relay is micom p343, it suggest that set the voltage threshold, V Dep OC V<2 Set to a value above the voltage measured at the relay and upper voltage threshold setting, V Dep OC V<1 Set, should be set below the minimum corrected phase-phase voltage level for a close-up HV earth fault.
But through this information I am not able to make out. Plz help
104 V as Below 110 can be opted - provided we are not getting this reading in loaded / fully loaded / start up - condition ( normal ) .
120 V as above 110 V may be chosen based on no load / min load condition - being measured in different shift timings .
If volage and upper voltage threshold required for us is being interchanged , overcurrent protection will be activated . In that case , interchange these values as well - please .
Phase to phase voltage if is different , work out the value in a similar way . Regards .