Anonymous Poster #1

Transformer Rated in kVA and Not kW

09/10/2013 8:00 AM

Hi

why is transformer rated in kVA and not it kW, i know it doesn't have pf (cos factor), the difference between kVA & kW is pf, but other than that, anything to add, knowledge shared.

thanks in advance.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Transformer rated in kVA and not kW

09/10/2013 8:07 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United States - Member - Lifelong New Yorker Popular Science - Biology - Animal Science Technical Fields - Technical Writing - Technical Writer

Join Date: Mar 2008
Location: NY
Posts: 2313
Good Answers: 59
#2
In reply to #1

Re: Transformer rated in kVA and not kW

09/10/2013 8:15 AM

The threads were started by two different users, but this user may find some of those comments useful. Thanks!

Reply
Participant

Join Date: Sep 2013
Posts: 1
#3

Re: Transformer Rated in kVA and Not kW

09/11/2013 2:43 AM

Rating of any equipment is decided by heating/losses of that equipment.In a transformer

heating is due to ohmic losses which are directly proportional to current,eddy current and hysteresis losses are directly proportional to voltage.so we just use KVA to represent transformer rating.

Reply