How To Figure Amps on 110V 400 Watt Motor

06/22/2013 1:45 PM

I have a servo motor with the model number DOL 88NS. It runs my Overlock stitcher that we use for micro mesh ( plankton nets).

It is 110 V and says 400 watts.

It can go from 0 to 2300 rpms with a turn knob under the table.

I have it plugged into a ground fault breaker that has no more than 10' of 12-2 romex feeding directly into the breaker box on a 15 Amp breaker. Nothing else on that line.

It keeps kicking the Ground Fault only.

When i plug it into another outlet that feeds a small fan, it runs with no trouble.

I need to keep it near the ground fault breaker location as that is where i need to work the machine.

I can not find it on the internet and the company guy I need to speak to will be out until midweek. i need to get this fixed up today so i can start working.

Suggestions?

__________________
There is no recall from extinction.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: HOW TO FIGURE AMPS ON 110v 400 WATT MOTOR

06/22/2013 1:54 PM

any electrician (doest have to be marine) with an amp meter and a VOM should be able to isolate your problem in a couple of minutes of testing

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: HOW TO FIGURE AMPS ON 110v 400 WATT MOTOR

06/22/2013 1:56 PM

You're probably getting some voltage bleed that is tripping the ground fault...I would just work around it...is it a wet location?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: HOW TO FIGURE AMPS ON 110v 400 WATT MOTOR

06/22/2013 1:59 PM

I=V/R will get you there

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: HOW TO FIGURE AMPS ON 110v 400 WATT MOTOR

06/22/2013 2:12 PM

That's less than 4 amps. Something else is tripping the GFCI.

I highly recommend one of these circuit testers.

Read what Wiki says. I've got two of these. They're great for quicky checking.

A receptacle tester being used to verify the proper wiring of an outlet. For this particular tester, proper wiring is indicated by the two yellow lights.

The much more important role of the outlet tester is to not only verify that electricity is present in the outlet but that the outlet is properly wired, with each plug being connected to the proper wire in the building's wiring. There are two primary reasons for testing

IDEAL INDUSTRIES, INC. - E-Z Check® Circuit Testers

Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#17
In reply to #4

Re: HOW TO FIGURE AMPS ON 110v 400 WATT MOTOR

06/24/2013 10:47 AM

Be sure to get the one with a GFI test button. If it works, the problem is with the motor. Has nothing to do with total amps, but miliamps to ground (not neutral. No, ground and neutral are "not the same") -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#5

Re: How To Figure Amps on 110V 400 Watt Motor

06/22/2013 2:14 PM

Current should be less than 4 amps (400W divided by 110v), but it's the leakage that's tripping it.

Maybe it's the mains noise supression components (capacitors from live to ground and neutral to ground) that are doing it.

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#6

Re: How To Figure Amps on 110V 400 Watt Motor

06/22/2013 2:26 PM

I don't know what you mean by servo motor, but if it has carbon brushes and you used it for a long time, the carbon dust, accumulated on the holders, to the ground can make your motor ground fault trip also. In this case blowing it clean inside with compressed air might solve the case. An other scenario can be caused by the isolation of the coils shellack. This motor should consume about 400/120 =3.3 Amps.

__________________
Plenty of room here
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7

Re: How To Figure Amps on 110V 400 Watt Motor

06/22/2013 2:46 PM

It's current leakage from the hot wire to ground that's causing the trip, not an over current condition. If I had all of the toys from work I would perform a high pot test between the black (hot) lead and chassis to look for a leakage path. Without that tool, I would examine the wiring to see if anywhere the black wire insulation is cracked, pinched or otherwise compromised. I would also use some canned air to clean out the brush dust.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#8

Re: How To Figure Amps on 110V 400 Watt Motor

06/22/2013 3:34 PM

Besides all the other answers, it could be a bad breaker. I had this problem with some old Federal-Pacific GFCI breakers.

It keeps kicking the Ground Fault only. Do you have another GFCI circuit that you could try it on? If it trips another one, your stitcher is faulty. If not, your breaker is probably bad.

Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#9

Re: How To Figure Amps on 110V 400 Watt Motor

06/22/2013 4:00 PM

If the GFI is tripping, you have a potentially lethal situation. GFI's do not trip because of over current, they trip because of a difference in current between the white and black wires. Follow Redskis advice below.

