Do I Need to De-rate a Neutral Cable Buried Underground?

07/16/2013 5:39 AM

Dear everyone,

I am laying an underground cable circuit, carrying 1000A (approx. 480kva) for a distance of 150m long.

Based on derating factor, L1, L2 and L3 are sized up to be 3 sets of 400mm2 multicore amoured, bring total copper size to 1200mm2 per phase. Based on this proposal, the ampacity per phase is around 1050A.

The question now is, what about netural and earth? Do I need to size it according to 1000A, 3 sets of 400m2 and earth is half of Live.

Anyone can share and guide?

Thank you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: do i need to de-rate a netural cable buried underground?

07/16/2013 5:43 AM
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: do i need to de-rate a netural cable buried underground?

07/16/2013 6:49 AM

Which would be preferable:

  • Sizing based upon a selection of educated guesses by well-meaning anonymous strangers on a global internet engineering forum that cannot see the installation with no assurance of correctness of each guess?
  • Sizing based upon the application of the sizing criteria contained in the applicable national electrical code/standard by a local Electrical Engineer with all the commercial come-back that this approach confers?

Tough call, isn't it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#3

Re: do i need to de-rate a netural cable buried underground?

07/16/2013 7:11 AM

If you are using an armoured multicore cable including the neutral conductor core, you have only 2 options, either 50% or 100% rating of phase capacity. The selection of 50 or 100% rating for neutral will be determined by the kind of connected load (balanced or unbalanced) and the estimated neutral return current. Selection of earth conductor is an altogether different subject and is determined not by the load current, but by the prospective fault current.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#4

Re: Do I Need to De-rate a Neutral Cable Buried Underground?

07/16/2013 9:38 AM

You need to know and understand the power distribution standards for this location and application! Depending on your circumstance and integrity you now have a few choices.

If you are actually employed at a company installing power distribution cabling then the safest thing for everyone is this. Identify and research the likely proper codes for this installation. Draw a conclusion and tell your boss this conclusion but inform your boss that you have no authority or experience to support your conclusion. Ask your boss if they have somebody with authority who could verify your work.

I hope that you are instead a student with a homework assignment. CR4 does not do homework.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Do I Need to De-rate a Neutral Cable Buried Underground?

07/16/2013 2:30 PM

The neutral should be rated to carry at least the maximum unbalanced load. If the load is all 3 phase, then there is no neutral amperage. However, I would consider at least 1 400 mm2. The grounding should be covered by the local code. There is no load except in the case of a fault. The NEC requires a grounding conductor based on the circular mil area of the phase conductors. For your conductor the grounding conductor would be a min of 85 mm2 (3/0 cu).

Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#6

Re: Do I Need to De-rate a Neutral Cable Buried Underground?

07/16/2013 10:47 PM

Neutral carries same amount of current that live carries so neutral is not all that neutral electrically. You will know the I*I*R losses to decide if cable is good enough.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Do I Need to De-rate a Neutral Cable Buried Underground?

07/16/2013 10:58 PM

In = √((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

But that doesn't take in to account harmonics in the neutral. Harmonics can drive the neutral current to above phase current.

I if was in you're shoes, I wouldn't down rate.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#8

Re: Do I Need to De-rate a Neutral Cable Buried Underground?

07/17/2013 8:09 PM

Shyam quote "Neutral carries same amount of current that live carries so neutral is not all that neutral electrically. You will know the I*I*R losses to decide if cable is good enough."

The poster is using a 3 phase cable. There may be little or no current in the neutral.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#9
In reply to #8

Re: Do I Need to De-rate a Neutral Cable Buried Underground?

07/17/2013 10:15 PM

You all should know how much I love to follow regional standards. Have you ever wondered why three phase circuit protection devices typically do not interrupt neutral?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#10

Re: Do I Need to De-rate a Neutral Cable Buried Underground?

07/18/2013 6:02 AM

Judging by the answers you have received, you might want to call on someone more qualified to do so. That person or company will get the information needed and the proper laws applicable for you.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11

Re: Do I Need to De-rate a Neutral Cable Buried Underground?

07/18/2013 10:59 AM

Yes, Yes & Yes! Whether it is phase conductor or neutral conductor, all de-rating factors are applicable for buried cables.