Running a 60 Hz Heating Element at 50 Hz

09/10/2013 9:27 AM

What will happen if you use a 120 V 60 Hz 1800 W heating element at 120 V 50 Hz.

Thanks

Berger316

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Running a 60 Hz heating element at 50 Hz

09/10/2013 9:34 AM

It will get as hot as usual, however if there is a fan it will run slower. If this a compact heater that relies on the fan to move a lot of air then it may overheat. Fans are cube law devices so that running it at 83% of normal speed will reduce the air volume to 57% of normal.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Member

Join Date: Jan 2008
Posts: 9
#3
In reply to #1

Re: Running a 60 Hz heating element at 50 Hz

09/10/2013 9:39 AM

It is a heating element only.

No motors involved.

Thanks

Berger316

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #1

Re: Running a 60 Hz heating element at 50 Hz

09/10/2013 10:04 AM

Flow is proportional to speed, pressure to speed2, and power to speed3.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#24
In reply to #4

Re: Running a 60 Hz heating element at 50 Hz

09/11/2013 8:39 AM

I'm curious who voted this OT; clearly somebody doesn't know their affinity laws.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#26
In reply to #24

Re: Running a 60 Hz heating element at 50 Hz

09/11/2013 10:20 AM

We can fix that.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 9:35 AM

If it's a normal resistive heating element there'll be no difference between using 50Hz and 60Hz.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 10:41 AM

When energised, either:

  • it will produce around 1800W of heat or
  • it won't

depending on the overload protective devices on the circuit onto which it is connected.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13
In reply to #5

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 11:22 PM

How do you work that out?

It's a resistive load.

It's voltage dependant.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #13

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 3:15 AM

Think about it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#28
In reply to #5

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 11:07 AM

I think you need to specify the conditions to produce 1800 watts or you are in the OT zone. The overload device will be in one state or another, but not controlling the wattage over a range.

Tony has a point.

__________________
Plenty of room here
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#6

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 10:59 AM

I would be surprised if you could tell any difference how this heating element worked using these two different power distribution frequencies. Now if this heating element is part of any appliance that is operated by an internal clock mechanism you might have things actually running 6/5 longer than the time you expect. Most clocks today run off of an internal time reference so not even this is likely.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 12:11 PM

The heating element will be at zero state(not producing any heat) 100 times a second, at 50 Hz, instead of 120 times a second at 60Hz.

So, my uneducated guess would be a very slight increase in heat produced.

Measurable? Don't know.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #7

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 6:11 PM

Notice that Ohm's law does not have frequency in it, only inductance and capacitance are affected by frequency, so for a purely resistive element frequency has no effect, even down to 0 Hz (DC).

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 6:39 PM

Maybe I'm thinking about induction heaters. Now, I'm not going to sleep tonight until I figure this out. (that's not really true)

Let's see what Wiki says.

Oh, never mind, I defer to you.

Register to Reply
Anonymous Poster #1
#10
In reply to #8

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 6:53 PM

I don't want to milk pigeons with boxing gloves. But considered the element is a wirewound coil element, it has some inductance too. Just to help out Mr. Lyn.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#23
In reply to #8

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 8:27 AM

This is correct!

But then please explain your #20 after your #5 contributuion.

Thanks

Register to Reply Score 1 for Off Topic
Associate

Join Date: Mar 2011
Posts: 34
#30
In reply to #8

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 3:37 PM

If the windings for the oven are coiled, there could be a change in inductive reactance.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#11
In reply to #7

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 7:33 PM

The element will also be at maximum state 100 times versus 120 times per second.

There should be no measurable diffference.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #11

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 7:42 PM

Don't confuse me with facts.

Point well taken.

Register to Reply
Guru

Join Date: Jun 2009
Location: Bangalore, India
Posts: 725
Good Answers: 24
#32
In reply to #11

Re: Running a 60 Hz Heating Element at 50 Hz

09/12/2013 9:55 AM

The thermal mass of the element will even out these excursions.

