Motor Won't Run Under Load

06/20/2013 4:08 PM

I bought a brand new Husky air compressor that was sold as is because the circuit would blow when it was turned on. It has a 110 volt Marathon Electric AC motor. I took the motor apart and wired it correctly because it was wired wrong, and the motor ran perfectly. However, when under load, it just hums and does not run. Even if I just hold the pulley that's attached to the shaft, it won't turn. When I let the pulley go, it starts up and runs again. Does anyone know what might be wrong? The motor looks new and should run, so I am wondering if some other damage was done to the motor when it was run under load previously.

Register to Reply
Pathfinder Tags: motor under load
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
5
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#1

Re: Motor won't run under load

06/20/2013 4:20 PM

Is it a capacitor start motor? if so, then check the conections and that the capacitor is not bad.

If it has a start winding, make sure that the centrifugal switch has the start winding contacts closed and that they will open when you manually actuate (compress) it.

Finally, but rarely seen, check that the rotor (a squirrel cage) bars are skewed and not straight.

All of the above abnormalities will give you exactly the symptoms that you describe.

Good luck

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply Good Answer (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #1

Re: Motor won't run under load

06/20/2013 8:45 PM

Great ideas Yahlasit. I also believe that the starter circuitry, whatever topology, is likely at fault.

I have some serious reservations about the validity of the information the OP has provided us. If this compressor was "brand new" then why was it sold "as is" and who found out that it would blow the circuit to sell it "as is"? What part would regularly blow, the built in circuit breaker or thermal switch on the motor of this compressor? What if the power distribution circuit breaker kept blowing when this compressor was turned ON? How did the OP determine that this motor was miswired and how was the wiring corrected?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Motor Won't Run Under Load

06/20/2013 5:07 PM

You should have both a start and run capacitor....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Motor Won't Run Under Load

06/21/2013 12:26 AM

Take it to a motor winding shop,dismantle and check

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5

Re: Motor Won't Run Under Load

06/21/2013 3:06 AM

could it be a 3phase motor and you have a single phase supply?

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Motor Won't Run Under Load

06/21/2013 10:13 AM

Im with the others on this one. when you say it ran " perfectly'" does this mean you took an amp draw and temperature of the body of the motor or does it mean it just seemed to spin at the right speed?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: Motor Won't Run Under Load

06/21/2013 10:37 AM

Single phase motors by their very nature have low starting torque so it's no surprise that you can hold the pulley with your hand (not a wise idea by the way), so now you have to look at what's at the other end of the belt, the compressor. If the compressor is started against the tank pressure, even if empty, it takes a lot of torque to get it moving.

The way around this is a combination electromechanical control valve that controls the cycling of the motor and contains a valve called an unloader which vents the line from the compressor to the tank so the motor has minimal load on it (equivalent to removing your hand from the pulley). Once the unloaded compressor is rotating fast enough to create a decent pressure the valve closes its vent to the atmosphere and allows the output to go to the tank. I suspect that the unloader valve is stuck in the closed position forcing the compressor to start against pressure, something it won't be able to do.

It's easy to check for though, open the tank vent and and remove anything attached to the pressure port and see if it starts and runs and air comes out. if not then there may be a faulty compressor, an obstruction in the airline, or a faulty controller. It's a electromechanical system, you have to move on from the electrical motor and see if the mechanical side is working properly as well.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
3
Guru

Join Date: Jun 2007
Posts: 1035
Good Answers: 40
#8

Re: Motor Won't Run Under Load

06/21/2013 11:20 AM

As happens all-too-frequently... here is another thread racing off on multiple tangents with a whole lotta "guess-work" going on.

Husky didn't make just a single model of "air compressor"...

Which model of 'oil-free' "Portable" _ or _ "Stationary" ("Husky air compressor") is it...?

Assuming "Stationary" (due to having a "Marathon Electric AC motor"), it should have all kinds of "tear-up-your-hands" if you hold onto the belt (or pulley) start-up-torque.

"Yes", something is wrong. You stated it was purchased "new" (but as-is), AND that the motor "looks new"...(?) Are you thinking it might have been switched-out?

"Specs Ahoy!" More details please! "Shot-gunning" is NOT the way to approach such difficulties.

You "took the motor apart and wired it correctly because it was wired wrong, and the motor ran perfectly"... except under load(?!?) "...it just hums and does not run."

An electric motor that "could be" wired-up to run on either 110-or-220 exhibits an interesting effect IF you wire it for 220 but plug it into a 110 outlet.

It "starts-up in correct rotation and runs just fine" ... UNTIL you place any load on it.

THEN , guess what....................................?????

Done for now.

(Edit / "PS" fashion: I *am* speaking from a bit of experience...)

Register to Reply Good Answer (Score 3)
Member

Join Date: Jun 2013
Posts: 5
#11
In reply to #8

Re: Motor Won't Run Under Load

06/27/2013 1:55 PM

you are right, this motor should have lots of power

it is a Marathon electric model 5KCR48TN2582Y

ithe motor sits on top of a HuskyPro portable 30 gallon compressor tank.

it is definitely a 110 volt single phase motor

I think the capacitors are the problem, and I think they might have been changed by someone else.

I contacted Marathon Electric and gave them the information to see if they could tell me which capacitors should go in this motor, but they have not answered me as of yet.

Register to Reply
Guru

Join Date: Jun 2007
Posts: 1035
Good Answers: 40
#12
In reply to #11

Re: Motor Won't Run Under Load

06/27/2013 3:16 PM

The 'model#' was probably an "OEM_Specific" part-run... (for Husky).

