Anonymous Poster #1

Meter Constant For Digital Energy Meters

08/21/2013 2:18 AM

Does the digital energy meters has a meter constant like analouge meters.?

In analouge meter people will take difference between the initial and final reading of the TOD meter and multiply it with the meter constant That will give the total consumption units.

So I was wondering if we use a digital energy meter wheather it will give the direct kWh reading or should i have to multiply the meter constant (if it is available)...

Thanks in advance

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Meter constant for Digital energy meters

08/21/2013 2:34 AM

Does the meter say "Xnnnn" anywhere on it? Does it show a decimal point?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Associate

Join Date: May 2012
Location: Ahmedabad, INDIA
Posts: 25
Good Answers: 1
#2

Re: Meter constant for Digital energy meters

08/21/2013 7:11 AM

it depends on different make of energy meter u r using

what ratios of CT u have used for energy measurement

Reply
Anonymous Poster #2
#4
In reply to #2

Re: Meter constant for Digital energy meters

08/21/2013 9:09 AM

u r you are

Reply
Anonymous Poster #2
#3

Re: Meter Constant For Digital Energy Meters

08/21/2013 9:08 AM

analouge analogue

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5

Re: Meter Constant For Digital Energy Meters

08/21/2013 9:19 AM

On the analog meters, the meter constant was usually labeled Kh. The equivalent constant on digital meters is usually labeled Ke. This has been the case on many meters I have calibrated in the past (GE, ABB, JEM/Scientific Columbus, etc.).

__________________
To get the right answers, first you need to ask the right questions.
Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Meter Constant For Digital Energy Meters

08/21/2013 10:42 AM

In the old days of spinning aluminum disks and dial indicators you needed a way of relating how many revolutions of the disk represented 1 KWH passing through the meter, that number was the meter constant. Depending upon the manufacturer and style of the meter there was often a Register Ratio and a Gear Ratio that related the revolutions of the disk to the incremental change in the motion of the register (read out dials).

This allowed utilities to use one meter style for different voltage/current combinations such as 120V/50A, 120V/100A, 240V/100A, 240V/200A, etc. simply by changing the gearing from the disk to the register. However, the actual consumption depends upon whether there are any potential or current transformers (PTs/CTs) between the meter and the incoming line. Again in the old days there was a TR (Transformer Ratio) that was usually tagged to the register or shown on the billing statement that related the kWh registered to the kWh consumed.

Modern digital meters can be programmed with the TR or not, so there is no way to tell by looking at the meter if it is direct reading or needs to be multiplied by the TR. Your billing statement is the only clue. If the meter and the bill kWh agree then the meter has been programmed for all the constants, if not then there will be a TR (which may still be called the metering constant) that gets multiplied times the reported reading to get the actual consumption.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Score 1 for Good Answer
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); MUSUTH86 (1); PeterT (1); RAMConsult (1); Tornado (1)

Previous in Forum: ABB ACS800 Not Responding to Digital Input   Next in Forum: Parallel Operation Of Self Generators With Government Grid

Advertisement