Parallel Operation Of Self Generators With Government Grid

08/21/2013 5:54 AM

I have observed that when the own generators are connected to Govenrment grid , the power factor , which used to be 0.95 has fallen down upto 0.65. Earlier there was import of electrical power from the government grid but now after parallel operation the power is being exported

How to improve this power factor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Parallel operation of self generators with Government Grid

08/21/2013 6:18 AM

Turn off the export.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Parallel operation of self generators with Government Grid

08/21/2013 6:30 AM

It has been some years since I operated a genset powerhouse, but IIRC the grid is considered isochronous and your governor(s) need to be in droop mode. (This may not apply to some types of electronic governors.) The kW furnished by each genset is controlled by governor adjustments. In turn the PFs can be altered by voltage regulator adjustments.

I'm not absolutely sure of this recollection, but it may suggest some items to look at.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#3

Re: Parallel Operation Of Self Generators With Government Grid

08/22/2013 6:03 AM

You did not mention PF of 0.65 Inductive or Capacitive.

You are lucky if your set is still operating and alternator has not burnt.

You are Exporting kVAR along with kW, if your power factor is inductive. Otherwise importing power if your power factor is capacitive.

You can control PF by adjusting excitation of the alternator.

If you are generating more inductive power and want to reduce it that means want to bring PF of your power station from 0.65 inductive to 0.8, reduce excitation slowly.

Note that generating more reactive, you are overloading AVR, exciter, main field and stator winding hence do not do it.

Also poor is the power factor of your generating set, poor is the efficiency of your 3 phase alternator hence increasing fuel consumption.

Also do not try to go less than 1 PF. If you go capacitive (importing kVAR from Grid) - will result in poor coupling between revolving fields of rotor and stator - hunting of rotor around stator revolving field and generation of induced voltage in rotor field poles and over heating of poles and failure of field windings.

Protect your machines by installing following:

1. loss of excitation relay based on offset impedance measurement which is set to operate if stator current is in third quarter and exceeds predetermined value.

2. Reverse Power Relay.

3. Power Factor Limiter (this will ensure your alternator will not try to feed heavy reactive current beyond its capability if grid voltage drops).

4. df/dt relay - this is to isolate your power station from Grid in case the grid is unstable or collapses. This relay will trip the Grid Incomer (not your Generator CB)

Register to Reply Good Answer (Score 2)