Surge Arrester in HT Side of the Transformer

09/13/2013 5:39 AM

Hi, Anybody here with experience in Transformer HT side surge arresters? Can you please share with me if we use a transforemer without surge protection in HT side what will be happen(of course LV side got install surge arresters)? According to my understanding in step down transformer HT side surge arresters for the protection of the transformer primary winding. LV side already protected with surge arresters and each DB also protected with surge arresters. In this case there is no way the equipment connected to DB cab be damage because of surge right? Please advise if you familier well with this type of surge protection. Thanks.

__________________
Improvement makes strait roads: but the crooked roads without Improvement are roads of Genius.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#1

Re: Surge arrester in HT side of the transformer

09/13/2013 6:45 AM

Sir: you said "According to my understanding in step down transformer HT side surge arresters for the protection of the transformer primary winding."

Your right. Consider a 250 KVA transformer with 15 KV primary/ 400v secondary. Disregarding efficiency, its primary is rated for 17A, its secondary for 600 amps, and those windings will be sized accordingly. Lets say for ex., the primary windings are 12 AWG = 2.5mm^2. Wouldn't u wanna protect those windings with a surge protector, and isnt such a protection required by code?

__________________
BSEE but always learning
Register to Reply
Active Contributor

Join Date: Oct 2009
Posts: 16
#2
In reply to #1

Re: Surge arrester in HT side of the transformer

09/13/2013 6:54 AM

Thanks you sir. I also same in your boat. Any country code of practise got stated need to protected the HT side of the transformer? If is it stated is it for protection of the transformer? Anyway surge can flow to LV side equipments connected?

__________________
Improvement makes strait roads: but the crooked roads without Improvement are roads of Genius.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Surge arrester in HT side of the transformer

09/13/2013 7:02 AM

<...no way the equipment connected to DB cab be damage because of surge...>

No-one can make any installation totally lightning-strike-free.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#4
In reply to #3

Re: Surge arrester in HT side of the transformer

09/13/2013 8:01 AM

Yet, the most common mistake is to install such surge protection devices incorrectly. Lightning represents a severe over-voltage event which requires a shunt type surge protector. It must be installed as close as reasonably possible to the point where a load takes its power. This device, of course, is a MOV (metal oxide varistor) rated for the line voltage at the load.

Another common type of surge protection is the line reactor which will help with limiting inrush from over-voltages caused by other (non-lightning) events. Both type of surge protection is the best approach. After that, you can use over-voltage, under-voltage, phase loss, and rotation relays to protect equipment for events that the other surge protection devices don't cover. Of course, you could always use a UPS to protect vital equipment. They have surge protection built in.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Score 1 for Good Answer
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Surge Arrester in HT Side of the Transformer

09/13/2013 10:10 AM

OP asks:

"...without surge protection in HT side what will be happen..." That's like asking if it's OK to use the transformer as a protective device.

When the unprotected transformer flashes over internally during a lightning strike or switching surge it may absorb enough energy so that the low side equipment doesn't "feel" the surge. The problem is that the transformer is a poor surge arrester because it doesn't "heal" or reset, it will be destroyed in the process, the plant will be without power, and it will take time to replace it. But maybe nothing on the low side was damaged.

Why not calculate how much you'll save by not installing surge protection against how much it will cost you to replace the transformer plus the cost of lost production. The answer will bring renewed meaning to the phrase "Penny wise and Pound foolish".

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#7
In reply to #5

Re: Surge Arrester in HT Side of the Transformer

03/22/2014 1:59 AM

Dear All,

We have an 18 MW Diesel Engine Generator of 11kV Gen. Voltage, connected to a 11/132 kV Transformer. Between the Generator and the Transformer we have a 11kV Vacuum Circuit Breaker acting as a Generator Circuit Breaker. Adjacent to Generator Terminals in Parallel to it, a Surge Arrester (Rated Voltage - 12kV, 10kA and 12.6 kV MCOV ) and Surge Capacitor of rating (15kV and .25 mfd) respectively is connected in parallel in all 3 phases to protect against any switching surges. (Between Generator and GCB)

We have also proposed to provide a Surge Arrester of Similar rating as mentioned above Between GCB and Transformer 11kV Terminals.

Could you please clarify whether a Surge Capacitor is also required to be provided between GCB and Transformer 11kV terminals in parallel with SA in all 3 phases.???

Besides, we have a 120kV and 10kA Lightning arrester connected at the transformer HT end.

Regards,

Raghavendran.R

__________________
"Engineering is Passion"
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #7

Re: Surge Arrester in HT Side of the Transformer

03/22/2014 9:18 AM

Please start a new thread if you want everyone to see it.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#6

Re: Surge Arrester in HT Side of the Transformer

09/14/2013 5:09 AM

If HT supply to transformer is via overhead line - You must install LA as close as possible to the transformer. This is to protect it against direct or indirect lightning.

If HT supply is through underground cable LA is not required as there is no question of direct or indirect lightning surge.

If HT supply is mixture of overhead line and cable, cable being at Transformer end AND the length of cable is long (say more than a kilometer) - LA is not required. Reason being the capacitance of cable to ground acts as a surge absorber. Hence energy of any lightning surge of O/H line, as it travels through the cable, is divert to earth, thus its wave shape modified to safe value by the time it reaches the Transformer terminals.

I do not know how big is your transformer but in case of large Transmission Line transformers, besides LA, the first turn of transformer winding has very thick insulation (say approx 25 mm in thickness compared to normal thickness of 0.5mm) and is gradually tapered of in first one or two turns to normal size. This is called surge coil and protects transformer against surge. This design is only followed in Transformers of few MVA and above and not in small Distribution Transformers.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); hasantha84 (1); NotUrOrdinaryJoe (1); powersolutionsFBD (1); PWSlack (1); Raghavendran R (1); RAMConsult (2)