Earth Fault Relay Acting Source or Load

07/09/2013 12:11 PM

in the below circuit diagram left side is the source from a 132/33 KV transformer and a radial feeder is seen which feeds the load through 33/6.6 KV bus. There are two motor loads of of 1080 KW each. There are two breakers one at source side and the other at the load side. Earth fault protection is given for both source and load side breakers. The source side ct ratio is 400/1 A and load side CT ratio is 75/1 A. the residual CT setting at both load and source side is 20% ( 80 A at source side and 15 A at load side). Now my question is that if a earth fault occurs in the radial feeder, whether both the source breaker and load breaker trips or not. If the fault occurs near the load side which breaker trips first source or load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Earth Fault Relay Acting Source or Load

07/09/2013 3:53 PM

Is this a homework question?

Looks like it to me.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jul 2013
Posts: 11
#2

Re: Earth Fault Relay Acting Source or Load

07/10/2013 7:37 AM

Obviously if fault occurs after the CT location in load side then Load side breaker must be tripped first. but fault occur just befor CT location then source side breaker will be tripped.

There are many things which needed to be considered here, like other load details connected to the source, this system is earthed system or floating system, etc.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Earth Fault Relay Acting Source or Load

07/14/2013 11:46 AM

That depends upon the type of earthfault protection (time delayed or instantaneous or residual, etc.) and the co-ordination between the load side & source side relays. Assuming time delayed protection with proper co-ordination, then for a fault at the load side (near the motors), then first only the 33kV CB must trip and of it does not trip in the rqeuired time, then the 33kV upstream CB would trip.

Whereas if the earth fault is at the location shown in the picture, then only the upstream 33kV CB will trip as the down stream 33kV CB protection relays would not see this fault.

Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); Ritz11 (1); TonyS (1)

Previous in Forum: Power Factor Improvement   Next in Forum: Power Factor Correction

Advertisement