If you really, really need to work. Wear dry clothes and dry tennis shoes. Preferably long sleeves and pants. Place the machine on dry auto floor mats. You should be standing on dry plywood. Did I mention "dry".

This should keep the GFI from tripping, until you can get it corrected.

Register to Reply
Associate

Join Date: Nov 2007
Posts: 53
Good Answers: 1
#16
In reply to #9

Re: How To Figure Amps on 110V 400 Watt Motor

06/24/2013 12:16 AM

The GFI balances the input current to the device against the return current from the device. A leakage path that causes these currents to be unequal will cause the GFI to trip with current differences in microamps. Providing a separate ground to the machine and bypassing the GFI would probably get you by, but I can't recommend it, especially without knowing more about the installation...Clint

__________________
Clintb3252
Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#10

Re: How To Figure Amps on 110V 400 Watt Motor

06/22/2013 11:15 PM

There are few simple ways to know if motor is leaking current to ground or has some poor connectivity node in the power paths.

1) Measure voltage at the mains distribution point and then across the plug which feeds the motor controller. The voltage need to be within 0% to 1% (on high side) error at best.

2) Measure current in live wire Li and also in neutral wire Ni separately and see of Li > Ni. If Current difference is significant then somewhere either in the controller or in the motor current is going through Ground path which should normally have near zero current.

3) If you have ground / earth connected to the controller and if its harmonic filters are finding differential power harmonics over live and neutral lines then they will run this current into earth / ground path also if filter is wired to earth line also. However, this part can be investigated by looking into internal diagram of the controller's technical manual.

Good luck.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
3
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#11

Re: How To Figure Amps on 110V 400 Watt Motor

06/23/2013 6:33 AM

It's not clear to me you've gotten a correct answer so far. First, as several have stated, it's not your motor's current or the controller's current, per se, that's tripping the GFI. That's because this current is normal mode, whereas the GFI protection is looking to trip on common-mode currents. The GFI looks to see if the sum of the current in the two wires, hot and neutral, is zero. That is, the same current returning on one wire as going out on the other.

Several have speculated that it's leakage current, which would unbalance the two wire's currents and lead to a non-zero total. But this is almost certainly not the case. Enough leakage current would certainly trip a GFI, but it's very unlikely you have such leakage current. Instead you're experiencing a common mismatch between GFI units and switching power supplies.

Switch-mode power supplies (smps) are noisy beasts. That is, their fast-rising multi-hundred-volt switching edges creates RFI, or radio-frequency interference. To keep from injecting this interference back into the AC line (and upsetting the FCC), smps modules include an AC RF input filter, as shown in the figure. The filter elements are a common-mode transformer, and an L-C stage. Innocent enough. But the dangerous item in the RFI filter, which concerns us with GFI protection, is the two capacitors to ground.

When you throw the power switch, these capacitors have to be instantly charged to AC line voltage, whatever it is at that point. If it's near zero, no problem. But if it's very high, or near the peak, the quick current surge to ground will be quite high. This is what trips the GFI. Once the circuit has stabilized, and the filter capacitors are following the ac sine wave, their ground current drops to a low value that's not troublesome.

If you reset the GFI and try again most often you'll be fine. Sometimes it may take two tries to get lucky. It may be irritating, but it's not dangerous, and technically-speaking, nothing is wrong either with the GFI or the motor controller's power supply. We could fault the GFI for tripping on such a short pulse of current, but then we want it to be sensitive, don't we? We could fault the smps for having too large filter capacitors, but we don't want it to inject loads of RFI noise into the ac line, do we?

Your servo motor and its controller no doubt are very well insulated, and it's clear they were not designed to be operated from a GFI outlet. That mismatch is what's at fault. Plug your servo system into an ordinary AC outlet, or put up with the extra efforts to get it started.

__________________
Thanks, Win
Register to Reply Good Answer (Score 3)
2
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#15
In reply to #11

Re: How To Figure Amps on 110V 400 Watt Motor

06/23/2013 4:48 PM

I saw lyn's comment on confusion. I'm sorry my answer was confusing. But I know my answer is correct, because I've experienced the problem multiple times and have therefore researched its engineering background.

I'm fortunate to have a very nice large Electronics Engineering Laboratory at the Rowland Institute. However it was originally constructed as a chemical lab, complete with setup benches and fume hoods, both with sinks and running water available, and other types of grounded piping. The ac outlets at these spots all have GFI circuit breakers, as is the rule and appropriate. I've not seen fit to replace the GFI breakers with ordinary ones, so we live with the consequences.

Virtually every computer, printer, etc., we plug into these outlets occasionally trips its GFI. We removed one fume hood, but kept a second one to house a 35-watt Epilog laser cutter (very useful, recommended). That beast trips the GFI all the time! Throw its switch, "click" comes from the breaker panel. Sheesh!

Anyway, the cause is very simple: the filter capacitors to ground in the ac offline switch-mode power supplies in these devices, as I detailed in my post.

And my suggested workaround is also very simple, use a regular outlet, or just keep on resetting the GFI.

(Maybe somebody will come along and tell us they've found a brand and model of GFI that's not susceptible to the issue, that'd be nice!)

My point was that there's likely no dangerous defective leakage to ground, which the GFI was designed to detect. Of course, the offending instrument, computer, or machine could be defective, it's possible I suppose, but if it was, it would trip the GFI every time, and furthermore the GFI would refuse to let the device start and continue running, ever! That's a different symptom from the one the O.P netmaker and I described.

As far as the CR4 electrical engineering community is concerned, we should all be aware of this GFI - switch-mode-supply mismatch, subtle as it is, because we could encounter it any time, and we will do so more often as time goes on and smps are more commonly used. Perhaps I should add, it's usually the larger power supplies that employ the two ground capacitors in their RFI filter. Smaller supplies, below 25 watts, etc., can pass the required FCC tests without any such capacitor, so they don't use them and they therefore have no danger of tripping a GFI.

I poked around a bit with Google, and I must say, there's a huge amount of misinformation out there over this issue. Folks struggling with microwave ovens in their kitchen, all types of experiences, asking what's up? and getting wrong answers!

__________________
Thanks, Win
Register to Reply Good Answer (Score 2)
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#12

Re: How To Figure Amps on 110V 400 Watt Motor

06/23/2013 7:16 AM

Your problem is not the amperage! Your motor has a high leakage current that trips the GFI.

If you have an isolation transformer on hand, with a size or capacity of more or less about 500 VA, you can use that temporarily. Plug your servo motor into it then plug the transformer to your GFI outlet. The isolation transformer will solve your high leakage current problem..

Remember the isolation transformer you need to use must have a 1:1 turn ratio meaning, it has the same input and output voltage rating!

Good luck!

__________________
vsar
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#18
In reply to #12

Re: How To Figure Amps on 110V 400 Watt Motor

06/25/2013 8:01 AM

Yes, an isolation transformer between the GFI and your servo system should take care of it. A 1KVA would be my choice.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13

Re: How To Figure Amps on 110V 400 Watt Motor

06/23/2013 9:03 AM

I'd say that we've managed to confuse and befuddle the poor OP with all our collective intellectual one upmanship, again.

The contributions of Shyam and Winfield Hill are especially confusing, especially to a simple fisherman. While I certainly don't suggest that either contribution is wrong, I do suggest that they are way too technical for the our friend who is seeking help.

It seems to me that through it all, what we have here is failure to communicate, again.

I'll save you all the trouble of voting this OT.

Register to Reply Score 2 for Off Topic
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#14

Re: How To Figure Amps on 110V 400 Watt Motor

06/23/2013 1:55 PM

In case it didn't filter through the verbiage, the GFI checks that the current that comes in on the hot (small blade) side goes out on the neutral (large blade) side. If there is an imbalance, it shuts the outlet down. The amount of the imbalance (the leakage) could be lost in an inside short and escaping down the grounding pin or externally by any of the several methods described in the posts above. This seems to imply that the leak is in the equipment or the wiring.

As someone said, another possibility is that the fault may be in the GFI.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: Cajun Country , USA
Posts: 1498
Good Answers: 23
#19

Re: How To Figure Amps on 110V 400 Watt Motor

06/26/2013 9:06 AM

Thank you all for the lessons in current. Yes, some were very much over my head.However, I sifted through enough of this to solve the problem.

My old stitcher ran off this Ground fault outlet for about 6-7 years. The Motor was belt driven and was about twice as large as this one.

