Tap Changing Transformer S.C Voltage

07/04/2013 6:50 AM

"Die Umschaltung darf nur im abgeschalteten Zustand erfolgen. Die Spannungsunterschiede, z. B. 20800 V-20000 V= 800 V, entsprechen der Kurzschlussspannung des Drehstromtransformators."
in a german book it is written (above) that the level difference in a tap-changing transformer is equal to the short circuit voltage (% 4,1 İS written on the plate of the xformer) of the xformer.
I am surprised to see this. What is the reason if so?

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Tap Changing Transformer S.C Voltage

07/04/2013 10:08 AM

"...I am surprised to see this. What is the reason if so?..."

1. Why are you surprised to see this?

2. What is the reason why you are surprised?

Perhaps you should tell us what your issue is with the original German, we cannot read your mind (there are other forums for that).

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Anonymous Poster #1
#2
In reply to #1

Re: Tap Changing Transformer S.C Voltage

07/04/2013 10:33 AM

Be simple and brief.

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#4
In reply to #1

Re: Tap Changing Transformer S.C Voltage

07/04/2013 8:24 PM

reply 1: I read for the first time as I implied above the relation between voltage levels of a tap change levels and short circuit voltage

reply 2: the same words mot-a-mot as the ones written above...

__________________
jinxnao
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#5
In reply to #1

Re: Tap Changing Transformer S.C Voltage

07/04/2013 8:26 PM

by the way, I had explained what these lines narrate in my original post. I guess you did not understand what I wrote.

__________________
jinxnao
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#7
In reply to #5

Re: Tap Changing Transformer S.C Voltage

07/04/2013 11:50 PM

Do you expect us members of this forum to understand French , German, Russian, Chinese , or Hindi? Most of us understand English only. So we expect you to explain your question in English please( if you do not mind) otherwise we cannot reply.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Tap Changing Transformer S.C Voltage

07/04/2013 1:16 PM

Do you know what the %Z means or how this value is determined?

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#6
In reply to #3

Re: Tap Changing Transformer S.C Voltage

07/04/2013 8:29 PM

exactly know. Just can not see why we must select the magnitude of the levels of the tap changing system since we change it in no-load condition. Even in under load condition it would be not reasonable to make this design since I can not see a relation between these two issue. (s.c voltage & tap levels)

__________________
jinxnao
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Tap Changing Transformer S.C Voltage

07/05/2013 12:49 AM

Your translation from the German, "... that the level difference in a tap-changing transformer is equal to the short circuit voltage.."

Google's translation, "...May only take place in the off state, the switchover. The voltage differences, eg 20800 V-20000 V = 800 V, corresponding to the impedance voltage of the three-phase transformer..."

Don't know how old the book is, but I suspect it's a typo, the missing word is "unterschied" or "differenz", difference in English; i.e., "...corresponding to the difference in the impedance voltages between taps ..." If it's a modern book contact the author and report back what he said.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#11
In reply to #8

Re: Tap Changing Transformer S.C Voltage

07/08/2013 8:37 AM

I agree with RAMConsult. This isn't talking about the transformer impedance, but about the difference in voltage between the taps of the no-load tap changer. It would help if you provided a bit more of the quote, to show what is said next. From what I interpret (my German is limted and rusty, but my NLTC knowledge is sufficient), this is a warning not to change the NLTC taps while energized. Of course, you do know why this is so, correct??? The contacts of the NLTC are not designed and constructed to make and break the load current of the transformer.

I think your reference to the transformer impedance is throwing you off. When I did a Google translation on this, the terminology that comes out is "short-circuit voltage." There does not appear to be a direct reference to the impedance here. The danger with switching the NLTC under load is that the arc drawn would first be due to the load current across the opening contacts of one tap. Then, if the switching action continued, this could escalate to a turn-to-turn short between taps, at the associated voltage difference between taps. Not a pretty thing.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#9

Re: Tap Changing Transformer S.C Voltage

07/05/2013 4:33 AM

excuse me, Forgive me if I am wrong but my german is well enough. This passage states that the difference between primary voltage tap-changing level magnitude = 800 volt is equal to the short circuit voltage of the transformer. This statement is very very strange to me:)

__________________
jinxnao
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#10

Re: Tap Changing Transformer S.C Voltage

07/08/2013 4:20 AM

why people are sticking to the "german part" of the issue :)

__________________
jinxnao
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#12

Re: Tap Changing Transformer S.C Voltage

08/19/2013 3:16 AM

the difference between steps in tap voltages is 5% because that is what purchasers of tap-changing transformers want and specifiy. once a voltage is 5% too low, we want to be able to increase it to nominal. we would specify smaller steps if useful and cost effective. at the consumer level, plus or minus 10% is usually the maximum acceptable voltage range, so at the HV level, plus or minus 5% easily keeps consumers voltage within that range.

__________________
BSEE but always learning
Register to Reply Score 1 for Off Topic