Why and When We Need NGR / NER?

07/24/2013 11:17 PM

hello engineers. i saw some dyn11 transformer star point go to soild grounding and some dyn11 transformer with same rating dont have soild grounding. the star point is connected to NGR/NER and then connected to grounding. why and when we have to connect NGR? i know we connect NGR to reduce earth fault current.. but i want much more clear answer.. plz help me...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: why and when we need NGR / NER?

07/25/2013 12:21 AM

Sounds like a Google project to me...but not for me.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: why and when we need NGR / NER?

07/25/2013 1:23 AM

Think voltage and fault current.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#3

Re: why and when we need NGR / NER?

07/25/2013 3:04 AM

For grounded system cables required are unearthed type. May be this could be your answer.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: why and when we need NGR / NER?

07/25/2013 3:07 AM

<...connect NGR to reduce earth fault current...>

Is that clear enough?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jul 2013
Posts: 2
#5

Re: Why and When We Need NGR / NER?

07/25/2013 10:30 AM

NGR/NER is often used to:

- Limit fault current on phase to ground faults (eg. on large generators to comply with NEMA MG-1 bracing requirements)

- Reduce circulating currents in neutrals where multiple machines are neutral grounded

- Suppress 3rd harmonic content where multiple machines or different characteristics (eg. generators of different pitch) are parallelled.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6

Re: Why and When We Need NGR / NER?

07/25/2013 4:44 PM

This link might be helpful: http://cr4.globalspec.com/comment/589279

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#7

Re: Why and When We Need NGR / NER?

07/28/2013 3:49 AM

What is the capacity of your dyn11 transformer?.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

msamad (1); oldtex (1); PWSlack (1); Simon Wan (1); TonyS (1); Tornado (1); vyral2311 (1)

Previous in Forum: Catenary Curves for 72mm ADSS Fiber (Outside Aerial)   Next in Forum: Motor Lug Burnt, but Drive Didn't Trip

Advertisement