Why The Generators Are Mostly Star Connected ?

07/10/2013 5:34 AM

Generators / alternators having stator windings as star connected mostly what is the reason for having star winding on stator side. The rotor is a permanent magnet rotating with the constant frequency with prime mover. why on the single line / designs we always prefer star connected generators.

Is this due to

Less voltage stress as compared to delta

Differential protection is easy to configure in star

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Why the Generators are mostly star connected ?

07/10/2013 7:25 AM

...or is it to do with the ability to connect single-phase loads to it? Hmmmm.....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Why The Generators Are Mostly Star Connected ?

07/10/2013 7:44 AM

Easier earthing arrangements?

__________________
The reports of my death are greatly exaggerated.
Reply
Active Contributor

Join Date: Jun 2013
Posts: 14
#3
In reply to #2

Re: Why The Generators Are Mostly Star Connected ?

07/10/2013 7:47 AM

Do we need earthing on delta gensets ?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Why The Generators Are Mostly Star Connected ?

07/10/2013 8:00 AM

Only if protection against electric shock is a consideration.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #3

Re: Why The Generators Are Mostly Star Connected ?

07/11/2013 8:34 AM

Read the question

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#5

Re: Why The Generators Are Mostly Star Connected ?

07/10/2013 2:05 PM

They are that way for the same reason that my new fiber optic phone, TV, and internet service access point needs a 8 foot ground rod.

Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#7

Re: Why The Generators Are Mostly Star Connected ?

07/11/2013 10:32 PM

Star, less insulation of windings needed, which will reduce the size of the equipment,.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Why The Generators Are Mostly Star Connected ?

07/14/2013 11:38 AM

i) Lesser insulation needed between line & earth (only for phase voltage)

ii) Can connect single phase loads

iii) Can earth the neutral and get the benefits of an earthed neutral system.

Reply