How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

06/30/2013 3:44 AM

Hi

My client has a UPS of 10kVA which feeds a UPS DB of outgoings of 20A 3P 8No.s, now they have asked me to determine the incomer breaker ratings, no more data/information has been passed, can you please suggest how to determine the same with calculations how to do so, i very much appreciate that.

thanks& regards.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#1

Re: how to calculate Incomer Breaker sizing for a 3phase 4 wire 415V 50Hz UPS DB

06/30/2013 4:31 AM
Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: how to calculate Incomer Breaker sizing for a 3phase 4 wire 415V 50Hz UPS DB

06/30/2013 8:59 AM

a breaker protects wire from carrying too much current.....start there then move to the loads and their expected amperage draws, you're protecting wiring not machinery with a breaker

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: how to calculate Incomer Breaker sizing for a 3phase 4 wire 415V 50Hz UPS DB

06/30/2013 10:13 AM

Give your client their money back and admit that you are incompetent.

Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #3

Re: how to calculate Incomer Breaker sizing for a 3phase 4 wire 415V 50Hz UPS DB

06/30/2013 10:15 AM

haha

Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

06/30/2013 11:25 AM

The given numbers don't match up well. The 10kVA UPS will produce about 14A, so how will that support (8) 20A outgoing feeders?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#6

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

06/30/2013 1:12 PM

Are you not supposed to ask the correct questions being the designer/ installer of the system. There are very many pertinent data you have to submit before you can expect forum experts to offer the answer. How about getting data of required battery back up capacity and the charging voltage for a start?

Reply
2
Participant

Join Date: Apr 2013
Posts: 2
Good Answers: 1
#7

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

06/30/2013 10:28 PM

Hi

You need to check the manufacturers specification of the UPS to find out what the max input current is for worst case (i.e. supplying load and charging batteries following an outage). The manufacturer will often specify an incomer CB size in the installation manual.

You will also need details of the cable between the incomer CB and the UPS to ensure that you are protecting this correctly. Also please be aware of the prospective short circuit fault current at the location and ensure that the CB is rated to break this.

Reply Good Answer (Score 2)
Anonymous Poster #2
#8

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

07/01/2013 12:30 AM

Dear All

Simple thumb rule is current drawing capacity is 18 Amp.for 3-phase system.So take 32 Amp 4- pole ,is appropriate for its incoming rating.

Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#10
In reply to #8

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

07/01/2013 3:07 AM

The OP has not specified whether it is online or offline UPS, the power factor, crest factor, short term overload capacity of UPS, % Harmonics as per UPS vendor specification, peak charging current from dead charge, voltage at which charging takes place, % efficiency of the UPS, prospective fault current at both incoming and outgoing side, provision of double wound isolation transformer etc. As a designer/installer (client relationship), he is supposed to drive all these parameters and incorporate in the design. Very unfortunate that he is clueless about what is needed. In fact I am not sure whether he is asking how to determine the rating of UPS incomer switch or incomer rating of UPS distribution DB. Also as stated by other peers in the thread, the 8 Nos. 20 Amps TP outgoing MCB of UPS DB defies logic. Also not sure whether it Harmonic immunised series MCB and whether the neutral bus and conductors are rated for twice the current rating of main phases.

Impossible to be of help with such pathetic inexperience.

Reply Score 1 for Good Answer
Member

Join Date: Jun 2013
Posts: 5
#9

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

07/01/2013 2:05 AM

Your question is full of question mark. How can the incoming only 10kva only which required to serve 8 outgoing. Please be more specific.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

07/01/2013 4:43 AM

British Standard 7671 again. <sigh>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Jun 2013
Location: LAGOS (NIGERIA)
Posts: 4
#12

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

07/01/2013 5:41 AM

From the data provided by you the 3phase 415VAC 10KVA power inverter will draw about 14A @ 415VAC and unity power factor. For you to get the MCB size @ input side, multiply 14A by a factor 1.5. That gives you 21A. As you know already, there is no 21A conventional MCB. So, go for a 25A MCB with 4poles. As for the battery charging and outage conductor, use a 25mm2 flexible copper type. That solves your problem. However, you have work to do on the DFB. Use your Clamp meter to pick the loads at startup, ramp up, and the continuous modes respectively. Multiply your ccontinuous load results each by a factor 1.35. That helps you to professionally select MCB sizes per load

Reply Score 1 for Good Answer
Participant

Join Date: Jun 2013
Location: LAGOS (NIGERIA)
Posts: 4
#13

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

07/01/2013 6:09 AM

Otherwise, if what you meant is the incomer at the UPS incomer, the average current per phase of a 3 phase 10KVA UPS is 14A @ 415VAC and unity power factor. Be professional in your choices. Forget the already existing UPS DFB MCB ratings of 20A each, 8 nos. Your incomer must not be more than 16A 3poles. So, total load per phase must not exceed 14A. Infact, you must not load the inverter beyond 80percent of 14A so that overload circuits don't respond too often. Please, do away with those junks of unreasonable MCBs. Make sure you properly distribute and balance the loads, so as to avoid line imbalances.

Reply Score 1 for Good Answer
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#14

Re: How to Calculate Incomer Breaker Sizing for a 3 Phase 4 Wire 415V 50Hz UPS DB

07/02/2013 9:16 AM

For 10 KVA UPS the out put current would depend upon UPS output voltage.

is output 3 Phase 380V / 400V / 415V etc.....

__________________
When was last time you did something for first time.
Reply
Reply to Forum Thread 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); BOLARINWA GBENGA J (2); Craig Conlan (1); Fredski (2); Happy singh (1); Lek (1); lyn (1); nobodysomebody47 (1); Pattabhiraman (2); PWSlack (1); Tornado (1)

Previous in Forum: Questions Regarding Pocket Type Filled NiCad Batteries   Next in Forum: Parallel Operation

Advertisement