__________________
bioramani
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#16
In reply to #7

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 11:51 PM

Dear Mr. lyn,

The Heat produced in a Pure Ressistance Circuit is dependent on Two Factors.

1. Voltage. 2. Resistance.

Power in pure RESISTIVE CIRCUIT is governed by the equation,

P = V^2/R or I^2/R or V x I and in this Equation, NO FREQUENCY is INVOLVED, since it is a PURE RESISTANCE CIRCUIT.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#17
In reply to #16

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 11:59 PM

Yes, you are right. I mis-spoke, again.

Thanks.

Register to Reply Good Answer (Score 3)
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#14

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 11:27 PM

berger316-

A resistive heater element operating anywhere between the common (or not so common) power frequencies of DC to 400 Hz will not have any noticeable difference in heat output.

Also at 1,800 watts, 6,120 BTU's, it should be able to thaw out you derriere and even your hands at the same time.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#15

Re: Running a 60 Hz Heating Element at 50 Hz

09/10/2013 11:43 PM

Dear Mr.berger316,

For Heating Element, the Frequency Variation has nothing to do (OR) it can be termed as HEAT OUT PUT INDEPENDENT of Frequency. It will develop same Heat.

HEAT developed depends upon the VOLTAGE and RESISTANCE of the element.

The Heat produced in a Pure Ressistance Circuit is dependent on Two Factors.

1. Voltage. 2. Resistance.

Power in pure RESISTIVE CIRCUIT is governed by the equation,

P = V^2/R or I^2/R or V x I and in this Equation, NO FREQUENCY is INVOLVED, since it is a PURE RESISTANCE CIRCUIT.

DHYANANDHAN.S

Register to Reply Score 1 for Off Topic
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#18
In reply to #15

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 12:27 AM

Quote:HEAT developed depends upon the VOLTAGE and RESISTANCE of the element.

The Heat produced in a Pure Ressistance Circuit is dependent on Two Factors.

1. Voltage. 2. Resistance.

Actually, the current and resistance are the predominant factors and since current can be changed by the total impeadance the inductance and capacitance can change the output slightly, but not enough to be noticible with only a 20% change in frequency. Resistance will be predominant.

Register to Reply Score 2 for Off Topic
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#34
In reply to #15

Re: Running a 60 Hz Heating Element at 50 Hz

09/12/2013 12:19 PM

Formula 2 isn't correct:

P= U X I and (U = R.I ) so:

P = R.I.I or

R I square or U square/R

__________________
Plenty of room here
Register to Reply
Power-User

Join Date: Jun 2013
Posts: 145
Good Answers: 5
#46
In reply to #34

Re: Running a 60 Hz Heating Element at 50 Hz

09/14/2013 12:34 PM

R I square or U square/R

Are I square or You square'er

Just a little comic relief

Register to Reply
Anonymous Poster #2
#19

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 2:12 AM

Heating element will produce more heat.

Heat produced in a heating element is only due to ohmic losses(hysteresis losses are neglected ).On decreasing frequency net impedance will decrease and as a result net current will increase & consequently ohmic losses will increase.

ohmic losses=I^2*R.

Register to Reply Off Topic (Score 6)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21
In reply to #19

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 3:17 AM

WALOOB

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#22

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 3:31 AM

I am surprised to see so many inputs on a simple discussion.

Basically one needs to inform the member raising the enquiry that it is 120V RMS, that is Root Mean Square value or equivalent DC voltage that will produce the same effect and thus is independent of frequency.

If someone puts more difficult or genuine queries - which require expertise in Electrical Engineering and Experience, I generally see comments like: Ask manufacturer, refer to manufacturer's O&M manual, hire an expert, What the standard says, or search the web, do your homework first or polish the wire etc. etc. a sad.....

Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#25

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 9:51 AM

It will require adding a "flux capacitor" in order to avoid time warp interference.