THIS motor is smaller, has no belt and has a rheostat that lets me set the rpms from 390 to 2100.

The machine is larger and judging by the power it has to ram a 80mm steel needle through a 4 ply layer of 1000 denier netting, I'd say it was twice as strong.

To solve the problem:

I simply ran a separate line from my meter box to the machine. Its on a 20 amp circuit with just a 2 amp fan. the machine itself has a fused connector.

I never work on anything wet and the machine is on a plywood floor. It runs top end now.

Thank you all. I may never really know what caused the GF to trip, but I have more of an understanding about what 'could' cause it to happen. Our work is about 70% hand sewn large mesh nets, 20% micro mesh 12mm through 750µ ( sewn only on the stitcher) and 10% rope and cable splicing. With this new stitcher , me and the wife can increase production time on those micro mesh nets, and take in more work in that area. the old machine was just plain worn out and slow.....like me!

Once again, another lesson learned from the CR4 Ol' Skool gang!

Thank you all again.

__________________
There is no recall from extinction.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#20
In reply to #19

Re: How To Figure Amps on 110V 400 Watt Motor

06/26/2013 9:10 AM

nice post

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#21

Re: How To Figure Amps on 110V 400 Watt Motor

07/01/2013 9:58 PM

Had similar problem with the GFI that was feed an outlet in my garage and three bathrooms. It would always happen after a storm with lightning and heavy rains with a high humidity.

The wire went from the panel box to the GFI located in the garage and then to non GFI outlets in the baths. For one of the baths I ran wiring through the basement to the bath and installed its own GFI. For the one bath on the 2nd for I did the same but through the attic. Couldn't do the for the other 2nd floor bath because the wiring was located on an outside wall, had a mirror adjacent to the outlet and most of all I couldn't get to above it due to the angle of the roof. What I did for that was change from feeding from "through the garage GFI" to feeding it and a GFI that replaced the duplex outlet in the bath in "parallel". Found out before this that the GFI was tripping due to spurious electrical pick up on the long length of wiring after the GFI. Now all the sockets are GFI and I haven't had one trip since the changes were done.

This problem was most inconvenient when the wife would wake me up on a cold early morning saying that her hair dryer didn't work. I would then have to go down to the cold garage to reset the GFI!

Locate your GFI closer to the machine. Preferably use it as the outlet that you plug your machine into.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#22
In reply to #21

Re: How To Figure Amps on 110V 400 Watt Motor

07/02/2013 9:37 AM

Like yours, I have a GFI equipt outlet in the garage that also feeds power to 4 other external outlets that are around the outside perimeter of the house.. Even those outlets were not being used, I found from time to time that GFI trips! To stop any unnecessary tripping of that GFI, I separated or isolated the wires coming out of the GFI that feeds power to the outside outlets from the others. I relocated them the away from the rest of the house wiring. In my thoughts by doing so, I will minimized stray capacitance between other house wires, which in turn should lower corresponding leakage currents. So far it seems to work since no more annoying and unnecessary power interruptions!

__________________
vsar
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#23
In reply to #22

Re: How To Figure Amps on 110V 400 Watt Motor

07/02/2013 11:51 AM

Yes, "If it works, don't fix it". You've got the problem solved and your solution sounds good.

After I did these wiring changes, and after a sufficient length of time to see that the problem was fixed, I asked two neighbors about the problem and how they would solve it. Neighbor #1, the PhD in EE, had no realistic solution except if I rearranged the electrons as they traveled through the protons in the copper of the wires. Neighbor #2, the electrician, told me what the problem was, how to fix it and kidded me for asking him such a silly question. When I told him that's what I had done he said I owed him not a can of beer, his usual rate for consultations, but a 6-pack for asking dumb questions that I already knew.

Yes, common sense solves most things.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bigg (1); Circuit Breaker (1); Clintb32 (1); dvmdsc (1); Fredski (3); JWthetech (1); lyn (2); netmaker (1); NotUrOrdinaryJoe (1); old salt (2); passingtongreen (1); redfred (1); Shyam (1); SolarEagle (1); user-deleted-1105 (1); vsar (2); Winfield Hill (2)

Previous in Forum: Heavy Floods in Utrakhand, India   Next in Forum: Belmont Barber Chair

Advertisement