If power factor formulas i.e KWH/KVAH and KWH /sq rt(kwh sq+ KVARH sq ) are same then why results at times are different.
Thanks
S Sharma
Good Answers: 109
Re: Power factor
09/12/2013 12:32 PM
Dont look the same!
Maybe the input is different.
Back to you!
Good Answers: 445
Re: Power factor
09/12/2013 12:35 PM
Because your formulas are wrong. Time (hours) is not used in calculating power factor, it's based on instantaneous values.
Re: Power Factor
09/12/2013 4:44 PM
I agree with RAM. PF = kw/kva . Where did you find the formula you used?
Re: Power Factor
09/12/2013 6:08 PM
If you get rid of all the H's, how are the results sometimes different?
Good Answers: 445
Re: Power Factor
09/12/2013 6:15 PM
Although the dimensions are the same (time/time), the periods (15 min. vs 30 min.) or the units (24 hrs. vs. 1 day) could be different. Anyway, when was the last time you saw a kVARH meter?
Good Answers: 131
Re: Power Factor
09/13/2013 8:13 AM
Actually, they do exist, or are a separate element of an electronic kWH meter. They are usually used in power generation plants where one of the things they can generate is kVAR for system voltage support. The generating plant needs to have a way to quantify and record the kVAR they generate for the purchasers (usually the transmission utilities and energy service providers).
Good Answers: 119
Re: Power Factor
09/12/2013 8:34 PM
kW = kilo Watt (Watt by definition is "real" power only)
kVA = kilo Volt*Amp (both a "real" power and an imaginary or "reactive" power component may be present)
kVAR = kilo Volt*Amp Reactive (only the reactive power component)
The addition of time only changes the internal units from power to energy. Since power factor is dimensionless and all the added time units will cancel out, the end result will be the same using either equation.
The equation you posted is basically correct. For power factor calculation, a more common usage would be the power equation (no "hours"):
PF = kW/kVA = kW/[sqrt{kW2 + kVAR2}]
If you are getting variable results, maybe you are not using the equation correctly?
ref.
http://en.wikipedia.org/wiki/Power_factor#Definition_and_calculation
http://en.wikipedia.org/wiki/Phasor
http://en.wikipedia.org/wiki/Volt-ampere_reactive
Re: Power Factor
09/12/2013 11:53 PM
When you use an energy meter which has time factor also built in you do get KWh and KVAh or KVARh. Your formulas are right. I too learnt that what they teach in college is incomplete. Pl take a true rms voltmeter and a true rms ammeter, multiply and see whether you get KVA and KW and now you use these get KVA. Power factor consists of two components (not taught in college) = Displacement component * distortion component.
Displacement component = cos (Θ) where Θ = angular shift between voltage and current of the FUNDAMENTAL COMPONENTS. Assuming voltage - from supply is not distorted, the curernt due to load can be distorted. So distortion component = rms of fundamental current / (√ (sum of squares of all harmonic currents). Hence your second formula assumes KVA = √(KW^2+KVAr^2) - which is not true when the waveforms are distorted (as it takes care of fundamental components only), which is true in real life (may not be in a college lab, in controlled conditions)
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member
Re: Power Factor
09/13/2013 7:36 AM
xyz, you get a GA because u opened up new thinking on pf and harmonics.
Are you saying kva (n) = kw (n) + kvAR (n)
here n= the harmonic number
and then ∑kva = ∑kw + Σkvar
or
kva (total) = √ [(∑kw)^2 + (Σkvar)^2]
or something similar?
BSEE but always learning
Re: Power Factor
09/13/2013 7:47 AM
The numerators are the same so let's look at the denominator. To make things less messy, let z=KVA, x=kw and y=KVAR, in other words, z = total power, x = real power, and y = reactive power.
z=sqrt(x^2+y^2) or z^2=x^2+y^2
KVAH=sum of z over time
kwh=sum of x over time
kVARH=sum of y over time
KVAH^2 = kwh^2 + kVARH^2 will be true if the power factor does not change during the time interval.
Here is an example using x,y, and z with unchanging power factor:
x=3, y=4, z=5
x=6, y=8, z=10
sum(x)=9, sum(y)=12, sum(z)=15
15^2 = 9^2 + 12^2
225=81+144
Here is an example with changing power factor:
x=3, y=4, z=5
x=5, y=12, z=13
sum(x)=8, sum(y)=16, sum(z)=18
324 not equal to 64+256
Re: Power Factor
09/13/2013 9:27 AM
Very well demonstrated. GA
For the OP: You get an average P.F. over the time span when using the H terms.
In the examples: 1) P.F. = 0.6 instantaneous
2) P.F. = 0.38 Instantaneous
When Adding them (as accumulation over a period), then P.F. = 0.44
Must use the instantaneous values.