Anonymous Poster #1

LPG Pump Suction and Tank Levels

07/19/2013 8:18 PM

I have an Ebsray R10 LPG pump connected to four(4) x 7.5KL LPG tanks. The four tanks are interconnected and share a common suction line to the pump. This installation supplies LPG liquid to heat butimen.

The installation has a pump by pass line that interconnects all four(4) tanks.The installation also has a vapour manifold that equalises tank pressures. All pump by-pass valves and vapour valves are open during pump operations.

The installation is layed out in a straight line arrangement as follows; Tank 1, tank 2, tank 3, tank 4 and the LPG pump. The LPG pump is beside tank 4.All four(4) tanks are open during pump operation.

We discovered recently that tank 4 continues to have a low liquid level than the other three tanks. e.g. Tank 4 will read 5% whilst tanks 3,2 &1 will read 70%. We deduct from evidence visible to us, the suction/pull from the pump is strongest on tank 4 and as a result draws down tank 4 quicker than tanks 3,2 &1.

How can I correct this installation to achieve equal suction from all four(4) tanks?

Brisbane, QLD

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: LPG Pump Suction and Tank Levels

07/20/2013 5:01 AM
  • Arrange for the tanks to be geometrically equidistant from a common point. Arrange for the pipelines to that point to be the same diameter. Take the suction of the pump from the common point, or
  • one could reduce the flowrate passing through the pump until the level difference is immeasurable, or
  • one could replace the four tanks with one tank four times the volume, or
  • one could put a partly-open valve in the line from tank 4
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Jul 2013
Location: Darwin , Australia
Posts: 14
#7
In reply to #1

Re: LPG Pump Suction and Tank Levels

07/22/2013 3:26 AM

Thank you PWSlack,

Point 4: partly open valve on tank 4 sounds like an ideal solution for me.

Best Regards

Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#2

Re: LPG Pump Suction and Tank Levels

07/20/2013 10:01 PM

The surest way is to make the piping symmetrical, especially the pump suction, but maybe also the by-pass line, probably not the vapor line. But first, all tanks are identical and installed at the same elevation, correct?

To make the piping symmetrical, pipe from 1 to 2 and from 3 to 4. In the center of each of these 2 lines, install a 'T' and then run a line between the 2 'T's. In the center of this line install a 'T' and run from here to the pump suction. In the first 3 lines, it is imperative that the lines be mirror images on both sides of the 'T', i.e. if it takes 2 elbows to get out of tank 1, make sure there are 2 elbows at the other 3 tanks as well. When you get through, you can follow the flow path from each tank to the pump and each path should go through the same number of fittings and the same length of pipe.

If a fitting is required on the piping to the pump is required, it is advisable to have 5 to 10 pipe diameters of straight pipe between the 'T' and the other fitting. This may not be clear. If not, can you post a picture of the installation?

Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2013
Location: Darwin , Australia
Posts: 14
#8
In reply to #2

Re: LPG Pump Suction and Tank Levels

07/22/2013 3:34 AM

Thanks Bigg,

I think you hit the nail on the head. Our design should have been as how your described it. PWSlack suggested for a partly open valve on tank 4 which I will use as my short term fix untill we modify the pipe work as above( long term fix).

Super

Reply
Active Contributor

Join Date: Jul 2013
Location: Darwin , Australia
Posts: 14
#9
In reply to #2

Re: LPG Pump Suction and Tank Levels

07/22/2013 3:38 AM

Thanks Bigg,

I think you hit the nail on the head. Our design should have been as how you described it. PWSlack suggested a partly open valve on tank 4 which I will use as a short term fix untill we modify the pipework to have a tee and suction coming from the center of all four tanks.

Super

Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#3

Re: LPG Pump Suction and Tank Levels

07/21/2013 12:01 AM

yes, post a picture of the installation...

__________________
A picture worth thousand words: needless to say if it is animated.
Reply
Active Contributor

Join Date: Jul 2013
Location: Darwin , Australia
Posts: 14
#10
In reply to #3

Re: LPG Pump Suction and Tank Levels

07/22/2013 3:39 AM

Hi yesyen,

A timely reminder.

Thanks

Reply
Associate

Join Date: Mar 2009
Location: Beverly Hills
Posts: 52
Good Answers: 7
#4

Re: LPG Pump Suction and Tank Levels

07/21/2013 12:06 AM

Hi Why worry about it?? IF you are getting enough fuel from the setup and you clearly know how much fuel you have then why even worry about it?? Your Assumption is correct in that the 4th tank is closer to the pump thus gets drained a little faster. IF you were drawing off Vapor rather than LP it could be a problem as the tank would ice up. But as long as you get enough fuel even if tank 4 runs dry I would just not even go to the trouble of redoing the system. In Short. If it works. Do not worry about it.

