during parallel operation of generators why slightly high incomming speed and voltage?

what is the reason?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Parallel Operation

06/30/2013 10:55 AM

Because as the incoming generator takes on load, its speed and voltage will decrease slightly to match the other generators.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor
Engineering Fields - Power Engineering - Thermal Power Plant Electrical Engineer

Join Date: Sep 2010
Location: INDIA
Posts: 18
#2

Re: Parallel Operation

06/30/2013 4:20 PM

Voltage and speed should be higher...Because current flow will there when there is a potential difference, in order to maintain it voltage will set somewhat higher than grid valve before sychronization.