Cooling Tonage ??

08/30/2013 4:00 AM

We have a 650 Ltr Jackated tank (SS) for Purified Water Store with water temperature 80 C. We want to cool down the temperature up to 20 C withen 20 min for process requirement.

Cooling media Chilled water with temperature 7 to 8 C. What will be the chiller Tonage Capacity? Pump flow rate will be matched with chiller, so does we need flow control valve for the tank or just circulation of coolin water is enough?

Tank Dia: 2' and Max capacity of the tank 700 Ltr.

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cooling Tonage ??

08/30/2013 4:10 AM

650L ≈ 650kg.

From steam tables,

hf80degC - hf20degC = 251kj/kg.

Total cooling needed = 251kJj/kg x 650kg = 163150kJ divided by 20min ≈ 160kW.

Convert that to tons-fridge and "Robert is your mother's brother".

The sizing of the chiller needed is best entrusted to a specialised company with the intent of securing a purchase order.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Cooling Tonage ??

08/30/2013 4:42 AM

About 37.8, call it 40 tons of refrigeration. The pump will circulate ~120 gpm; piping and clearances in the jacket will need to be sized accordingly. If it is only the one tank, no control valve will be needed.

That said, I'm not sure the jacketed area can be large enough to accomplish this.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Cooling Tonage ??

08/30/2013 4:44 AM

<...not sure the jacketed area can be large enough to accomplish this...>

Absolutely. The proposition is a non-starter.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#4

Re: Cooling Tonage ??

08/30/2013 7:05 AM

Rethink your 20 minute criteria for cooling.

Unreasonably quick temperature demands made by unreasonable managers causes huge capital expenses......which, of course, get blamed on the engineer

__________________
We have met the enemy....and he is us. POGO
Register to Reply Score 1 for Good Answer
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Cooling Tonage ??

08/30/2013 7:37 AM

Update using back-of-the-envelope figures only:

  • The tank is in the order of a metre in diameter and a metre tall.
  • So the jacket area is of the order of 6m2.
  • An ambitious water-to-water heat transfer coefficient of, say, 500W/m2K would mean an initial cooling rate of 240kW. The energy to be removed is around 160000kJ, suggesting that there is a first-order system time constant of 680sec.
  • Things take 5 time constants to get to 99% of where they want to be, so the contents will take in the order of 3400sec, or the "thick end of an hour", to get close to the final desired temperature.
  • Therefore the cooling surface is too small to comply with the 20min criterion, by a factor of around 3.

So, to hell with the chiller plant for the moment, because a rethink is required either:

  • on the heat exchange surfaces, or
  • the Process Requirements, or
  • both the above
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#8
In reply to #5

Re: Cooling Tonage ??

08/30/2013 9:22 AM

Yes, differential equations do become useful.

I also wonder about freezing consuming some of the energy here in this rapid cool down. With an insufficient surface area, such a large volume of water to cool and this absurdly short time period to cool this. I know the OP states a 7~8C cooling water will be used but what cools this water?

Unlike many economic "laws", the laws of Physics and Mathematics cannot be waived for a business venture.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Cooling Tonage ??

08/30/2013 7:43 AM

I suggest you size your chilling capacity to match your "on demand" process requirements, rather than chilling and storing your entire capacity, you'll save more money that way

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Cooling Tonage ??

08/30/2013 7:52 AM

GA for a good Process Rethink. Chill before use means that the contents can remain bateria-free until there is demand, and the low temperature water becoming available in seconds. Although the forum does not know the Process use of the water at this time (and why would it given a Mechanical Engineering posting? [rhetorical question - NNTR]), it is being kept at 80degC for a similar reason.

One wonders how the jacket services are being arranged with the proposal for a both a heating medium and chilled water to be available in the same jacket. Perhaps there is a vent and an air inlet to blow the terminating service back down its return main? So long as the treated chilled water doesn't go back down a steam condensate return line then maybe all will be well. Of course, the preferable chill-on-demand solution overcomes that particular problem.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: May 2012
Location: Ahmedabad, INDIA
Posts: 25
Good Answers: 1
#9

Re: Cooling Tonage ??

08/31/2013 12:44 AM

dear u haven't provided on what flow you are circulating chilled water (7-8) from your 650 ltr jacket

without knowing chilled water circulation flow we can not assume Refrigeration TR capcity

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Sep 2007
Location: I am located in Mumbai,India.
Posts: 125
Good Answers: 2
#10

Re: Cooling Tonage ??

08/31/2013 12:57 AM

If you can use water cooling in place of chilled water to cool from 80 C to about 40 C, this will save over 50% of energy. For further cooling up to 20 C, you can use chilled water. Of course, this way it will take more time to achieve the desired temperature. But this will save a lot of energy.

__________________
Rajesh
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #10

Re: Cooling Tonage ??

09/02/2013 4:26 AM

The total energy to be removed from the stored water in the original post concept is independent of the method of cooling.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #12

Re: Cooling Tonage ??

09/02/2013 4:33 AM

The energy required to do it would change, though.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Sep 2007
Location: I am located in Mumbai,India.
Posts: 125
Good Answers: 2
#14
In reply to #10

Re: Cooling Tonage ??

09/02/2013 6:21 AM

I agree, my view is to use room temperature water in place of chilled water to the extent possible to save precious electrical energy required for chilling unless the time factor is critical.

__________________
Rajesh
Register to Reply
Associate

Join Date: May 2012
Location: Ahmedabad, INDIA
Posts: 25
Good Answers: 1
#11

Re: Cooling Tonage ??

08/31/2013 4:57 AM

if you are asking how much TR your 650 ltr tank will use to cool 80 C temp to 20 C in 20 minutes

from your existing chiller you are circulating chilled water of 7-8 C at 1000 l/hr flow from tank jacket

you might get jacket leaving chilled water temperature near about 47

your DT will become 40, chilled water circulation is 1 m3/hr, so you will get 13.22 TR/Hr

here you want to do the same in 20 minutes so Total refrigeration TR you will needed is 13.22 x 3 = 39.68

from above mentioned condition you can assume how much TR your 650 ltr consuming for refrigeration from your existing chiller system

if you are planning to buy a new portable chiller you need to go for 50-55 (considered other heat losses ) TR capcity with assesories of flowing chilled water at 1m3/hr

Register to Reply Score 1 for Off Topic
Anonymous Poster #1
#15

Re: Cooling Tonage ??

09/02/2013 6:35 AM

A chiller tonage of 392 or 440 Hz is the most musical.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16
In reply to #15

Re: Cooling Tonage ??

09/02/2013 6:36 AM

Sounds like a G A to me!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Fredski (1); MJCronin (1); MUSUTH86 (2); PWSlack (5); redfred (1); rsalaskar (2); Tornado (3)

Previous in Forum: center of gravity for L shaped objects   Next in Forum: Need Help in Designing

Advertisement