Current Transformer For Transformer Earth

07/31/2013 3:24 AM

HI,

Is that CT used for transformer earth is identical to the CT's used for lines in the star side of the transformer

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Current transformer for transformer earth

07/31/2013 3:27 AM

What does it say on the as-built drawing? Only, it cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#2

Re: Current Transformer For Transformer Earth

08/01/2013 4:10 AM

Dear Mr. Devinda,

I understand from your question that you are referring to EARTHING TRANSFORMER and CURRENT TRANSFORMER, is the SAME TYPE.

If so, the Answer is THEY ARE NOT THE SAME. and there is a difference between them.

DHAYANANDHAN.S

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: Current Transformer For Transformer Earth

08/01/2013 7:25 AM

I understand from your question that you are referring to EARTHING TRANSFORMER and CURRENT TRANSFORMER, is the SAME TYPE.

If so, the Answer is THEY ARE NOT THE SAME. and there is a difference between them.

How did you come to that concussion?

We don't know what the CT's are being used for.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5
In reply to #3

Re: Current Transformer For Transformer Earth

08/01/2013 11:46 AM
Dear Mr.TonyS,

The CT is used for measuring the Current of Large Magnitude.

Earthing Transformer is used for Large Generators. You can see the details here

http://yourelectrichome.blogspot.in/2011/10/earthing-transformer.html

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Current Transformer For Transformer Earth

08/01/2013 11:30 AM

Could it be identical? Yes. Possible but not probable due to the lower current presented in the ground conductor and the need for high speed ground/earth fault protection of equipement.

Could it be of the same type but with a different "turns-ratio"? Yes. Possible and highly probable.

Selection of CT type and "turns-ratio" selection is dependent on the circuit design, level of system equipment protection required, and the field application.

This may be confusing but it is "real" and the only way to be sure is to first do the reasearch and gain an understanding then review and verify the field application.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 1 for Good Answer
Member

Join Date: Jul 2013
Location: Colombo
Posts: 5
#6
In reply to #4

Re: Current Transformer For Transformer Earth

08/02/2013 3:34 AM

Dear DHAYANANDHAN

I am asking about protection current transformers used for transformer protection , not regarding earthing transformers used for earthing the delta winding of the transformer. I understood about your explain regarding earthing transformers.

Dear Shockhiscan,

can you give details of currents transformers like turns ratio and burden, which are used for transformer over current and earth fault protection

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Current Transformer For Transformer Earth

08/04/2013 10:32 AM

That depends upon what type of protection you have for lines and for earth.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Devinda (1); dhayanandhan (2); electricalexpert65 (1); PWSlack (1); SHOCKHISCAN (1); TonyS (1)