requires metal-to-metal contact between the enclosure and the EEx d gland, which also has a tapered thread, so-many-turns of which need to be engagement between the enclosure and the gland itself. The reason is that it cools the potential flame path below the temperature needed to ignite a flammable atmoshpere outside the enclosure from an explosion within it.

Other methods of protection from explosion in hazardous areas do not require the prevention of migration of flammable gases through a gland fitting, the protection from explosion being effected by other means.

2) Here's an additional vote for this possibility - maintenance of an adequate Ingress Protection rating. GA

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: sealing fitting

05/23/2013 7:48 PM

Do you know who Abdu is?

You both sound like the same person.

Reply
Anonymous Poster #1
#4
In reply to #2

Re: sealing fitting

05/24/2013 10:14 AM

Dear Lyn,

May be if I see him?

Thanks man

Regards

Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#5

Re: Sealing Fitting

05/28/2013 9:30 AM

If the client is requesting a seal fitting, then before doing anything else:

1.- Find out the electrical classification of the area the unit will be located.

2.- Next make sure that the cables, cable glands, and other electric or electronic components are suitable for the are classification.

It would seem to me if they are asking for seal fittings the unit will be in a classified area, and if so they want to protect the equipment from electrical hazards.

I would suggest you talk to an engineer from the client to confirm the requirements.

Reply
Anonymous Poster #1
#6
In reply to #5

Re: Sealing Fitting

06/29/2013 3:15 AM

Dear All,

I've submit Engineering query to clarify the requirement of the sealing fittings, however client insist to install due to their Standard Operating Procedure.

Thanks a lot for your support.

Regards

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Iris (1); lyn (1); PWSlack (1); vargaalex (1)

Previous in Forum: (AC & DC )High voltage   Next in Forum: DC Breaker in AC Circuit

Advertisement