UPS P.F 0.9

08/25/2013 8:44 AM

I see some manufacturers give 0,9 output p.f .Then I can ask what if I load a 1000 kva ups with 0,9 p.f with a pure resistive 1000 KW p.f if I increase its battery from 900 kw to 1000 kw? if we can then a 0,9 p.f does not mean an advantage in a real sense..

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#1

Re: UPS p.f 0,9

08/25/2013 9:01 AM

Maybe for the battery company. They'd love to sell you anything.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: UPS P.F 0.9

08/25/2013 9:55 AM

It's not an advantage or disadvantage, it's a rating. The manufacturer is telling you that stable operation is expected as long as the load does not exceed 1000 kVA and/or 0.9pf.

The batteries do not have any effect as long as they can provide 1000kW, adding an additional 1000kW of batteries will not magically double the output capability of the UPS, but it will probably cause it to shutdown or fail.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#3

Re: UPS P.F 0.9

08/25/2013 11:21 AM

Here is a white paper that applies to pf in a UPS. They seem to say that only 900 kW would be supported at a pf of 1.

__________________
Think big. Drive small.
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#4

Re: UPS P.F 0.9

08/25/2013 11:39 AM

So what is the restriction if I add 100 kw battery this ups is rated for 1000 kva and currents are same for 1000 kva and 1000 kw cases.

__________________
jinxnao
Register to Reply
2
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#6
In reply to #4

Re: UPS P.F 0.9

08/25/2013 12:47 PM

The restriction is the UPS, not the battery*. A 1000 kva UPS rated for a .9 power factor can deliver only 900 kW, regardless of the size of battery supplying it. (In the days of mainly inductive power supplies this was less of an issue.) Here is another paper that states this more concisely than the first paper I provided.

*Typically the existing battery can supply 10% more power easily, for a reduced time period.

__________________
Think big. Drive small.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #4

Re: UPS P.F 0.9

08/26/2013 3:37 PM

The currents won't be the same, though. They will be larger.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#9
In reply to #4

Re: UPS P.F 0.9

08/26/2013 8:05 PM

Pl do not confuse Selection or sizing of battery with with sizing of UPS.

1. The UPS will work even with Zero or no battery, only you will loose power to load moment the main supply is lost. That means in this case UPS is just regulating mains supply to a clean supply defined by specifications of UPS for Output parameters.

2. Batteries are defined by AH rating. Further these are classified from application point as slow discharge (Discharge rate is low enough that the battery is fully drained in 8 to 10 Hours), Medium Discharge, (battery is being drained out in 2 to 5 hours) and heavy discharge (Battery is being fully drained out in less than an 1 hours).

For UPS normal back time is few minutes to max. 1 to 2 hours.

For Example, 5 min. Back up time, sufficient for safe shut down of your computer and save data or for DG Set to Start and take the source. In this batteries selected will be of High Rate of Discharge.

Or say 2 hours for very expansive equipment as Power Plant or Grid, so that even if DG Set fails to start, the lubricating system of turbine and its barring gear can be run for period enough for shut down. In this case batteries selected will be for Medium or Moderate Rate of Discharge.

Similarly batteries of UPS you are referring must have been designed for certain back up duty. If you reduce the capacity of batteries or increase the load, the back time will be reduced. And if the battery selected is of Medium Duty, after reducing its size, keeping load same may result in High rate of drain and batteries life will suffer (Shedding of active material from plates and short circuiting of plates).

As stated Earlier, the UPS is not a dynamic machine, like 3 phase generator, where you can change excitation and manage any Power Factor.

UPS is a Static machine converting DC to AC and internally designed for unity PF. The reactive demand of Load is balanced by keeping capacitors.

Example if you specify in your order, 100kVA 0.8PF UPS, which is 80kW + 60kVAR. The UPS is basically manufactured as 80kW and to meet 60kVAR inductive load he will use 3 phase 60kVAR Capacitors in the output of UPS. Hence electronics inside UPS always sees 80kW load.

Therefore if the Load PF is better, we can not expect increased output from UPS - its electronics is designed for 80kW only.

Well I learnt above hard way. In 1988, I had sold once UPS of 400kVA to Petroleum Organisation in Oman - Customer wanted same rating for rating between 1 to 0.8PF- for which UPS had to be heavily derated. That was my first sale and working with UPS. After that I sold one more to Customer for 1600kVA the next year and by then I had become, so called, an expert on UPS (we sold Merlin Gerin UPS against most popular of ABB then BBC) Merlin Gerin (now Group Schneider) were so happy with out performance that they nominated my company as authorised dealer. That was my last working on UPS - after that I moved to Diesel Power. If I have to work again on UPS, I have to freshen up with latest technology.

Register to Reply
Commentator

Join Date: Aug 2008
Posts: 82
#5

Re: UPS P.F 0.9

08/25/2013 12:15 PM

Adding battery can increase Back-up hours for the system ; not for the power rating .

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#7

Re: UPS P.F 0.9

08/26/2013 1:40 AM

Please note that UPS is not a dynamic machine which can generate kVAR. UPS are designed for say 500kVA, 0.8PF. This is the rating at 0.8PF lagging and reactive current is supplied by power capacitors provided.

Therefore if you are using UPS at any other PF, there is heavy derating because of current rating of its component and change in efficiency. For actual derating please refer to the manufacturer of UPS.

Increasing or decreasing AH capacity of Batteries can not change the rating of UPS but only effect the back up time at given discharge rate or load.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10
In reply to #7

Re: UPS P.F 0.9

08/26/2013 9:23 PM

FBD, You are correct in your statement, "...If I have to work again on UPS, I have to freshen up with latest technology...", it's time to join the 21st century. Modern electronically controlled UPS/inverters are quite capable of dealing with both leading and lagging pf loads, it's called "P-Q control", and can be specified for high end commercial UPS/Inverters.

From this (modern) article:

"...Many UPS modules, especially the older legacy type, are not designed to support higher power factor loads and must be de-rated accordingly because more of the KVA units capacity must be used to support the load. Newer UPS designs are more compatible with and are rated to support leading power factor loads with little or no de-rating due to their output filter design and controls. Often this problem is not apparent up front because the initial loads on the UPS are a small percentage of the full load rating so the system is naturally de-rated. However, as the loads increase and become closer to the full load, this problem becomes more evident.."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#11
In reply to #10

Re: UPS P.F 0.9

08/27/2013 1:19 AM

RAM,

Noted your comments with thanks. The P-Q control suggested by you is similar to additional STATCON (static condenser and reactor controls) which is very expansive.

I remember that STATCON of ABB installed by a cold rolling mills about 4 years back in north India, cost the firm more than Rs. 10 million for a rating of 1600kVAR, which is some what the cost of conventional UPS itself. As I said earlier I am not familiar with latest design of UPS but if P-Q Control or STATCON has to be added to make UPS accept any PF without derating the cost will be almost twice of conventional design.

Economy and competitiveness dictates it would be better to oversize conventional UPS for unity PF than to add on another expansive system to it.

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jinxnao (1); K_Fry (2); powersolutionsFBD (3); PWSlack (1); RAMConsult (2); redfred (1); sivaa (1)