Catenary Curves for 72mm ADSS Fiber (Outside Aerial)

07/24/2013 3:27 PM

Hey guys,

I'm working in AutoCAD on drawing CAT curves for our overhead fiber network. The LISP routine I have is for 12kV/60kV lines, also I don't believe it is appropriate for communication wire because of the temperature for overhead lines.

Does anyone know of any curves that are posted or a LISP routine or a more appropriate equation (I can code it myself in AUTOLISP) I can use? Pretty slim pickings on google.

__________________
gisdude
Register to Reply
Pathfinder Tags: catenary curve fiber overhead
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: CATENARY CURVES FOR 72MM ADSS FIBER (OUTSIDE AERIAL)

07/24/2013 3:47 PM

Of course, you asked the supplier?

Or, maybe: The Fiber Optic Association

Installing and Testing Fiber Optics - NECA - National Electrical ...


I don't have a clue, myself, but ↑

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: CATENARY CURVES FOR 72MM ADSS FIBER (OUTSIDE AERIAL)

07/24/2013 4:29 PM

A catenary is a geometric shape. The equation doesn't change on account of voltage or composition of material that is hanging. A parameter or two will change on the length of material, which depends on temperature, but not the overall equation.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#3
In reply to #2

Re: CATENARY CURVES FOR 72MM ADSS FIBER (OUTSIDE AERIAL)

07/24/2013 11:06 PM

He is talking about sagging in the cable where you lay in the cable to handle different temperatures. The least clearance for a given length of cable is, or used to be, at 257oF. The greatest tension, least sag, is at the lowest ambient temperature

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#4

Re: Catenary Curves For 72mm ADSS Fiber (Outside Aerial)

07/24/2013 11:16 PM

I'm with Tornado, the catenary curve is the shape. It does depend on several input quantities though; things like lb per foot of the cable, tension, span, etc. Increasing temp will make the cable longer, thus more sag. I should have the equations here somewhere, but they should also be available "out there."

__________________
Lehman57
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Catenary Curves For 72mm ADSS Fiber (Outside Aerial)

07/25/2013 12:00 AM

Definitionally, a catenary is specified completely by the locations of its endpoints and the length of the suspended item (assuming no interfering objects.) Weight per length doesn't affect the shape, but of course it affects the tension. One can "work backward" from the tension versus weight-per-length to find the total length and shape, but the length is the fundamental quantity.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#6

Re: Catenary Curves For 72mm ADSS Fiber (Outside Aerial)

07/25/2013 7:06 AM

Guys, what you say is correct but misses the OP's point.

When you design a transmission or distribution line, you pick a cable and based on its strength, figure a sag for each span for equal tensions (insulators hang vertically). Then the other conditions are checked for their effect on sag for that length of cable, icing for that district, high winds and high temperature. These days, these are handled simultaneously by a computer program. OP seems to be asking if the high temperature is appropriate for the fiber line since there is not a high current flowing.

I would say that the high temperature sag can be ignored.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
Guru
Engineering Fields - Nuclear Engineering - New Member

Join Date: Sep 2009
Location: Louisville, OH
Posts: 1925
Good Answers: 36
#7
In reply to #6

Re: Catenary Curves For 72mm ADSS Fiber (Outside Aerial)

07/25/2013 11:29 AM

I would say that the high temperature sag can be ignored.

I don't think so. Is this communications cable going to be exposed to the sun and weather? The expansion due to temperature change will definitely affect the sag.

__________________
Lehman57
Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#8
In reply to #7

Re: Catenary Curves For 72mm ADSS Fiber (Outside Aerial)

07/25/2013 2:10 PM

It will have a high temperature sag, but not as high as for a transmission line carrying maximum current on a hot day. The sag tables/programs cover other temperature steps as well as the extreme.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
Associate

Join Date: Jun 2007
Location: Sacramento, CA
Posts: 33
#9

Re: Catenary Curves for 72mm ADSS Fiber (Outside Aerial)

07/29/2013 2:31 PM

Hey guys,

Thanks for all the responses. Doing a little more research "out there" the sag for Fiber Comm wire is negligible, ie. most companies won't even bother to create a sag chart/drawing. Typically for 12kv, 60kv, Transmission, Distribution, we WILL create charts due to the SIMPLE FACT that these are current carrying conductors and (based on loading) will have (at some points) significant sag (3, 4, 5 feet). The heat that is generated by the load will cause the wire to sag more (also will make it eventually more brittle), then maintenance will get the job...

Thanks for all the input guys.

__________________
gisdude
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

GISdude (1); Lehman57 (2); lyn (1); passingtongreen (3); Tornado (2)