Anonymous Poster #1

Voltage Drop in Three Phase Lighting Circuits

09/04/2013 7:13 PM

Hi,

I have a technical question and would appreciate if somebody could point me in the right direction.

If I have a set of lights along a highway. (let's assume there's 6 250W HPS spaced evenly at 50m and the first light is 50m from a 3ph. DB, i.e from the DB to the last light, there's 300m)

The lights are each 250W single phase but the way the reticulation is done is like this:

Two actives/phases are run to each light column that has an auto transformer at its base which converts 400V(3ph) to 230V(1ph). The phases that get connected to the lights alternate so the lights would be connected: BW - WR - RB - BW - WR - RB. (Red, White, Blue are phases)

I need to find a quick way of checking the voltage drop in the circuit assuming I know the length and the cable size. I also assumed that each light(at the autotransformer) would use 250W/400V*0.8 = 0.78A - but I'm not sure if I did that correctly :(

I'm confused with the current that each autotransformer would use and the return path of the current (since there's no neutral I presume) and how the currents interact at each branch! I've done a similar calculation with the single phase connections(active and neutral connected to a light) and that was simple but this one is a little bit more confusing. Please help!

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Voltage drop in three phase lighting circuits

09/04/2013 7:28 PM

Let's start with basics and assume you have done no research for your homework assignment.

When does your homework have to be handed in, it could take quite a while to arrive at an answer.

Just to add, why would you use an autotransformers or any transformer for that matter. A neutral core in the cable makes economic sense to me.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Voltage drop in three phase lighting circuits

09/04/2013 7:49 PM

I don't see a point in any of your questions but OK let's say I have plenty of time so time is not an issue...

Secondly, the setup is as I described it in my first post, there's no point in reinventing the wheel and "imaganing" that there's no autotransformer. The light fixture comes with a column that has an autotransformer at the base of the column which output is then connected to the lights ballast.

I assume advantages are that you don't need a neutral, smaller current and hence smaller voltage drop so longer circuits are achievable but I really don't want to go into a discussion of comparing this circuit arrangement with some other arrangement.

Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#8
In reply to #1

Re: Voltage drop in three phase lighting circuits

09/04/2013 9:32 PM

I liked your response better than the OPs

Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Voltage Drop in Three Phase Lighting Circuits

09/04/2013 8:30 PM

Voltage drop?

What will that tell you?

I'd use a meter if you really want to know. You should have a fair idea what the supply voltage is. Measure it at the last light in the string.

But, what do I know?

Reply
Anonymous Poster #1
#5
In reply to #3

Re: Voltage Drop in Three Phase Lighting Circuits

09/04/2013 8:49 PM

I need to find the voltage drop to check if the value is compliant (less than 5% of the supply voltage)

I don't have a luxury of using a meter but I would love to do a small scale experiment in the lab if I could. My main problem is understanding how the currents are interacting at each "branch out".

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Voltage Drop in Three Phase Lighting Circuits

09/04/2013 8:31 PM

Look up the wire data (ohms per 1000 ft). Determine how much current in each wire and apply Ohm's Law. I don't know if the autotransformers are set up that way, but they might have taps for adjusting to the modestly different primary voltages.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Anonymous Poster #1
#6
In reply to #4

Re: Voltage Drop in Three Phase Lighting Circuits

09/04/2013 8:52 PM

Hey,

I have cable data, that's easy but I don't know how to determine current in each wire that's where I need some assistance. There's no taps on the AT, only two actives are connected to it and that's it. Have a look at

http://www.gelighting.com/na/grainger/downloads/ballast/10-0102GraingerSS-480V-277VAutotransformers.pdf

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Voltage Drop in Three Phase Lighting Circuits

09/04/2013 9:12 PM

When all else fails :1-888-GEBALLAST (432-2552)

Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9

Re: Voltage Drop in Three Phase Lighting Circuits

09/04/2013 9:37 PM

"the return path" on 3 phase?? most interesting concept

Reply
Member

Join Date: Oct 2012
Posts: 7
Good Answers: 1
#12
In reply to #9

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 12:33 AM

The luminaire is connected to the two actives. Imagine a 800W luminaire rated for 400V connected to the two of the three phases. What would be the running current in one of the phases? So, if it's conneced to the Red and White phase with 6mm PVC single core cable 50m distance, what is the voltage drop that I need to compare to the standard so I see that the installation is compliant, that's the question. The third phase (blue) is not loaded...

Of course there would never be just one light on the circuit and usually the connecting phases would alternate so the blue phase would be loaded as well but I guess you can see the point?

