Anonymous Poster #1

Woodward LSM Problem

08/25/2013 8:02 AM

hai guys

i have a probelm with woodward LSM modulde ie,my vessel have 3 no caterpillar generator.when no.1 & no:2 generator in load sharing it is working fine.but if we start the no.3 generator (breaker is open )other two become unstable.when removing the loadsharing line from no.3 generator LSM then no.1&2 working ok.

if no.3 is with the any one of the other generator then also hunting is happening.no variation in engine speed.

can anybody give good suggestion for solving the same

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Woodward LSM Problem

08/25/2013 9:57 AM

Could be moon phase.

Maybe a broken framus.

I think I see a problem with the #3 genset fuel supply. From here, it is really hard to tell.

Try asking these guys: LSM - Woodward

Reply Score 1 for Off Topic
Active Contributor

Join Date: Feb 2013
Location: Titusville,Fl.
Posts: 15
Good Answers: 1
#2

Re: Woodward LSM Problem

08/25/2013 10:47 PM

I had a similar problem one time with 2 Cat generators.and it turned out to be a bad speed sensor on the incoming gen.

__________________
"Hope for the best,expect the worse,and take whatever comes!"
Reply
Participant

Join Date: Aug 2013
Posts: 1
#3
In reply to #2

Re: Woodward LSM Problem

08/25/2013 10:56 PM

Bur in this caise their is no speed sensor to LSM . This problem is happening in ino.3 gen deal running/on load also.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Woodward LSM Problem

08/25/2013 11:25 PM

"can anybody give good suggestion for solving the same"

Call a service tech and have #3 genset fixed.

Yes, it will cost money.

Don't waste time hoping that it can be fixed free of charge.

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Woodward LSM Problem

08/25/2013 11:29 PM

What happens if you run sets 1 & 3 or 2 & 3?

__________________
The reports of my death are greatly exaggerated.
Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#6

Re: Woodward LSM Problem

08/25/2013 11:48 PM

A generic solution with plc is far superior to vendor dependent solution in the long run.Any one can locate and solve.Solid example.

__________________
Better not count the cent if the risk is many many dollars.
Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#7

Re: Woodward LSM Problem

08/26/2013 1:28 AM

First ensure that the cable used for equalising line between various LSM modules is good quality shielded cable with twisted pairs.

2nd Ensure that screen of all shielded wires are earthed BUT only at one end.

3rd ensure that shielded cable is not laid in the trunking in parallel with any AC power cable.

If problem exists, use twisted pairs for 24V DC power supply to LSMs of each machine.

If nothing of above works do following:

For LSM to start sharing load, Terminals 13 and 14 are shorted via DG ACB contact. To sort out the cause of problem, instead of disconnecting equalizing lines from LSM of DG 3 open 13 and 14, if the problem of instability of DG 1 and 2 disappears, check the cable and auxiliary contact connected across 13 and 14 for possible short or poor insulation resistance between the cores of cable or across the contact. This is a marine application and most probobly any tracking across the contacts could be the reason of problem. Though the chances are remote as I have noticed that Panels are located in a bottom portion of the ship with sealed doors and ventilated room - but in case the ship was out for some long maintenace and doors were left opened for long period in the docks, possibility of salt moisture and tracking can not be ruled out.

Best or luck.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Woodward LSM Problem

08/26/2013 3:39 PM

What was the outcome of the telephone call with the equipment manufacturer's Technical Helpline?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Woodward LSM Problem

08/26/2013 3:44 PM

No instant gratification that way.

And, they might want to charge for their valuable time.