Derating Factors for Cable

08/26/2013 4:53 AM

I need the derating factor for the cable that to be laid under ground in trench. Specifically i need the groupn rating factor for the under ground cable. in IS 3961 there is certain graph fig 1 to fig 4 but these are not sufficient to obtain the data fior different combination. Please help. Any vendor catalog that contain the specific group rating factor as mentioned will also be very usefull .....please help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Derating Factors for Cable

08/26/2013 9:46 AM
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Derating Factors for Cable

08/26/2013 3:29 PM

Good ol' British Standard 7671 gives full protocol.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: Derating Factors for Cable

08/26/2013 10:55 PM

Sir,

The cable size has to be large enough so the heat losses into the surrounding soil do not heat the cable beyond the temperature the insulation is rated for. Knowing the configuration of adjacent ducts in the cable bank and the temperature rating of the insulation are both essential. Keep searching, whether in the resources already suggested by the other posts, or in the NEC (USA), which has a number of tables for different duct bank configurations, or other sources. Realize, however, that these tables or charts are only a part of the answer.

--JMM

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#4

Re: Derating Factors for Cable

08/27/2013 5:01 AM

Dear Mr. SARASWAT,

A simple search and look at CR4 SEARCH will give plenty of replies/responses.

Pl. look at the link given below.

http://cr4.globalspec.com/search/sitesearch?do=show&srchobjs=t%2Cc&order=asc&fs=12&sort=textmatchrank&srch=CABLE%20DERATING%20FACTORYou can

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Derating Factors for Cable

08/27/2013 5:33 AM

...which makes this thread a duplicate.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8
In reply to #5

Re: Derating Factors for Cable

10/27/2013 12:28 PM

Dear Mr. PWSlack,

Indeed, It is repeat.

This topic discussed 5 times earlier, and the link given by me is one such repetition.

DHAYANANDHAN.S

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#6

Re: Derating Factors for Cable

08/28/2013 12:29 AM

The derating factors of power cables are dependent on many factors depending on ambient temperature,depth cable trench,soil conditions distance of the cable length and more .Normally cable manufacturers provide the derating factors of their cable.

http://www.cablesizer.com/help/principles/

cable sizing.

" 3.1 Base Ampacities

International standards and manufacturers of cables will quote base ampacities for specific types of cable constructions (e.g. copper conductor, PVC insulated, 0.6/1kV voltage grade, etc) and a base set of installation conditions (e.g. ambient temperature of 40°C, installation in conduit / raceways, etc). It is important to note that these ampacities are only valid for the quoted types of cables and base installation conditions.

3.2 Installed / Derated Ampacities

When the proposed installation conditions differ from the base conditions, derating (or correction) factors can be applied to the base ampacities to obtain the actual installed current ratings.

International standards and cable manufacturers will provide derating factors for a range of installation conditions, for example ambient / soil temperature, grouping or bunching of cables, soil thermal resistivity, etc. The installed current rating is calculated by multiplying the base current rating with each of the derating factors, i.e.

Ic = Ib . kd

where Ic is the installed / derated ampacity of the cable (A)

Ib is the base cable ampacity (A)

kd are the product of all the derating factors

For example, suppose a cable had an ambient temperature derating factor of kamb = 0.94 and a grouping derating factor of kg = 0.85, then the overall derating factor kd = 0.94x0.85 = 0.799. For a cable with a base ampacity of 42A, the installed / derated ampacity would be Ic = 0.799x42 = 33.6A."

Plesase read IS 1255 1983 .This gives the IS standard for selection and laying of under ground cables.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Nov 2009
Posts: 27
#7

Re: Derating Factors for Cable

08/28/2013 12:43 AM

Dear All

Please note I have not asked about how to do the cable sizing and even also not asked about of the basic of derating factor. I have seen the topics discussed earlier. I have specifically asked about the grouping factor for the under ground cable as per indian standard. this is given in IS 3961 fig 1 to 4 . which is not sufficient to derive the data.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: