No Load Current of Motors & Pumps

08/30/2013 12:09 AM

I have got induction motors & monoblock pumps in our company.i want to do a study on the no load current of motors.the motor which got rewinded 4-5 times certainally its no load current increases from its standard.due to this its efficiency reduces.if i got a table of no load current according to its hp .then i can be able to do my exercise.can any one help where i can get this data or any other view on this pl. Suggest.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#1

Re: no load current of motors & pumps

08/30/2013 12:42 AM

You need to contact the original motor manufacturer. There has been significant improvement in motor efficiency in recent years and some manufacturers have literally left the others in the dust.

You will also need to specify whethere the pumps are coupled to the motors during the test or the motors are free standing since the resistance of the pump will influence the current draw.

Also, if motor current is drawing higher current, then rewinding appears to have used larger diameter wire, or lesser length (fewer turns) either of which will change other motor characterisitics in addition to no-load current.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#14
In reply to #1

Re: no load current of motors & pumps

08/31/2013 6:06 AM

Fewer turns will increase the no-loas current, but larger diameter wire will decrease the no-load current....

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: no load current of motors & pumps

08/30/2013 1:17 AM

Measure it.

The exercise is a waste of time. Don't bother, you won't know what the data means anyway.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: no load current of motors & pumps

08/30/2013 4:42 AM

Ideally, the no-load current of all motors is zero. The reason is that if the motor is not doing anything, the best thing to do is switch it off.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8
In reply to #3

Re: no load current of motors & pumps

08/31/2013 2:11 AM

Not true.

For AC induction motors you have the magnetizing current, that aproaches a 90 deg phase shift. Depending on the motor, it may be 30% of the total full load current.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #8

Re: no load current of motors & pumps

08/31/2013 3:57 PM

So, why not switch it off?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#17
In reply to #3

Re: no load current of motors & pumps

09/01/2013 12:22 AM

Dear Mr. PWSlack,

You are right, when Motor is switched off, current is zero. But when the motor is started, motor reachs rated speed, and it is not loaded, the current drawn by the motor,will follow the path of Circle Diagram, which you know, and during No-Load, you also know that the Power Factor will be very less.

Pl. explain your point further,

DHAYANANDHAN.S

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: No Load Current of Motors & Pumps

08/30/2013 10:46 AM

As you can see from the previous responses, this is mostly a fruitless exercise. There are no tables, no two motors of the same size but different models will have exactly the same no load current, it can range from 20-50% of the FLC depending on the motor design. The current that you measure with no load on the motor is at such a low power factor that it means next to nothing. The only possible value it has is specific to each individual motor as empirical data that is evaluated over time to detect a trending change that might indicate impending failure. Even then, it is subject to differences in applied voltage and current imbalances, so all of that would need to be tracked and logged concurrently, then used to adjust any findings. The value of that dims with the time and effort expended on it.

Besides, there is no direct correlation to unloaded current as a meaningful indicator of what the efficiency under load will be anyway. So trying to equivocate it is like trying to determine the fuel efficiency of a car that sits idling in a parking lot. What's the point? If it is doing no meaningful work, why is it still running?!

If what you are after is a way to determine whether or not to continue rewinding a motor or deciding to replace it because it is becoming too inefficient, the only proper way to do that is to measure the input kW (absorbed power) under a specific load and compare that to a known efficiency model that you have created with an optimum installation. A dynamometer is a good tool for that, but again, you have to weigh the costs of doing all of this against the potential gains from it. It might be easier to just make a record of every NEW motor installation under a specific loading (for example flow in a pump) and keep it as the efficiency model, then periodically check it against that model, or check it again it after each rewinding.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: No Load Current of Motors & Pumps

08/30/2013 11:12 PM

If motor manufacturers print the value of no load current in the motor name plate there won't be a problem. Why not BEAMA,NEMA,ISO do it?.

__________________
pnaban
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: No Load Current of Motors & Pumps

08/30/2013 11:19 PM

"Why not BEAMA,NEMA,ISO do it?."

Because:

  1. There is no value to the information
  2. If it is shown, ignorant people will be taken advantage of by unscrupulous salespeople who will try to use that information to make them believe there IS value to it, and that their numbers (higher or lower) mean something valuable compared to someone else' numbers (higher or lower).