We are all, by now, *assuming* that the motor you are dealing with looks more like the one on the right ("capacitors", plural) than the one on the left (both Marathons).

[[ You *could* start-off such a thread (as I wish that ALL posters would!) with any-and-all complete motor-nameplate data (including hp / rpm!)... as well as the compressor model#... (numerous different motors will be found atop a "30 gallon tank")... and a photo or two...

Here's hoping you get the (combination) "Wiring-&-Capacitors" correct...!

Register to Reply
Member

Join Date: Jun 2013
Posts: 5
#13
In reply to #12

Re: Motor Won't Run Under Load

06/27/2013 4:38 PM

you are right

the motor looks like the one on the right

I still think the problem is with one of the capacitors

and that the capacitors in there are not correct

I have tried to contact Marathon Electric to see if they could enlighten me as to which capacitors should go in there, but I have not been able to get a response from them as of yet

Register to Reply
Active Contributor

Join Date: Jan 2013
Location: Abu dhabi, UAE.
Posts: 21
#9

Re: Motor Won't Run Under Load

06/24/2013 2:30 AM

I would like to about this motor, Please check the manual of the machine. Then check what you done on it. Some time we know something different than what actually inside the manual.

So, you will have an idea about it. As you said that machine is new, it should come with some warranty. If yes, then take to their authorize dealer.

If it is out the time then follow the other procedure....!

__________________
sudhir_g_thombare
Register to Reply
Member

Join Date: Jun 2013
Posts: 5
#10
In reply to #9

Re: Motor Won't Run Under Load

06/27/2013 1:50 PM

the motor is a marathon electric motor

model 5KCR48TN2582Y

120 volt single phase

I also think that the capacitors are the problem but I am not sure that the capacitors in the motor are the correct ones. I think maybe someone changed them before I purchased it.

I have contacted the company that manufactures the motor 2 times already to see if they would tell me which capacitors go in this motor but they have not responded. I think that as a last resort I will take it to a place that fixes motors. I hate to buy a new one because this one starts and works, it just has no power when I put some tension on the pulley.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14

Re: Motor Won't Run Under Load

06/28/2013 1:23 PM

You seem hyper focused on the capacitor issue. it's highly unlikely. If the caps were incorrect, either it would never start, or it would start, but the caps would heat up and pop.

In the realm of troubleshooting, it is always best to BEGIN with the simplest things FIRST, not the more bizarre, because the chances are far greater that the issue is more simple than it is more complex.

Focusing on someone having disassembled the motor, changed the capacitors, and reassembled the motor is far far less likely than what RamConsultant said, that the unloader valve is stuck. To my mind the problem has always been the bad unloader, but someone before you did the same thing, hyper focused on a less likely thing, that the motor voltage was wrong, and tried that first. Then you bought it and the motor voltage WAS wrong, but fixing that did not cure the original problem, that the unloader was stuck.

Marathon would have sold a custom OEM motor like that in lots of 10-50,000 units to Husky for dirt cheap with the expressed understanding that as an OEM motor, they would NOT handle any warranty issues from the field. That would be Husky's responsibility. So your emails or phone calls are going straight to the trash, they are never going to respond to you. If anything, they MIGHT be forwarding this on to Husky, but they are unlikely to respond either. Most likely, the initial problem was found and Husky, like most high volume consumer goods OEMs, determined that it was far cheaper to scrap this than it was to fix it. So they instructed the dealer to smash it and gave them a replacement unit. The dealer however, looking to make more money, sold it "as is" to you; free money. You now own something that Husky and everyone else determined was not worth fixing because of the labor involved. If you can get an exploded parts manual for it and can identify the unloader, and you can buy a replacement or disassemble it to try to figure out what is wrong with it, you might get it working. But the labor and time involved is likely more than the price you paid for it. That's why it was scrapped and should NOT have been re-sold.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#17
In reply to #14

Re: Motor Won't Run Under Load

06/28/2013 4:13 PM

"bizarre" is always so much more fun to uncover!

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#15

Re: Motor Won't Run Under Load

06/28/2013 1:41 PM

Here's a silly idea. Buy a new electric motor. Then you can find out if the air compressor is broken, too.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16
In reply to #15

Re: Motor Won't Run Under Load

06/28/2013 3:57 PM

GA.. it's brilliant....

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Off Topic
Member

Join Date: Jun 2013
Posts: 5
#18
In reply to #16

Re: Motor Won't Run Under Load

06/28/2013 6:21 PM

I have an older compressor where the motor works, so I will replace it with that one. But I know the compressor works because when I first fired it up it ran for about a minute and it did build up compression, so that's why I think it has to be the motor and not the compressor itself.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#19
In reply to #18

Re: Motor Won't Run Under Load

06/28/2013 8:16 PM

Once again the details slowly creep toward revelation. Does the motor die when the compressor tries to exceed tank pressure? What pressure did you achieve in that minute of operation before something stuck? Was that tank pressure ever relieved? Did you measure the inductance of the stator windings? Is the motor an induction or brushed motor configuration? Is there a velocity switch that drops out starter circuitry windings? What does the phrase "sell as is" mean to you?

Oh, I'm sorry but I'm repeating the thread.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (2); Craig Mannor (4); Fredski (2); JRaef (1); ndt-tom (2); pnaban (1); RAMConsult (1); redfred (3); SolarEagle (1); sudhir_g_thombare (1); Yahlasit (1)