The element will produce an amount of watts based upon and limited only by the impedance in/of the circuit and the voltage magnitude applied.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#27

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 10:35 AM

After reading most of the comments, I think there is a practical answer and a technical answer. From a practical standpoint, at either 50 or 60 Hz, the element is "ON" 50 % and "OFF" 50 %. So, not much heat difference if, as was pointed out there is no difference in material flow over the element related to the frequency change.

Exaggerating this case produces a different set of circumstances. If Hz is 0 (DC, on state), the element should run hotter, may even burn out, 0 Hz (DC, off state) no heat at all.

My feeling is from practical standpoint, no difference. (Based on testing cooking equipment rated for 50 Hz use on 60 Hz, seeing no noticeable difference in control cycling, but not actually running product to see the effect of load, and no complaints from customers using the equipment) From technical standpoint maybe some measurable difference.

Point was made that there is some inductance - changes everything! -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#29
In reply to #27

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 11:29 AM

"the element is "ON" 50 % and "OFF" 50 %" - only if the supply is a unipolar square wave (i.e. chopped DC)!!!!!

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#38
In reply to #27

Re: Running a 60 Hz Heating Element at 50 Hz

09/13/2013 4:00 PM

From a practical standpoint, at either 50 or 60 Hz, the element is "ON" 50 % and "OFF" 50 %.


Not true.

The negative side of a sine wave is not "OFF". It is the equivalent of a reverse polarity voltage application, which is fine for heating up the resistive element.

The amount of time the sine wave is applying 0 voltage is incredibly small.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2013
Posts: 145
Good Answers: 5
#31

Re: Running a 60 Hz Heating Element at 50 Hz

09/11/2013 4:35 PM

Hard to say.... I've ran a oven at full temperature with the door open until the element failed while I was on the other side of a partitioning wall from it. I could see evidence of massive flash of sparks and heard it it buzz similar to the sound of a sub station but much louder. (The buzzing sound woke me up and I could see the light casted on surrounding walls) I can testify that this is an extremely stupid way to save money heating an apartment by using a centrally located oven as opposed to using strip heaters located under windows on the periphery. The replacement broiler element cost me $54 plus shipping and two weeks of no oven use. (Can't blame my neighbor for sharing his cost saving techniques. I made the choice to try it.) Is there a similar risk to using a 60Hz element on a 50Hz system? Who knows? Could the manufacturer found a cost competitive advantage with similar specs by slight differences in alloy composition, manufacturing procedures or design tolerances? I imagine they could find a way to shave costs and improve profit margins enough for your element to fail. Good Luck!

Register to Reply Off Topic (Score 3)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#33

Re: Running a 60 Hz Heating Element at 50 Hz

09/12/2013 11:24 AM

How about, "It doesn't really matter".

<unsubscribe>

Register to Reply
Guru

Join Date: Aug 2009
Posts: 573
Good Answers: 5
#35

Re: Running a 60 Hz Heating Element at 50 Hz

09/13/2013 1:22 PM

I always think in extremes for thought experiment purposes.

Heating is only produced by the resistive portion of the element. The average current for DC will be, obviously, higher than AC, because peak voltage only happens every 50Hz or 60Hz as the case may be. Lessening the frequency until it approaches DC, say 1Hz or 0.1Hz will increase the average current and therefore increase the heat dissipated. So I'd vote for a bit more heating at 50Hz. If the waveform were square, the heating would essentially be the same as DC, regardless of frequency (at common AC power frequencies). But it's not.

If my thought is ill-founded, then so is my conclusion. Correction welcomed.

Register to Reply Off Topic (Score 3)
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#36
In reply to #35

Re: Running a 60 Hz Heating Element at 50 Hz

09/13/2013 2:30 PM

Look at Ohm's law and its derivative the Power triangle, where do you see AC, DC, or frequency mentioned? From a Basic Circuits site:

The answer wouldn't be any different if the question was stated as, "What's the power dissipated in a straight piece of nichrome wire that's powered by a power supply that outputs a DC offset triangle wave with a 30% duty factor" or any other such nonsense.

