Anonymous Poster #1

HVAC TQ - Valve

06/25/2013 9:52 AM

Dear FRIENDS....

I have some questions....

1.what is TQ valve?I telling something.......It is using in CARRIER 30GX & 30HX Chiller.......how is it operate????

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: HVAC

06/25/2013 10:09 AM

it makes water cold

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: HVAC

06/25/2013 11:08 AM

1) what is TQ valve? Electronically controlled expansion valve.

how is it operate????

It operates electronically.

Carrier 30gx chiller - free eBooks download - GoBookee.net

Do some research!!

Reply
Anonymous Poster #2
#3

Re: HVAC

06/25/2013 2:59 PM

Looking at the Danfoss diagram on page 8, I don't see how superheat is measured. At least they are not showing it as an input to the controller. Maybe that's too much detail.

I worked with experimental electronic TX valves ~1979 from Singer (heat pump research). These were for small tonnage systems. It used a thermistor to measure superheat. And 24VAC was system voltage. I looked back a few years ago, and it looks like these never made it to market.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: HVAC TQ - Valve

06/25/2013 4:39 PM

In one implementation I saw (quite some time ago) the superheat was measured by comparing the readings of two 1000Ω platinum RTDs, one where the refrigerant piping enters the evaporator and the other where the refrigerant leaves the evaporator. Low superheat (~2°C) could be maintained.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster #2
#5
In reply to #4

Re: HVAC TQ - Valve

06/25/2013 10:56 PM

I would think they would integrate one of the thermistors in the valve. What really is confusing is the equalization pressure line, in the document say's to connect near the valve output, not where the superheat is measured at the evaporator output, this makes no sense. Which is probably why the OP is asking.

Does this valve control constant superheat, or is it controlling some full flooding of the evaporator, like a low side float system. The text indicates controlling real small superheat values. I would assume there is a suction accumulator to prevent liquid slugging the compressor.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: HVAC TQ - Valve

06/26/2013 10:17 AM

The tech sheet doesn't show what is attached to the controller, such as possible temperature sensor(s).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.