08/05/2013 7:50 AM

Can anybody tell me the difference between ON line UPS's battery and OFF line UPS's battery?

Because one information I got that whichever the battery have been used in OFF line ups can't able to fix and operate in the ON line UPS.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Difference between online ups's battery and offline ups's battery.

08/05/2013 8:11 AM

The only difference between an on-line UPS' battery and an off-line one, is that the equipment is taking power from the mains in the first case, and it isn't in the second.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/05/2013 9:54 AM

See #1.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/05/2013 10:41 AM

The one information you got doesn't sound very sensible, either.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/05/2013 10:51 AM

...so if there is no difference, it would be unlikely that anyone can.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#5

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/05/2013 11:16 AM

As long as the voltage, amp hour capacity,charge, and discharge rates are the same it doesn't matter what battery is doing what or where.

The online or offline function is more or less determined by the circuitry not the battery set.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/05/2013 11:49 AM

Google and other search engines must be having a hard time staying in business, since it is obvious that very few use them any more.

Register to Reply
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#8
In reply to #6

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/05/2013 1:11 PM

The CR4 member based search engines are far more efficient. They can read between the lines where the rest of the search engines just give you a lot of choices of which you have to sort through yourself.

Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/05/2013 12:02 PM

I think we have a language barrier issue here.

Can you provide a one-line to illustrate what you are referring to as an online and an offline UPS for your configuration?

In my vernacular an on-line UPS is a double-conversion style system, where the battery is always connected to the inverter section, resulting in no loss of power to the load when incoming power fails.

An off-line UPS would be an UPS which would require switching the battery to the inverter upon loss of incoming power which would take a few milliseconds but constitutes a loss of power for sensitive electronic systems.

Register to Reply Good Answer (Score 2)
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#10
In reply to #7

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/06/2013 8:13 AM

No doubt our usage of these terms elsewhere contributes to the confusion. For instance: An offline power supply actually uses the utility power for it's energy source because it is working "off the lines". Wouldn't that really be an online power supply?? Oh, well. (English is a wonderfully confusing language without doubt)

At any rate, yes the current vernacular of the UPS industry is to define a "double-conversion" UPS as one that provides power continuously from the battery-fed inverter and a separate battery charger that is powered from the utility power maintains the charge on the battery, hence double-conversion as Cuba_Pete aptly stated.

The other typical style UPS is usually referred to as a "line-interactive" UPS where the inverter is in a stand-by mode waiting for a power failure at which time it is switched on and fed by the battery. There is usually several milliseconds of delay from utility power drop-out until the inverter is able to begin feeding power to the loads. Systems that cannot tolerate the momentary glitch, will generally use the double-conversion UPS.

A line-interactive UPS can generally use a smaller battery charger (less expensive) than the double-conversion UPS because it only needs to maintain the charge on the battery and not required to provide continuous full rated power.

Cheers !!

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#9

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/05/2013 7:53 PM

On line UPS always feeds the load through the inverter and the battery get loaded to feed the inverter.

Off line UPS lets the load feed on the grid instead of on the inverter. Once there is a power interuption the inverter takes over.

In both systems the battery is loaded by the grid,

I stop here.

__________________
Plenty of room here
Register to Reply
Commentator
United States - Member - New Member Engineering Fields - Instrumentation Engineering - Popular Science - Cosmology - Beam me up Scotty!

Join Date: Jun 2013
Location: The Sunny Side
Posts: 85
Good Answers: 5
#11

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/06/2013 9:40 AM

There are actually three types of UPS's online, offline and line interactive. In an offline system the load is normally provided for by the input power and the backup is only called upon when the power supply fails. An online system converts the AC input into DC current for charging the rechargeable battery and then converting the DC current back to AC current to power the equipment. This is a double conversion method. A line interactive system uses an inverter to supply current when the power supply is lost by redirecting current from the regular charging mode of the inverter.

The offline UPS connects the equipment directly to a power supply. It only provides basic features such as battery backup and surge protection. Whenever there is a variance in the input supply, the system within milliseconds switches on the circuitry which converts the DC current available in the battery to AC current and supplies it to the device. The time taken to switchover from the input supply to the backup supply depends on the time taken by the circuitry to find the lost voltage. This type of UPS can only be used for equipments like home computers which require very little power and can handle fluctuations in the supply

The online UPS is considered ideal for equipment that is sensitive to fluctuations in the power supply or for environments in which electrical isolation is essential. In most countries nowadays electrical anomalies like outages, sag in utility power, etc., are a common occurrence. The basic components of an online power system is similar to that of the offline UPS. This type of UPS also has 2 supplies and transfer switch that selects between the power supplies. The difference is that the primary supply of the UPS is the UPS's battery and the secondary supply is the mains.

Each system has its own unique advantages and disadvantages. The advantage of the offline UPS is that the initial cost is less, the efficiency at which the system operates is really high, and it is silent during operation. The advantage of the online UPS is that not only does it provide continuous power conditioning there is also no break when the mains fail and it has a wide tolerance range of input voltage. However this type UPS is more expensive than the other UPS systems. But when comparing both the online and offline UPS, the online UPS clearly has the upper hand barring the difference in price.

__________________
"Experience: that most brutal of teachers. but you learn, my God do you learn." - C.S. Lewis
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#12

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/06/2013 11:03 AM

So, back to the OP's question (who is apparently absent)...

Why would their online and offline batteries be incompatible?

At least, that is how the question translates in my mind.

Register to Reply
Commentator
United States - Member - New Member Engineering Fields - Instrumentation Engineering - Popular Science - Cosmology - Beam me up Scotty!

Join Date: Jun 2013
Location: The Sunny Side
Posts: 85
Good Answers: 5
#14
In reply to #12

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/06/2013 1:27 PM

This is what you call a drive by question, Just throw out a Crappy question with lithle or no understanding of what you are asking and none of the data necessary to allow for an adequate answer just to see if anyone is bored enough to waste their time discussing it. (this only works on an engineering website) Then they come back every once in a while to see how many bored engineers there are! I think its a game, kind of like fly paper for bored and retire engineers

__________________
"Experience: that most brutal of teachers. but you learn, my God do you learn." - C.S. Lewis
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#13

Re: Difference Between Online UPS Battery and Offline UPS Battery

08/06/2013 12:52 PM

Without actually having the battery specs, it is difficult to say what will work.

  • What are the battery specifications
  • Voltage?
  • Amp hour rating?
  • Physical size?
  • Model number?

Compare these to the system you want to install it in. If the voltage is the same, probably 12VDC then your Amp hour rating and physical size are what matters!

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

1tech (2); Brave Sir Robin (1); cuba_pete (2); dvmdsc (1); lyn (2); Original_Macgyver (1); PWSlack (2); tcmtech (2); Tornado (1)

Previous in Forum: Voltage and Current Needed to Plate Copper to Lead?   Next in Forum: Solving for Four Resistors with Four Equations

Advertisement