You simply calculate the RMS value of the waveform, square it, and divide by the hot resistance of the nichrome. That's what a "Hot-wire Wattmeter" does, integrates the heating effect of the combined voltage and current imposed on it, waveform doesn't matter.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#37
In reply to #35

Re: Running a 60 Hz Heating Element at 50 Hz

09/13/2013 2:44 PM

Really?

Do you know what the actual peak-to-peak voltage is in a 120 VAC circuit ?

Voltage, heater resistance, current flow. None of these will change with frequency, hence wattage won't either.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru

Join Date: Aug 2009
Posts: 573
Good Answers: 5
#39

Re: Running a 60 Hz Heating Element at 50 Hz

09/13/2013 8:14 PM

Yes, RAMConsult and WJMFIRE it was an error in my thinking. I was concentrating on the increased time around the peak value being extended for much longer periods, as the change is much slower there. For any one cycle, it would always be the RMS value, with no change in average heating. But if timed correctly, a heater run at 27X10-6 Hz, would provide more heat during a night's sleep, for instance, than the same heater run at 50Hz, during the same time period... unless I'm thinking poorly again. (Senility is looming on my horizon.)

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#40
In reply to #39

Re: Running a 60 Hz Heating Element at 50 Hz

09/13/2013 10:33 PM

Hz. Hz................it Hz me to respond to this...but here goes...

With any frequency, with a given RMS voltage, the current applied to a resistive load will always be the same. This applies to DC and AC. This is true for 0 HZ, 60 HZ, 400 HZ, or 1,000,000 HZ.

There is no exemption. Time (or even overnight) cannot alter this fact.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#41
In reply to #40

Re: Running a 60 Hz Heating Element at 50 Hz

09/14/2013 6:22 AM

The RMS current, yes, but if the frequency is non-zero but so low that the period is best measured in hours, the temperature of a heating element would vary significantly during the cycle.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#42
In reply to #41

Re: Running a 60 Hz Heating Element at 50 Hz

09/14/2013 8:31 AM

No Sir

If frequency is near zero or it tends to zero, then it is a DC voltage.

In case of DC Voltage Vpeak = Vrms

In case of sinusoidal, 50HZ, 60Hz, 400Hz or any frequency (ignoring skin effect on resistance of element)

Vpeak = 1.414 x Vrms

When we say 120V AC that means 120V RMS and not average or peak values.

Root mean squares means divide waveform in to nth number of small segments with time time 0 deg to ∏/2, each forming a small rectangle of base dθ and height Vθ. Multiply these two to get area of each imaginary rectangle, then square area of each rectangle, add all these squares and then take square root. That is RMS V.

Since Power of any circuit is proportional to square of voltage, hence the RMS voltage thus calculated is the voltage which produces power (in this case heating).

No where frequency comes in to play.

Think this small topic has engaged many as it is pure mathematics or imagination between zero and infinity.

Why not to close this topic - my sincere request to all.

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#43
In reply to #42

Re: Running a 60 Hz Heating Element at 50 Hz

09/14/2013 9:29 AM

Consider a supply with the frequency reduced to just one cycle per hour (while maintaining the sinusoidal nature of the waveform).

What will be the heating effect during the 10 minute period centered around zero crossing?

How will this compare with the heating effect during the 10 minute period centered around one of the peaks?

OK, the element may burn out as its power rating may be exceeded, but I think you must agree that it will tend to be hotter?

Once the period of supply variation is of the order of or longer than the thermal time constant of the element, the temperature will vary over time.

Do not close this topic until the correspondents get it right! To do so would perpetuate their ignorance.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#44
In reply to #43

Re: Running a 60 Hz Heating Element at 50 Hz

09/14/2013 10:58 AM

You are making an argument while changing the paramaters, which is not what the OP is asking.

If the sine wave period is one hour and heat is measured for one hour as well, the heat dissipated is the same as a DC voltage, 60 HZ, etc.

If the sine wave period is 60 HZ and you measure heat dissipated for 1/100000 second, a different result will be measured.