However. If for some reason not mentioned this is a problem then use larger pipe from the other 3 tanks. Even with the Vapor Crossover to keep the pressure the same in all tanks the problem is simply a law of force. It is easyer to flow from tank 4 than the other tanks. But a Larger Pipe will help and also hook a pipe to tank 1 to the pump via a T joint just before the pump and at the pipe. But this will only cause tank 1 and 4 to drain faster than 2 and 3 as the flow from what ever is closer to the pump as far as flow goes rather than distance is realy the cause because as it is now tank 4 the fuel hits the drain pipe at a 90 degree angle and causes a higher pressure area cutting flow from the others until it gets lower on fule. There are many ways to fix the issue and I give some below.

Another way is to build a manafold. Pretty much what you have with your current pipeing system. But have all 4 tanks go to One Larger pipe and hook to the Larger pipe that will be the manafold at a 90 degree angle from the 4 incoming pipes. Make this larger pipe long and at least 5 times the size of the incoming pipes. Why do this. because of what is causing the problem in the first place that I do not see as a problem based on Data given but if it is a problem then this will fix the issue as you will not have the flow comming into the current pipe from tank 4 causes a higher pressure in that part of the pipe thus blocking off the flow from the others. This also tells us that you are using a lot of fuel when the thing is running. Anyway I hope all is working for you and you can just say leave it alone. Why do all tanks have to be the same level??? Think about it. Also when the shift is done the tanks will almost level out to the same. Not all the way but close. So I would say Just leave it alone.

Jim

Reply
Active Contributor

Join Date: Jul 2013
Location: Darwin , Australia
Posts: 14
#13
In reply to #4

Re: LPG Pump Suction and Tank Levels

07/22/2013 3:56 AM

Hi Jimmyjoejetter,

Thanks mate for shooting from a different angle. It opened me up

Best Regards

Reply
Associate

Join Date: Jan 2009
Posts: 37
Good Answers: 1
#5

Re: LPG Pump Suction and Tank Levels

07/21/2013 3:50 AM

Hello Anon,

This really must be a homework question eh?

Considering an operational pumped LPG system,your questions would have all been answered & addressed by the installers & engineers leaving your pump to be concerned with.

That said,either your pump is failing or simply lost a phase resulting in reduced pumping performance.

As for your homework,basic pumping design considerations should be applied.

HTH

Jay

Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2013
Location: Darwin , Australia
Posts: 14
#11
In reply to #5

Re: LPG Pump Suction and Tank Levels

07/22/2013 3:48 AM

Hi Mr Fixit,

No, it is a real life challenge. A lesson I guess to ensure the dos & don't of pump installation is discused with the manufacturers prior to installation.

Best Regards

Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6

Re: LPG Pump Suction and Tank Levels

07/21/2013 5:19 AM

The difference between 5% and 70% is too high to be attributed to just pipe length or proximity!

Your problem is due to the fact that some vapor will become present in the interconnecting pipes, and will be drawn to the connection nearest the pump. This will cause a kind of vapor lock that will prevent the 3 back tanks from delivering liquid as should be normally. Tank 4 will be draining to the pump at much higher rate!

Solution: you need to slope the pipes down from tank 1 to 2, to 3 and to 4 (Lowest point before pump suction entry). This way, any Vapor formation will be going back to the end of the pipe, towards tank1 and, there, have an extra pipe going back and Up to the top of tank1, to the vapor zone. This will allow tank1 to drain evenly, like the others

The most important issue is to prevent the vapor from sloping upward towards the pump suction! If the system was working fine for some time before exhibiting this problem, and this just happened recently or does happen from time to time, then the pipe slope is either zero or just slightly upward to the pump, or something just happened to sag it this way. Check and good luck

Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2013
Location: Darwin , Australia
Posts: 14
#12
In reply to #6

Re: LPG Pump Suction and Tank Levels

07/22/2013 3:53 AM

Hi LAA Lucke,

Your analysis is good. Consolidating the responses from all I think I have found myself a short term and a long term fix + other design considerations that will prove useful in future.

Best Regards

Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#14
In reply to #12

Re: LPG Pump Suction and Tank Levels

07/23/2013 1:15 AM

Restricting valve on tank 4 might not work if the problem is a Vapor trap in the pipes.

You might experience the same problem on another tank (Maybe nr 3 this time). or loss of priming whereby no fluid in the pump!

Check the pipe work installation to see if there is any high point where Vapor can get traped, thus preventing flow from the 3 tanks, in favor for tank 4. Might be between Nr 3 and Nr 4.

Balancing the flows from the different tanks by patial closure of the valves would have been suggested if the liquid levels in the tanks were gradually decreasing from Nr 1 to Nr 4. You said that 1, 2 & 3 were 75% full when 4 was only 5% full. This points to a possible block between 3 and 4, and this blockage can be a vapor trap if nothing else (like restriction in pipe or some foreign matter ...

Reply Score 1 for Good Answer
Reply to Forum Thread 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bigg (1); jimmyjoejetter (1); LAA_Lucke (2); Mr Fixit (1); PWSlack (1); Ronald Nawa (7); yesyen (1)

Previous in Forum: What is the Main Use of Cyclone in CFBC thermal Boilers   Next in Forum: Reduction in RPM During Normal Operation of Steam Turbine Driving a Pump

Advertisement