Dear all
in 132kv sub station one phase of the current transformers become damage, this
CT mitsubishi type.
can we replaced this CT with another CT have same (burden,ratio,accuracy)
but ABB type OR must be replace all 3phase
thanks for all
Pathfinder Tags: Replace current transformer
Re: Replace current transformer
06/15/2013 2:00 PM
For accuracy in your measurements, I believe you should replace with a unit of the same type if at all possible. If not you may want to replace all three with the same type. However, for financial reasons this may not be wise. Determine an acceptable percentage of error. Some bench testing may be in order to make these determinations for yourself vice published specs. It comes down to what your acceptable error levels and financial means are.
common knowledge...less common than common sense
06/15/2013 2:07 PM
yes.
No.
Good Answers: 59
Re: Replace Current Transformer
06/15/2013 11:08 PM
You have not the means to bench test and calibrate to the necessary degree of precision.
Replace with the correct model. Or replace the set.
Current transformers are passive elements. They rarely fail. What caused this to get damaged?
06/15/2013 11:16 PM
no need to replace all CTs.. but should have all 3 same burden, ratio, accuracy.. even deferent manufacture .
06/16/2013 12:32 AM
Dear sir what about coil resistance for current transformer
the different effect or not effect
thanks
Good Answers: 59
06/16/2013 12:00 AM
RE #4. Er, a very firm Yes/ No.
If the Current trafo is used for troubleshooting purposes only, and OP can live with its lack of precision, (very) different high frequency response, Yes, ok.
If, on the other hand precision is a requirement, and equal high frequency response wold be nice, the equal or set replacement becomes sensible.
See, it depends.
06/16/2013 11:29 AM
Dear Mr.FADHEL,
YES. You can replace wth adifferent make,provided the burden and other characters are very close and the ACCURACY CLASS is NOT DEVIATED.
DHAYANANDHAN.S
06/16/2013 5:12 PM
You can replace it with a different make, (manufacturer), as long as the ratios match and the burden matches. If you provide the new supplier with the original details they will produce a CT that matches. Be aware, the height and pad mount may differ, so additional connection modifications may be required.
Mitsubishi should be able to provide you a new CT to fit with, and match the existing operation pair, or be able to repair the faulted unit, they normally keep parts and spares. (Unless it blew up and wiped out the porcelain bushing?).
Put a call out as many utilities have a store full of redundant items, they may sell you a CT that is in stock and of no use to them anymore.