By the same token, if you measure accumulated water in a bucket from a dripping roof, you will get a different rate of accumulation by using an hourly measurement versus a time period so short that the first drip hasn't reached the bucket.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#45
In reply to #44

Re: Running a 60 Hz Heating Element at 50 Hz

09/14/2013 12:12 PM

You can call a supply which changes from 0 to 169.68V as a very very poorly regulated DC and not commercial AC.

And if this is a DC fluctuating supply - it should not have so poor regulation, that is, -100% to +41.4% in half an hour.

I am sure that you are an Engineer and must be aware that a good grid stays stable to the extent that variation at Consumer's point is with in +/- 5%.

Hence in this case peak shall be 126V maximum and you will agree that nothing shall happen to the heater element.

You also may be aware why 50HZ/60HZ frequency of power supply was standardized - to avoid flicker in incandescent lamps (specially the carbon coated filament lamps of earlier era) - hence please stay within Engineering parameters - even 1HZ or 0 Hz is not a problem but supply shall stay within limit. Please look again at my earlier explanation, on which you had raised the issue once again, where I said for DC supply Vrms = Vpeak = 120V.

I think this shall be my last comment on this subject.

Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#47
In reply to #44

Re: Running a 60 Hz Heating Element at 50 Hz

09/14/2013 12:41 PM

"You are making an argument while changing the paramaters" - Passerby changed the parameters in post #39, in which he cited a frequency of 27X10-6 Hz (period = 10.29 hours).

In your reply, you stated that "With any frequency, with a given RMS voltage, the current applied to a resistive load will always be the same". This is inaccurate, and would be better stated as "With any frequency, with a given RMS voltage, the RMS current taken over an integral number of cycles will always be the same".

"If the sine wave period is one hour and heat is measured for one hour as well, the heat dissipated is the same as a DC voltage, 60 HZ, etc." - this is only true of the total integrated heat, not the heat output at any given time.

Passerby was right (assuming that the element didn't burn out!).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Aug 2009
Posts: 573
Good Answers: 5
#49
In reply to #47

Re: Running a 60 Hz Heating Element at 50 Hz

09/16/2013 12:38 PM

Thank you JohnDG for picking up the slack that can happen to posts I make on Friday evenings. I rarely get on CF4 on weekends. And your answer was more efficient that mine would have been.

Not that it needs clarifying, but in the interest of a summation, the answer to the OP question is that for 50Hz the heating would be the same as 60Hz in practical experience. My post that said I would vote for a tad bit more heating at 50Hz was wrong.

Sometimes my convoluted, myopic thinking leads to mixing apples and oranges, without that being my intent. I'm sorry for that happening here and detracting from the discussion of the OP.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#50
In reply to #49

Re: Running a 60 Hz Heating Element at 50 Hz

09/16/2013 5:33 PM

No prob. mate.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#51
In reply to #40

Re: Running a 60 Hz Heating Element at 50 Hz

09/17/2013 2:26 PM

Pardon me if I restate material from other posts, but I am trying to bring this all together:

…between 50 and 60 Hz...? It would be hardly noticeable...but not immeasurable. Of note is that the heating element is cycling at 120x per second (60 Hz), or 100x (50 Hz). The frequency (Hertz) measures complete AC cycles. However, the resistive element is powered on both sweeps of the waveform.

Alternating current at a lower frequency, however, will cause production of less heat. In this case the lower the frequency, the lower the duty cycle.

A 10 Hz 120VAC RMS power source produces noticeable flicker in a tungsten filament incandescent lamp. (An incandescent lamp is more of a heat bulb than a light bulb with efficiency around 10% light-wise, so we can use it as a demonstration of the facts.) The 50 or 60 Hz waveform is pretty close to ideal to keep the tungsten filament at heat capacity, thus producing apparent continuous light (and heat) without noticeable flicker. The perception limit of the human eye is many times below this.

High speed footage, however, can catch this.

The heat capacity of the tungsten filament (or heating element material) must be taken into consideration to determine the rate of change.

Therefore, the frequency of the incoming power will have an effect on a resistive heating element. The effect is measurable with the proper equipment and can be calculated, but the effect is not noticeable by human only...unless your perceptions are outside of the norm.

Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jun 2013
Posts: 145
Good Answers: 5
#48

Re: Running a 60 Hz Heating Element at 50 Hz

09/15/2013 1:29 AM

"If the sine wave period is 60 HZ and you measure heat dissipated for 1/100000 second, a different result will be measured." However, 50 Hz is .020 seconds and 60 Hz is about .017 seconds. With this difference of roughly .003 seconds or 3/1000 second. But measurable to .00001 seconds due to ????? Is this an assumption? Perhaps your thinking is similar to the analogy of tank of water leaking at a fixed rate (heat output) yet never overflowing the top because the rate of water pouring in averages out to the same amount (120 V RMS)?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#52

Re: Running a 60 Hz Heating Element at 50 Hz

09/17/2013 2:26 PM

Pardon me if I restate material from other posts, but I am trying to bring this all together:

…between 50 and 60 Hz...? It would be hardly noticeable...but not immeasurable. Of note is that the heating element is cycling at 120x per second (60 Hz), or 100x (50 Hz). The frequency (Hertz) measures complete AC cycles. However, the resistive element is powered on both sweeps of the waveform.

Alternating current at a lower frequency, however, will cause production of less heat. In this case the lower the frequency, the lower the duty cycle.

A 10 Hz 120VAC RMS power source produces noticeable flicker in a tungsten filament incandescent lamp. (An incandescent lamp is more of a heat bulb than a light bulb with efficiency around 10% light-wise, so we can use it as a demonstration of the facts.) The 50 or 60 Hz waveform is pretty close to ideal to keep the tungsten filament at heat capacity, thus producing apparent continuous light (and heat) without noticeable flicker. The perception limit of the human eye is many times below this.

High speed footage, however, can catch this.

The heat capacity of the tungsten filament (or heating element material) must be taken into consideration to determine the rate of change.

Therefore, the frequency of the incoming power will have an effect on a resistive heating element. The effect is measurable with the proper equipment and can be calculated, but the effect is not noticeable by human only...unless your perceptions are outside of the norm.

Register to Reply Score 1 for Off Topic
Associate

Join Date: Jun 2019
Posts: 50
Good Answers: 1
#53

Re: Running a 60 Hz Heating Element at 50 Hz

07/20/2019 1:02 AM

The resistance of the conductor also depends on the frequency. The resistance of the conductor increase with an increase in frequency and gets decrease with decrease in frequency. This happens because of the SKIN EFFECT.

If 120 V 60HZ 1800 W heating element is supplied 120 V,50 Hz the resistance of the heating element will slightly decrease and the power will slightly increase.

P=V^2/R

Read More:Effect of frequency on Resistance

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#54
In reply to #53

Re: Running a 60 Hz Heating Element at 50 Hz

07/20/2019 5:24 AM

The key word being slightly. As the graph in your link shows, the difference in skin depth between 50 and 60Hz is minimal.

__________________
Give masochists a fair crack of the whip
Register to Reply
Participant

Join Date: Jul 2019
Posts: 3
#55

Re: Running a 60 Hz Heating Element at 50 Hz

07/30/2019 9:09 AM

Will not be difference

Register to Reply
Register to Reply 55 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); Anonymous Poster (2); berger316 (1); bioramani (1); Brave Sir Robin (1); Circuit Breaker (1); Codemaster (1); cuba_pete (2); dhayanandhan (2); dvmdsc (2); garyrich2000 (3); Hoovyendy (1); JohnDG (6); LAA_Lucke (1); lyn (5); old salt (1); oldchemist (1); Passerby (3); powersolutionsFBD (3); PWSlack (3); Rajesh52 (1); RAMConsult (3); redfred (1); SHOCKHISCAN (1); TonyS (1); Tornado (2); WJMFIRE (5)

Previous in Forum: Transformer Rated in kVA and Not kW   Next in Forum: Is the Classic Control Methods -PI - Still Low Compared with Intelligent Methods

Advertisement