Regards,

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10

Re: Voltage Drop in Three Phase Lighting Circuits

09/04/2013 11:32 PM

So you know the loading, the voltage and the length.

Why can't you calculate the volt drop?

I don't know the regulations you work to. In the UK we use BS7671 which sets a maximum volt drop of 3% for lighting circuits. Power is allowed 6%.

A few years ago I wrote a spread sheet for electrical calculations (it's still growing) which includes cumulative volt drop. It's now in wide use by members of three UK electrical web sites.

As you're an anonymous poster I can't help.

__________________
The reports of my death are greatly exaggerated.
Reply
Member

Join Date: Oct 2012
Posts: 7
Good Answers: 1
#11
In reply to #10

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 12:26 AM

Hey,

I was posting as anonymous because I don't post much to this forum (even though I follow it a lot) and I'm slightly intimidated by all the smartasses that come along and try to ruin almost every topic with their smartass comments without actually providing any value/help or anything that even resembles an answer to the question OP asks... I admit a lot of questions asked here are silly and repeated but sharing the knowledge is supposed to be something purer than just acting smart in front of other people who ask for help.

Now that I've said that, I wouldn't mind having a look at your spreadsheet even though I'm in Australia as the standards are I believe somewhat similar... :D

Cheers,

Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13
In reply to #11

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 12:40 AM

When all else fails :1-888-GEBALLAST (432-2552)

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #11

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 3:30 AM

The practice does make tracking response threads rather difficult, and abstruse because of it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#16
In reply to #11

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 7:45 AM

slightly intimidated? at what? most of us here are grownups. I can't speak for everyone but I know most of the regulars around here don't come here out of obligation to perform work for free. most come for a bit of commradery and a bit of levity.Had you began your post with, "I have a lab/homework assignment and I'm a bit stumped and could use a little help", you would have gotten a different set of replies, seeing as how you know lengths and voltages already your cables drop should have already been clear. you didn't supply resistance values on your t-formers and since they probably aren't superconductors we are just left to guess, or joke about the formation of your question. I wont do your assignment for you but I don't mind aiding you in understanding the concepts involved. btw, if I were you I'd make an effort to befriend Mr Slack, that can only benefit you.

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#21
In reply to #16

Re: Voltage Drop in Three Phase Lighting Circuits

09/06/2013 2:28 AM

GA!

__________________
The square root of nothing is what you make it!
Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#22
In reply to #11

Re: Voltage Drop in Three Phase Lighting Circuits

09/06/2013 8:20 AM

Hi Jay! Bad habit, posting as anonomous! Even I have been known to snipe at anons. I thought this question was quite reasonable though.

I can't understand why simple ohms law should not apply either to each line separately, so I am waiting for a good answer too! Even though it was my trade for so many years, I never "designed" a multi phase circuit, and many three phase mysteries remain a dark art to me.

(Pure laziness on my part...I admit it. More fun to study history than electrics.)

There are really knowledgable people like RedFred and others who get it though. We both await the answers!

Cheers mate! Hoist a lager for me!

__________________
If it was easy anybody could do it.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 3:29 AM

Why British Standard 7671 is such an unknown and its application so uncommon is a complete mystery here <sigh>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
2
Member

Join Date: Oct 2012
Posts: 7
Good Answers: 1
#17
In reply to #14

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 9:42 AM

Problem solved, thanks for your help guys...

The rated current of the light gear was found to be around 0.7A (luminaire gear consists of an autotransformer+ballast). The current is per phase, i.e. current in each of the two actives connected to the gear is 0.7A on 400V when running a 250W lamp.

The voltage drop is then easily found from the distance and cable impedances.

Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#19
In reply to #17

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 9:38 PM

So what percentage volt drop did you calculate?

__________________
The reports of my death are greatly exaggerated.
Reply
Power-User
United States - Member - NE, USA Hobbies - Target Shooting - New Member Engineering Fields - Aerospace Engineering - Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jul 2007
Location: USA
Posts: 199
Good Answers: 6
#18
In reply to #14

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 2:01 PM

I don't know British Standard 7671 ... I assume because I am in the USA.

Would that be why?

If not, alternatively, it is: because I am lazy.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#20

Re: Voltage Drop in Three Phase Lighting Circuits

09/05/2013 10:45 PM

Did you use the pf and loss in control gear from the manufacturer in your calculation?.

__________________
pnaban
Reply
Reply to Forum Thread 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); brich (1); Fredski (3); Jay Tesla (3); JCase (1); lyn (3); pnaban (1); PWSlack (2); TonyS (3); Tornado (1); Yusef1 (1)