Dear
All
I
need your help in finding out cause for the flash over incident occured in our
company.I will brief the incident below.
While
an electrician was opening the door of a cubicle (inside MCCB - breaker,
control and protection circuit) of a LT(440V) motor feeder in a Low Voltage
(440V) MCC panel, sudden flash over occured towards his face and got burnt.
Other
points to be considered :-
1)
portion of the motor POWER CABLE got burnt 3 days before this incident at the
motor terminal box end due to an external Fire.
2)
Breaker was in switched OFF position, but busbar was alive and power was there
at the input side of the Circuit breaker
3)
Electrician told me that he did not use any tool , just opened the cubicle door
only.
4)
The short circuit (cause for the flash over ) was occured at the input cable
side(cable coming from busbar to the input side of the breaker) .
5)
dust was there inside the cubicle
6)
On investigation bakelite cover of the circuit breaker was showing zero megger
value , means short circuited
7)
Short circuit between two or three phases or between phase and ground , either
of them
We
could not find out a solid reason for the flash over , kindly provide your
thoughts to help us.