Capacitors

09/12/2013 1:26 PM

Sir,

I have some problem when I am trying to increase the power factor for motors. I have fixed new capacitors for 20HP motors 2 nos and fixed 6 KVAr 3PH capacitor for each motor.Then I have checked the Power factor,it shows 0.57.Why not increasing the power factor and what will be the reason.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Capacitors

09/12/2013 2:33 PM

Where are you measuring the PF? On the motor leads only, or at a point that includes both the motor and capacitor?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Capacitors

09/12/2013 4:02 PM

How about telling us what the PF was before you installed the capacitor. Also important is more info on the motor type, ratings, etc., and exactly what information/calculations/logic that you used to select those particular units.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3
In reply to #2

Re: Capacitors

09/12/2013 4:11 PM

Now come on RAMC... the ones they chose from the catalogue looked pretty.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Capacitors

09/12/2013 4:42 PM

How are you measuring the PF?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: Capacitors

09/12/2013 4:42 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Sep 2012
Location: Seattle, WA, USA
Posts: 147
Good Answers: 9
#6

Re: Capacitors

09/12/2013 5:05 PM

Do you have a load on the motor? If the motor is unloaded, that looks about right. PF increases with motor load.

__________________
You have to actively participate in the manifestations of your own joys and good fortunes - they are not ready made for the taking, they are available for the making.
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Capacitors

09/12/2013 11:13 PM
  • "Do you have a load on the motor? If the motor is unloaded, that looks about right. PF increases with motor load."

Bingo. For all we know, the unloaded PF was .2, now with the caps it is at a .57, which would indicate that the caps are accomplishing something very significant. But that would also mean the initial premise was flawed at the outset.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: Capacitors

09/12/2013 11:24 PM

Dear Mr.marariayan,

How did you connect the two Capacitors - Is it in series or is it in parallel. What was the Power Factor before connecting the Capacitors.? What is the supply frequency. Is it 50 c/s or 60 c/s.? Where did you connect Capacitors.?

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9

Re: Capacitors

09/12/2013 11:42 PM

Size of PFCC depends on speed,voltage and frequency and % load on motor.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Capacitors

09/13/2013 3:31 AM

Exactly. If the motors are not doing much work, their power factors will be pretty low.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2007
Posts: 1035
Good Answers: 40
#11

Re: Capacitors

09/13/2013 1:33 PM

"Pretty-good-answers, all..." however, given that mararjayan NEVER (since 2011) made it back to his first request:

"What are the precuations to be taken before energising a 250 KVA oil type,11KV/440V transformer of a unitised substation and how to check the transformer oil is good or not. Experts please give me the answer."

...nor has he followed-up with further info after this:

"I have a Generator 3PH,415V. There is no name plate on it. How do i know the capacity(Kva) of generator.Please let me know."

... I doubt that he will find his way back here, so as to receive this "Well-Wish":

May the road rise up to meet you....rather than you stumble-and-fall-nose-first.
May the wind always be at your back....so that no sparks might fly into your face.
...
May God hold you in the palm of His hand....keeping you far-away-from any energized circuits.

(truly, wishing him well...)

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2013
Posts: 12
#12

Re: Capacitors

09/22/2013 7:26 PM

It might depend on how you connect the capacitors to the motor working of a 3 phase supply. You may want to connect the capacitors in delta configuration and then connect the bank of capacitors in parallel with the supply at the terminals of the motor. Let's say that the capacitor delta configuration (a trianglular arrangement is A, B & C. L1 goes to point A; L2 goes to point B and L3 goes to point C. Or you may connect a synchronous motor, running on "no-load", in parallel with the motors. Make sure to increase the DC excitation current of the motor to give a leading power factor.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); JRaef (1); Mike W (1); ndt-tom (1); North of 60 (1); pnaban (1); PWSlack (1); RAMConsult (1); SolarEagle (1); Tornado (1); triniboy (1); wareagle (1)

Previous in Forum: Power Factor   Next in Forum: Max. No. of Three Phase and Single Phase Circuits to be Connected

Advertisement