As i know power factor formula = kwh/kvah = active/reactive power.
But Ethiopian Electricity Board calculate power factor as following
PF = Cos (Inv.tan (Reactive/Active)).
Kindly reply with full details.
Re: Power Factor formula
06/24/2013 4:03 AM
They are two expressions of the same thing.
06/24/2013 2:31 PM
Good Answers: 42
Re: Power Factor Formula
06/25/2013 9:59 AM
If we shall measure the voltage and the current with an oscilloscope we shall get a curve representing voltage and current wave and we shall see an angle between these two curves. cosinus of this angle-fi=(volt,current)- will be the p.f.[power factor]=cos(fi).
kwh=active ENERGY [measured by kwh meter (monitor) and not by wattmeter!]
kVArh=reactive energy[could be measured on a kVArh monitor]
kVAh=apparent ENERGY[usually it is not measured]
kwh=Volt*Current*cos(volt,current)*hour [for a steady-state load]
kvarh=Volt*Current*sin(volt,current)*hour
kVArh/kwh[reactive energy/active energy]= Volt*Current*sin(volt,current)*hour/Volt*Current*cos(volt,current)*hour=
sin(fi)/cos(fi)=tan(fi).
arctan(fi)=Inv.tan =fi. That means p.f.=cos(fi)=cos[Inv.tan(reactive energy/active energy)]
Julius
06/26/2013 5:30 AM
The first Equation power factor formula = kwh/kvah = active/apparent power