Overload Protection with DOL Starter

05/26/2013 5:03 AM

I am doubt with the MCB size for motor overload protection. I understand that a DOL starter would develop a very high inrush current / locked rotor current during start up. If I would use 6 - 8 times the FLC as the reference to size a MCB, I found that it is not same as the common practice. Is there any misconceptual so far ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: overload protection with DOL starter

05/26/2013 5:36 AM

The MCB should be rated at up to 250% of motor FLC. The MCB provides short circuit protection. Overload protection is provided separately, based on the nameplate FLC of the motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Overload Protection with DOL Starter

05/26/2013 11:30 AM

Read THIS↓carefully, twice, then you won't have to ask again.

Motor Calculations - Electrical Construction & Maintenance

Register to Reply
Commentator

Join Date: May 2013
Posts: 66
#9
In reply to #2

Re: Overload Protection with DOL Starter

05/27/2013 3:19 AM

Thanks Iyn for your attached link. If follow the NEC rules, sizing the overload protection for motor with DOL starter would be mainly based on the FLA. That means we totally no need to bother about the high starting current at overload protection MCB because all these have been tackle by the DOL starter, am I right ? I understand that DOL starter is only built with overload relay, circuit breaker etc. What is the principle behind which made a DOL starter can develop high current with the low inline current during start up. Please correct me.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #9

Re: Overload Protection with DOL Starter

05/27/2013 3:54 AM

"Overload protection MCB" is an incorrect phrase; the circuit breaker is not considered as overload protection.

Inverse-time CBs can carry progressively larger currents for progressively smaller lengths of time. I.e., a CB at 250% FLA can support starting current of say 6x FLA for several seconds, as can be seen from its trip curve.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Nov 2007
Posts: 86
#3

Re: Overload Protection with DOL Starter

05/26/2013 11:54 AM

Dear Members,

In all our existing installations we have an earth flat running parallel to the cable in cable tray, we use this earth flat for power earthing the electrical installations. this earth flat is connected to earth pit at one end.Let me know if this practice is wrong? What is the correct way as per standards.

Regards

Register to Reply Off Topic (Score 3)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Overload Protection with DOL Starter

05/26/2013 12:01 PM

What standards apply?

The fact that you have no idea if this is OK, or not, and don't know what standards apply leads me to believe that I should simply say, hire some competent help, fast.

<unsubscribes rapidly>

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5
In reply to #3

Re: Overload Protection with DOL Starter

05/26/2013 3:28 PM

Someone should have read the country and site standards and codes of practice before installing the earthing system.

If this is your job to see if this is correct or not you will need to obtain and read the standards yourself. If this is general interest, I don't have access to your country and site standards and codes of practice.

__________________
jack of all trades
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #3

Re: Overload Protection with DOL Starter

05/26/2013 4:41 PM

You seem to have accidantally replied to the wrong thread. There was a recent (5/23) thread titled "Grounding" that might be helpful.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Overload Protection with DOL Starter

05/26/2013 7:12 PM

Why does it always start with "I have doubt?"

O/L's set to FLC of the motor.

MCCB's set to protect the installation with allowance for the inrush a n d ……….

I'm in a bad mood!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #7

Re: Overload Protection with DOL Starter

05/27/2013 11:49 AM

"Why does it always start with "I have doubt?""

Tony, after many years of following this forum, I came to the realization that non-English speakers are mis-translating this from what we would say as "I have a question"

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#8

Re: Overload Protection with DOL Starter

05/27/2013 12:41 AM
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11

Re: Overload Protection with DOL Starter

05/27/2013 6:46 AM

MCBs MUST not be used for motor overload protection. The thermal overload protection charactersitics prescribed for MCBs (IEC 898 Curve) are for the protection of cables and NOT for motors. Motors need to follow the IEC 647 Curves for overload protection.

However, MCBs can be used as a back-up switching device cum short circuit protective device - if properly selected.

If your problem is MCB tripping due to the high inrush current and/or the starting current of the motors, then this may be easily overcome by selecting a "D" curve MCB for the purpose.

Pl. learn a bit about the B, C & D Curves of MCBs.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12

Re: Overload Protection with DOL Starter

05/27/2013 11:45 AM

I firmly agree that the demonstrated lack of understanding of basic motor protection and control concepts means that the OP is unqualified to be performing this work.

But for the benefit of the others in our community who can likely argue this ad nauseum, I perceive a possible semantics issue here that the OP may be fostering BECAUSE of his lack of understanding AND use of acronyms.

MCB in North America means Main Circuit Breaker

MCB in most of the English speaking world means Miniature Circuit Breaker

MCB in many non-English speaking countries is often mistakenly used to mean Motor Circuit Breaker, referring to the devices that are a combination of CB and adjustable overload relay otherwise known by many other names, depending on the manufacturer, such as Motor Circuit Protector (which also has a different meaning in NA), Motor Protective Switch, Motor Switch Protector etc.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Overload Protection with DOL Starter

05/28/2013 3:20 AM

The <...misconceptual...> is that of not using the applicable national standard for such things, such as British Standard 7671.

One cannot protect a motor against overload with an MCB for that device is there to protect the cabling downstream. The correct device to protect the motor is a motor overload. The technique needed to get these two to work together in the same circuit is called "co-ordination", the detail of which is all in BS7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#15

Re: Overload Protection with DOL Starter

05/28/2013 12:32 PM

Refer literature from MCB manufacturers like Hager,ABB,Siemens,Schneider/Merlin Gerin etc

__________________
pnaban