Bottom line, it would just create needless confusion.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #6

Re: No Load Current of Motors & Pumps

08/31/2013 12:06 AM

Value of no-load current of a new motor serves as a guideline for testing a motor after repairs,although it need not be exactly same due to damage to stator,bearing etc

__________________
pnaban
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 20
#11
In reply to #7

Re: No Load Current of Motors & Pumps

08/31/2013 3:33 AM

Thanks for your suggestion i have tried to get the no load current detail from motor manufacturerer & from internet but not find anything.now i have got somw brand new motors in our company i will checked there no load currrent & then compare it with the installed motor on machine.if suppose the no no load current is 30 percent high after replacing it i will gert the 30 percent energy dave. Is that s

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12
In reply to #11

Re: No Load Current of Motors & Pumps

08/31/2013 4:32 AM

Some manufacturers mention power factor,noise level,bearing sizes too in the name plate. Instead of writing to manufacturers or referring to their website users should get information at sight. Before internet was introduced imagine the situation-you write to them & wait?. I suggest to print size of capacitor required for PF correction as well as that for shunt capacitor type starter in the name plant.

__________________
pnaban
Register to Reply
2
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#9

Re: No Load Current of Motors & Pumps

08/31/2013 2:13 AM

Ashutosh, there is no mention of rating of motor in your message.

It is mono block pump hence could be a small motor.

It has been rewound 4 to 5 times.

It has lived its life better replace it.

If you are still keen, next time when it burns, after the stator is ceared of burnt winding, get a magnetising test on the core and you may find hot spots. This could be reason of increase of no load current and losses and could be frequent failures.

I will not suggest to re-insulate core plates, if hot spot is noticed - better in that case will be sell this in scrap and buy a new pump set. Reason for not insulating core plates being; 1. The core factor may become poor -> the rewinder will quietly remove few plates, this will have same effect - increased flux density -> increased no load (core) losses. Core may become loose in stator frame -> result in shifting with every start -> snapping of leads and short circuit. To avoid all subsequent problems - better to replace the pump motor set.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#10

Re: No Load Current of Motors & Pumps

08/31/2013 2:20 AM

Rewinding a motor should not significantly change its characteristics.

I used to work for Reliance Electric in their large AC motor plant in Canada. (500 to about 5000HP)

Occasionally we did do a rewind - burn out the old coils in an oven, and then rewind.

Depending on the insulation system, wire size, etc, you could actually end up with a superior motor.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#13

Re: No Load Current of Motors & Pumps

08/31/2013 5:50 AM

Don't bother about the no load current. This varies widely from maker to maker and local conditions.

As already suggested, try to check the kW reading when pumping against the expected kW theoretically needed to transport the required flow under the back pressure (or to what height...). This will give the overall efficiency of pump-motor assembly. Check against the pump chart that the pump supplier should give.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#16

Re: No Load Current of Motors & Pumps

09/01/2013 12:12 AM

Dear Mr. ashutosh goyal,

The No-Load Current will be in the range of 30% to 40% depending upon the Power Factor, and you draw the circle diagram, for your self and see. If it is above 40%, then re-winding is not proper and some error has taken place, knowingly or unknowingly.

DHAYANANDHAN.S

Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#18

Re: No Load Current of Motors & Pumps

09/01/2013 1:11 AM

Poster,

There is a lot of information you left out of your question.

  1. Why do you need to know the no load current?
  2. If it is for reference, then do as earlier posters have suggested.
  3. What is the HP of the motor?
  4. What information is on the data plate on the motor?
  5. What type of pump is the motor connected to? (Centrifugal, Positive displacement, Etc?)
  6. What type of fluid are you pumping?

Why don't you do this,

  1. Measure the current with the motor running not connected to the pump.
  2. Measure the current with the motor running connected to the pump without fluid. Don't run it too long dry! Just long enough to get your current reading.
  3. Measure the current with the motor running and pumping fluid at your rated flow and back pressure.

You're going to get 3 different numbers and that is the data you want. Next time you have a technical question, we need as much information as possible to help us help you!
BA

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ashutosh goyal (1); dhayanandhan (2); GW (2); JRaef (2); Just an Engineer (1); LAA_Lucke (1); lyn (1); Original_Macgyver (1); pnaban (3); powersolutionsFBD (1); PWSlack (2); rudy.leurs (1)