We have a battery bank of 104 number of cells of pocket type filled NiCad battery, connected in series with each cell having voltage 1.4Vdc and and an overall voltage of 147Vdc. The bank is placed in a cabinet in a hall with a temperature of around 35~40deg C during peak summer. The bank is kept on float charge at 147.0Vdc thru' a PLC controlled battery charger. Monthly maintenance of the bank is carried out which includes topping up electrolyte level with distilled water, taking per cell voltage (in connected position) and overall cleaning. Recently white crystal like deposits around the vent caps have been observed. Not around the +ve/-ve terminals but around the cap only. Searching on the internet I found that these are Potassium Carbonate crystals formed due to the reaction of electrolyte (KOH being released alongside Hydrogen and Oxygen) with CO2 in the air. These can be cleaned with a damp cloth easily but what concerns me is this is becoming a regular feature. Every time after cleaning, the deposits appear again in 3~5 days. The charging voltage is same (147Vdc) and the charging current is so small that it does not register on the clamp meter so i don't know what the charging current actually is even if it is in milliamps. There are 4 separate units of such battery bank under same conditions of temperature and charge but the white deposits are appearing frequently on only one particular bank only. I want to know why? Are the batteries damaged? Do they need to be replaced? Are they being overcharged? if yes then how? Ive guessed my own reasons for the formation of these deposits, don't know if they are correct though, i would love to know what do you people suggest.

Another issue in a separate battery bank of same type as above is that one of the cell shows 0.45Vdc instead of 1.4Vdc. Its electrolyte level also does not drop like other cells which means it is not being charged, though the entire bank is on float at 147Vdc. Should that damaged cell be removed till a new cell is installed otherwise it may become a load onto itself and drain the rest of the bank? or should it remain connected till new cell is installed?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Questions regarding pocket type filled NiCad batteries

06/28/2013 2:15 PM

The excessive crystal formation probably due to outgassing caused by overcharging....bad cell in bank, ok till changeout...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#2
In reply to #1

Re: Questions regarding pocket type filled NiCad batteries

06/28/2013 3:09 PM

Overcharging how? The charging voltage is 147Vdc, same as for other banks, while charging current less then 0.1 Amp. And crystal formation is not only in one cell but in 50% of the cells out of 104.

Even if the reason is bad cell so do you mean just one bad cell or several? and how do i determine that which cell(s) is/are bad? per cell voltages of each cell 1.4Vdc, specific gravity of the cells is between 1180 & 1220 and electrolyte drop does occur in the cells which we check every month.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #2

Re: Questions regarding pocket type filled NiCad batteries

06/28/2013 6:11 PM

The crystals are formed from the electrolytic fluid....This is most common due to overcharging where the fluid is boiled out, and may be an intermittent occurrence.....I would explore the possibility of replacing the charger, if it is a real problem... In a battery bank such as this, the single bad cell is ok to leave until battery changeout, it will not effect the other cells...

http://www.davidsonsales.com/docs_pdf/NCPPO&Manual.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#10
In reply to #5

Re: Questions regarding pocket type filled NiCad batteries

06/29/2013 7:08 AM

What i thought was the reason for recurring crystal formation was the absence of rubber seal around the vent caps. Most of the vent caps are missing these rubber seals or some of them have it broken. Now what i think is that the electrolyte vapors evolving escape through the broken or absent seals and convert to carbonate on exposing to air and deposit around the caps. If the seals were there intact, the evolving electrolyte vapors would try to pass through the vent caps instead of opening thru the seals. These vent caps have plastic particles in them which would stop the electrolyte from further passing and send it back inside the cell to rejoin the electrolyte body. Only H2 and O2 would escape.

About the charger replacement, what fault could it have when the charging voltage and current levels appear constant?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Questions regarding pocket type filled NiCad batteries

06/28/2013 3:23 PM

I thought that NiCd cells needed to be discharged quite far before recharging them, or else they developed a "memory" that would "let" them discharge only partly. In other words, not suitable for trickle-type charging.

(Unless I am confusing these with another battery type or am out of date.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#4
In reply to #3

Re: Questions regarding pocket type filled NiCad batteries

06/28/2013 3:37 PM

I thought there was no such thing as 'memory' of battery, not that the manual says anything like that a...anyway, the batteries are not on recharge. They're tested once a year on load till their voltage drops to 1.0V/cell. Then they are put on boost charge till completely charged. For the remaining period the bank is on float charge on 147Vdc charging voltage and less than 0.1 Amp charging current.

What about my second query about the damaged cell at 0.45Vdc. Is it okay to be connected in the bank or should it be removed to protect the remaining cells in the bank?

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#6
In reply to #3

Re: Questions regarding pocket type filled Ni Cad batteries

06/28/2013 7:49 PM

Lyn your correct on memory. In the 1st post I noticed that they are refilling Ni cads with electrolyte? Never heard of Ni-Cads that need this? They are normally sealed as far I as know.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7
In reply to #6

Re: Questions regarding pocket type filled Ni Cad batteries

06/28/2013 9:27 PM

The NiCad chemistry isn't limited to sealed batteries. and wet chemistry cells don't have the same charge/discharge limitations that small, sealed, paste type do, especially the memory effect. Take a look at these:

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#8
In reply to #7

Re: Questions regarding pocket type filled Ni Cad batteries

06/28/2013 10:41 PM

Well as I have said many times in the past, your never to old to learn something new. Thanks RAMConsult

Register to Reply
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#9
In reply to #6

Re: Questions regarding pocket type filled Ni Cad batteries

06/29/2013 6:56 AM

Refilling NiCads with distilled water, not electrolyte!

Register to Reply
Commentator
Pakistan - Member - New Member

Join Date: Dec 2007
Location: PAK
Posts: 68
Good Answers: 1
#11
In reply to #3

Re: Questions regarding pocket type filled NiCad batteries

06/29/2013 7:26 AM

Does that mean that the batteries should deep discharged and that too frequently to avoid the memory affect? But the manufacturer manual does recommend float charge.

And as i said, these are tested once a year till discharged to about 1 volt per cell and they seem to be performing satisfactorily.

Register to Reply
Commentator

Join Date: Nov 2008
Posts: 80
Good Answers: 4
#12

Re: Questions Regarding Pocket Type Filled NiCad Batteries

06/29/2013 1:55 PM

Question on using the clamp meter for measuring current. Are you using a clamp meter that can measure DC current. Most clamp meters can only measure AC current. In my 40+years in the electrical trade, I have only seen 1 clamp meter that could measure DC current, and then it was used to measure larger currents. Most good multimeters have a 10 amp DC current function, but this has to be inserted in the circuit. If some of the cells are shorted, then the voltage across the other cells will be higher. I would check the voltage across each cell individually to check for overcharging.

Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#13
In reply to #12

Re: Questions Regarding Pocket Type Filled NiCad Batteries

06/29/2013 4:12 PM

You need to check out what is available nowdays.

DC clamp meters are available, reasonably-priced, and can be accurate down to currents of less than an amp.

__________________
paulusgnome
Register to Reply Off Topic (Score 5)
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

fixitorelse (2); Paulusgnome (1); RAMConsult (1); rizwan (5); SolarEagle (2); Tornado (1); vtbgiraud (1)

Previous in Forum: Transformer Tripping Problem   Next in Forum: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

Advertisement