Frequent Failure of Lightning Arrester

05/31/2013 5:28 AM

We are having 33/11 KV outdoor substation near mist cooling tower also surrounding is dusty, this makes the deposition of water & dust particles to accumulate over the LA. Hence the LA gets weakening quickly.please any body suggest to change the type of Lightning arrester (LA) according to environmental condition (or) any type of external coating we can do (or) making proper shed will avoid this.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Frequent failure of Lightning arrester

05/31/2013 5:39 AM

Why not deal with the dust instead? If it's affecting the lightning arrestor, then imagine what it may be doing to people's lungs!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#6
In reply to #1

Re: Frequent failure of Lightning arrester

05/31/2013 11:18 AM

I would consider ther OP's handle and expect that the dust they are referring to is from the (natural) environment.

Register to Reply
Member

Join Date: Jan 2013
Posts: 8
#10
In reply to #6

Re: Frequent failure of Lightning arrester

06/01/2013 5:16 AM

try to get enclosed type of arresters or use longer ones than the ones you are using now and also use insulated leads.

thanks

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Frequent Failure of Lightning Arrester

05/31/2013 9:44 AM

Have you contacted the manufacturer? The last thing you should be doing is coating or modifying the sheds.

UK power companies use a high pressure water mist to clean live equipment. You're local power company may be able to do this.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Frequent Failure of Lightning Arrester

05/31/2013 11:07 AM

Go for LA with a higher creepage perhaps!

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: Frequent Failure of Lightning Arrester

05/31/2013 11:14 AM

Find the engineers who decided to put the substation down wind of the cooling towers while being in a dusty location and make them go and clean the LA off once a week wearing a full body HV suit.

It may not fix your problem exactly but I guarantee that from now on the engineers will pay much closer attention to the local wind,atmospheric conditions, and primary systems placements in everything they design for today on!

----------------

The other option is to replace your lead line going to the LA with a section of insulated underground type power line lead then insulate and seal the connection point as well so that the HV has much further to travel before arcing over.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5

Re: Frequent Failure of Lightning Arrester

05/31/2013 11:15 AM

The arrestor is weakening? How are you testing this? Do you mean the lightning air terminal?

All in all, I would refer to NFPA 780-2011 for assistance in choosing the proper materials for the job. Stacks (your cooling tower) are directly addressed in the publication.

Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#7

Re: Frequent Failure of Lightning Arrester

05/31/2013 5:28 PM

Do you mean electrical failure or structural? is the dust insulating the cable or is the dust overloading it?

If there is a chimney upwind, you may have acid forming on the cable. Follow cuba pete's advice, above.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #7

Re: Frequent Failure of Lightning Arrester

06/03/2013 3:33 AM

Never mind the local community's lung damage, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#15
In reply to #13

Re: Frequent Failure of Lightning Arrester

06/06/2013 10:30 AM

I would consider ther OP's handle and expect that the dust they are referring to is from the (natural) environment.

Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#8

Re: Frequent Failure of Lightning Arrester

05/31/2013 11:39 PM

The cooling tower mist is the problem, cooling water chemistry is for the water to coat a surface, the lightening arrestor when new the water will bead on the surface. Sometimes this problem only occurs during some months of the year when the prevailing winds change.

Consider relocating the cooling tower or the substation, there is no other solution. I have seen substation(s) try all kinds of "solutions" to no avail.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply
Participant

Join Date: Mar 2013
Posts: 3
Good Answers: 1
#9

Re: Frequent Failure of Lightning Arrester

06/01/2013 1:46 AM

Hi Sir, You may need to change the brand of surge arresrors because there are various brands. You can look at the Ka rating (increase the lightning withstand fault level from 10ka and move up to 40ka). There are different brands available that have better moisture ingress capabilities and withstand. You could move away from porcelain outer bodies to silicon insulated bodies. Some manufacturers provide a insulated cap that fits onto the surge arrestor. However, surge arrestors all have a lifespan and are subjected to replacement. They are exposed to surges and lightning and are expendable after a given number of years and Live Line Technology are surge arrestors with a replaceable function. These "drop out surge arrestors" are replaceable via a link stick, have live line capabilities and they have decent moisture ingress withstand. This version of surge arrestor is of a great quality and is adaptable to all the brands available on the market. In South Africa, these have been used for years and work very effectively across networks that are largely rural. Eskom, SEC, BPC and Namibian networks all employ them. These drop out surge arrestors cater for frequent surge arrestor replacement for places such as the Congo where there is high lightning densities and intensity. Most surge arrestors in this environment need frequent replacement. There are two versions of the drop out surge arrestor. One unit is placed in a "Firewall" bracket for protection of the overhead line and ancillary equipment such as auto-recloser etc. The "Transformer Combi unit" is a Combination of the (LA) surge arrestor and MV fuse for transformer protection. The units are available from 3,3kv-33kv. All this information is available on the Internet.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#11

Re: Frequent Failure of Lightning Arrester

06/01/2013 5:56 AM

Silicone rubber insulators prevent flashovers under dusty/humid environments. 'Silgard' is the silicone coating that can be applied on already existing porcelain insulators.

__________________
Raghunath
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#12

Re: Frequent Failure of Lightning Arrester

06/01/2013 10:57 AM

You didn't identify the type of surge arrester or the failure mechanism but the best type of arrester to use in a heavily contaminated environment is polymer-housed, gapless metal oxide. Gapped silicon-carbide surge arresters will have some type of internal grading circuit across the gaps to more uniformly grade the line to ground voltage across the gap structure. External leakage currents, due to lightly wetted surface contamination, can upset the internal grading circuit, and cause failure of the silicon carbide blocks. If the external leakage current exceeds about 100 mA, the housing may flashover externally. Check the power frequency withstand of the housing and consider a polymer-housed, gapless MOV surge arrester with the appropriate external leakage distance and withstand.

Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#14

Re: Frequent Failure of Lightning Arrester

06/05/2013 1:17 PM

There is a cover manufactured for the L/A you are talking about. Go back to the manufacturer and they will give you the information for it.

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bluestone (1); CoronaCameraMan (1); cuba_pete (3); electricalexpert65 (1); electrobrains (1); Kevinrisi (1); Munster (1); passingtongreen (1); PWSlack (2); raghun (1); tcmtech (1); TonyS (1)

Previous in Forum: Motor Starting Time.   Next in Forum: How To Find Capacitor Ratting of Water Pump Motor?

Advertisement