Alternator Frequency

08/05/2013 7:31 AM

Dear All

alternator standard frequency is 50 Hz, if we reduce frequency from 50 to 49 then are the effect on electrical KW

example if Kw 14 MW on 50 Hz what are the KW on 49 HZ

if star delta motor load are 7 Mw & drive motor load are 7 Mw

& effect on motor efficiency & life

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Alternator Frquency

08/05/2013 7:41 AM

Never mind that. If the motors are driving pumps then pump performance will fall off, altering the economics of the operation rather more than simply the change in life of the motors!

Stay at 50Hz.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: May 2012
Posts: 26
#2
In reply to #1

Re: Alternator Frquency

08/05/2013 7:52 AM

thanks for Reply

pump discharge decrease but is input power of star delta motor also decrease. ie if it getting load 60 KW is new KW is less than 60 Kw

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Alternator Frquency

08/05/2013 8:08 AM

This is folly. Stay at 50Hz.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#3

Re: Alternator Frquency

08/05/2013 8:06 AM
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Alternator Frequency

08/05/2013 11:09 AM

Sure, why not do it.

Since you don't know how calculate the difference, it shouldn't bother you that efficiencies of most devices will suffer and all your clocks will run slower.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6

Re: Alternator Frquency

08/05/2013 1:32 PM

This sounds like mis directed penny pinching to me.

If you want to have maximum profit at the least operating cost never take short cuts or underfunded the service and maintenance departments. Go after the managements paychecks. That's usually where the most money is going that does the least good for the betterment and longevity of a company in the end.

Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Alternator Frquency

08/05/2013 3:34 PM

Don't !

__________________
jack of all trades
Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#8

Re: Alternator Frequency

08/05/2013 11:17 PM

Whats the idea behind this.R U trying to save energy , than forget it on power circuits.

Register to Reply
4
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#9

Re: Alternator Frequency

08/05/2013 11:28 PM

Hi Lalit,

Lowering the operating frequency of alternator will increase the burdon on the excitation circuit of the alternator; Excitation Circuit = AVR + Exciter Stator + Exciter Rotor+ Rectifier Assembly + Main Rotor, and inturn will incresae the losses (I2R Losses, whith the very little benefit on the Iron Losses).

To avoid the over burdoning on the excitation circuit, you need to reduce the output KVA of the alternator, this can not be calculated with an imperical formula, but needs to restrict the Excitation Values same as Full Load 50 Hz.

Lowering the frequency will further increase the No Load Current drawn by the Induction Motors, which is again a loss.

If you want to get max Efficiency, please talk to the Manufacturer of the Alternator and ask for the Efficiency Graphs at various PF and various Load Conditions. As per my experience the Max Efficiency is arround 85 - 90 % of Full Load.

I certainly do not advocate lowering Frequency will save money, rather it will take a penny more from your pocket.

Regards,

Vishram Lele

Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Alternator Frequency

08/06/2013 8:17 AM

If it were a good idea, then why is nobody else doing it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#11
In reply to #10

Re: Alternator Frequency

08/06/2013 9:24 AM

The main problem with lowering the frequency is that the core flux density goes up. Many motors and generators of current design do not have much margin. If the core goes to saturation then damage will occur. Design for alternators take into account that there will be some fluxuation but if you try to run at less than rated (50 HZ) continuously you will not have the tolerance available for short term variance. There probably would be little damage at 49 but if the frequency drags down during starting you could get into big problems. Going into saturation destroys equipment, not just overheats it.

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#13
In reply to #11

Re: Alternator Frequency

08/09/2013 11:58 PM

4w silver, u r obviously someone who's got up from their desk, gone out into the field, and actually understands how things work... and so you are 100% right. thx! :)

__________________
BSEE but always learning
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Alternator Frequency

08/06/2013 12:07 PM

Dear Mr. Lalit Shukla,

This topic/similar topics have been discussed several times.

If the frequency falls down, the motor speed will fall down - considering 50 C/s. Frequency, drop to 49 C/s.speed will drop to 98% - fall of 2 % and for the Pumps, fans etc., capacity will varyas Proportional to the speed, Pressure will vary as Proportional to the SQUARE of the speed, and the Power will vary as CUBE of the SPEED.

Further, as replied in Post No. 9, the EXCITATION CURRENT, will INCREASE, the Power Factor will vary etc.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); 4wsilver (1); Anonymous Poster (1); dhayanandhan (1); jack of all trades (1); Lalit Shukla (1); lyn (1); pillay (1); PWSlack (3); tcmtech (1); vishram lele (1)

Previous in Forum: Tranformer 1500KVA 11KV/415V   Next in Forum: Voltage and Current Needed to Plate Copper to Lead?

Advertisement